Default 2 pole breaker

Hello everyone

Would you be allowed to run a pool pump and a salt generator from the same 2 pole breaker. The pool pump at 240V runs around 5-6amps and the salt generator at 240v runs at 1amp. Well below 80% or 12amps.

Discussion greatly appreciated

Mark
Reply With Quote
  #2  
Old 4/18/08, 12:01 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

As long as each has its own disconnect
Reply With Quote
  #3  
Old 4/18/08, 12:07 AM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

Hi Mike

So you are saying that there should be a separate 240v double throw switch for each unit. I think double throw is the correct term for the switch.
Reply With Quote
  #4  
Old 4/18/08, 12:30 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

Yes.
Multimotors are allowed on the same circuit as outlined in 430.24 of the NEC as long as each motor has some sort of disconnect insight of each motor.
These disconnects can be anything from cord and plug up to a knife disconnect with or without fuses or a breaker.
Reply With Quote
  #5  
Old 4/18/08, 12:45 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

If they were grouped they could use the same disconnect if it was in sight of both of them.
Reply With Quote
  #6  
Old 4/18/08, 9:04 AM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

The Salt generator isn't a pump. It some how puts salt into the pool water. The reason they want the salt generator to stop when the pool pump isn,t working is because harmful gases will build up. There is a panel inside the pool shed where everything is located.
Reply With Quote
  #7  
Old 4/18/08, 12:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

It is actually a chemical generator that causes the Cl in NaCl (salt is already in the pool at about 5-6 PPT) to be freed for a few seconds and sanitize the water. The manufacturer's instructions call for it to be on the pump circuit, like a heater, so it won't run when the pump is off.
Reply With Quote
  #8  
Old 4/18/08, 12:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 pole breaker

Quote:
Originally Posted by Greg Fretwell
It is actually a chemical generator that causes the Cl in NaCl (salt is already in the pool at about 5-6 PPT) to be freed for a few seconds and sanitize the water. The manufacturer's instructions call for it to be on the pump circuit, like a heater, so it won't run when the pump is off.
This is exactly right. Some folks think it is the salt itself that does the work. These things should not be called salt generators. They should be called chlorine generators.

It is very common to have them on the same disconnect as the pump. This makes sense since they both MUST run, and not run, at the same time.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 3:05 PM
Double pole breaker, metal showing between sections lfoster Electrical Inspections 2 9/6/07 1:25 PM
Double pole breaker with one wire. abolt Electrical Inspections 5 5/1/07 2:47 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 10:04 AM


All times are GMT -4. The time now is 5:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts