Default 2 prong

Hey guys, how are any of you reporting on two prong outlets being converted to 3 prong without ground?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 8/1/09, 9:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 2 prong

Ungrounded outlet
Reply With Quote
  #3  
Old 8/1/09, 9:21 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: 2 prong

Quote:
Originally Posted by nbhi View Post
Hey guys, how are any of you reporting on two prong outlets being converted to 3 prong without ground?
As a potential safety hazard in need of repair.

Google ungrounded 3-prong receptacles.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 8/1/09, 10:33 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: 2 prong

Many outlets were the 3-prong type and nearly all were ungrounded. Although a ground isn't required of 2-prong outlets, if the receptacle is 3 prong and ungrounded it gives a false sense of safety. Grounding of all 3-prong outlets, reverting back to 2-prong outlets, or protecting them with ground fault circuit interrupters (GFCIs) is recommended for safety reasons.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 8/2/09, 12:06 AM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 prong

I believe someone else posted this before.


One or more open ground, three-pronged electric receptacles were found. This is a safety hazard due to the risk of shock. A qualified electrician should evaluate and make repairs as necessary. For example, replacing receptacles or correcting wiring circuits.

Grounding type receptacles began being required in residential structures during the 1960s. Based on the age of this structure and the presence of 2-pronged receptacles in some areas of this structure, an acceptable repair may be to simply replace the ungrounded 3-pronged receptacles with 2-pronged receptacles. However the following appliances require grounding type receptacles:
· Computer hardware
· Refrigerators
· Freezers
· Air conditioners
· Clothes washers
· Clothes dryers
· Dishwashers
· Kitchen food waste disposers
· Information technology equipment
· Sump pumps
· Electrical aquarium equipment
· Hand-held motor-operated tools
· Stationary and fixed motor-operated tools
· Light industrial motor-operated tools
· Hedge clippers
· Lawn mowers

This list is not exhaustive. Grounded circuits and receptacles should be installed in locations where such appliances will be used.



Gary
http://www.hsspropertyinspection.com/
Reply With Quote
  #6  
Old 8/2/09, 12:12 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,564
Default Re: 2 prong

Quote:
Originally Posted by jfunderburk View Post
Many outlets were the 3-prong type and nearly all were ungrounded. Although a ground isn't required of 2-prong outlets, if the receptacle is 3 prong and ungrounded it gives a false sense of safety. Grounding of all 3-prong outlets, reverting back to 2-prong outlets, or protecting them with ground fault circuit interrupters (GFCIs) is recommended for safety reasons.


what Joe said...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #7  
Old 8/2/09, 7:14 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 2 prong

Quote:
Originally Posted by jfunderburk View Post
Many outlets were the 3-prong type and nearly all were ungrounded. Although a ground isn't required of 2-prong outlets, if the receptacle is 3 prong and ungrounded it gives a false sense of safety. Grounding of all 3-prong outlets, reverting back to 2-prong outlets, or protecting them with ground fault circuit interrupters (GFCIs) is recommended for safety reasons.
Can GFCI's still protect for grounding purposes with out a ground wire? I know that GFCI'S protect for areas around water and such.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 8/2/09, 8:20 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 2 prong

Quote:
Originally Posted by nbhi View Post
Can GFCI's still protect for grounding purposes with out a ground wire? I know that GFCI'S protect for areas around water and such.
Yes.
Reply With Quote
  #9  
Old 8/2/09, 10:06 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: 2 prong

Quote:
Originally Posted by jfunderburk View Post
I would be very careful about calling it a safety hazard. It's not a violation of the code I'm aware of, yet you're calling it unsafe?


406.3(D) Replacements Replacement of receptacles shall comply with 406.3(D)(1), (D)(2), and (D)(3) as applicable.

(1) Grounding-Type Receptacles Where a grounding means exists in the receptacle enclosure or a grounding conductor is installed in accordance with 250.130(C), grounding-type receptacles shall be used and shall be connected to the grounding conductor in accordance with 406.3(C) or 250.130(C).

(2) Ground-Fault Circuit Interrupters Ground-fault circuit-interrupter protected receptacles shall be provided where replacements are made at receptacle outlets that are required to be so protected elsewhere in this Code.

(3) Non–grounding-Type Receptacles Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).

(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).

(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked ``No Equipment Ground.'' An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted to be replaced with a grounding-type receptacle(s) where supplied through a ground-fault circuit interrupter. Grounding-type receptacles supplied through the ground-fault circuit interrupter shall be marked ``GFCI Protected'' and ``No Equipment Ground.'' An equipment grounding conductor shall not be connected between the grounding-type receptacles.


Also, here is a potential safety hazard example that someone posted here in the past:

There is more to it than a false sense of security. A 3 prong receptacle installed on a two wire system, and used to power a metal appliance with a 3 prong plug, can actually be an electrocution hazard. Think what happens when a conductor with old, dried out cracking insulation is moved around while replacing the receptacle, then shoved back into a metal box. All it takes is for the conductor to make contact with the metal box, energizing the box, the receptacle yoke, the grounding hole, and the metal cabinet of the appliance.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 8/2/09, 10:24 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: 2 prong

Nice info Larry
Reply With Quote
  #11  
Old 8/2/09, 11:14 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: 2 prong

Please disregard my statement about it not being a safety hazard. I was thinking the thread was about 2 prongs, when it's about 2 prongs converted to 3 prongs. My bad. It is a safety hazard.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 8/2/09, 12:30 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 2 prong

Quote:
Originally Posted by nbhi View Post
Hey guys, how are any of you reporting on two prong outlets being converted to 3 prong without ground?

First things first....

Is this home wired with BX, Romex or cloth wiring? Knob and Tube maybe?

Determine the type of wiring in order to obtain the correct answer!

Last edited by dvalley; 8/2/09 at 12:33 PM..
Reply With Quote
  #13  
Old 8/2/09, 12:40 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 2 prong

The house is wired with Romex, that's whats coming out of the panel. the home is 80 yrs. young.
Joe, where in your statement you say that it isn't a safety concern?
I didn't read it as such. Your post does mention a sense false security.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #14  
Old 8/2/09, 12:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 2 prong

Quote:
Originally Posted by nbhi View Post
The house is wired with Romex, that's whats coming out of the panel. the home is 80 yrs. young.
Joe, where in your statement you say that it isn't a safety concern?
I didn't read it as such. Your post does mention a sense false security.

Gary,

If this home is wired with Romex, then where's the ground wire?

It's disconnected somewhere! Simply recommend that an Electrician connect all ground wires to the 3-prong outlets.

Last edited by dvalley; 8/2/09 at 12:47 PM..
Reply With Quote
  #15  
Old 8/2/09, 1:09 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 2 prong

David
Here are the pics.
2-prong-copy-p8010061.jpg

2-prong-copy-p8010075.jpg



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two Prong Outlets jallingham Electrical Inspections 22 6/27/07 2:07 AM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
2 Prong Receptacles dnasser Electrical Inspections 5 2/26/07 11:24 AM