Do 2 prong outlets pose a problem for computers a/d electronic equipment? I have a client that's about to walk away from a house because of the 2 wire system. I suggested asking a qualified electrician. Is there an issue here?
Tim
Reply With Quote
Find an InterNACHI certified South Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 6/8/09, 9:13 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: 2 prong outlets and computer equipment

As far as I know, its the same basic issue of any grounded appliance. If you use an adapter, or upgrade the outlets with GFCI's then the appliance will work, but won't have the same protection through the grounded pin.
Reply With Quote
  #3  
Old 6/8/09, 9:21 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,409
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by thowell View Post
Do 2 prong outlets pose a problem for computers a/d electronic equipment? I have a client that's about to walk away from a house because of the 2 wire system. I suggested asking a qualified electrician. Is there an issue here?
Tim
Surge protectors will not work with out a ground thats about the only problem, What i suggest run a dedicated circuit. This is what I write up.

Suspected 2 wire system present meaning there is no ground present which would be expected on this age of a home. However beware that surge protectors will not work without a ground . This would effect appliances like computers, High end TV, Stereo's
I am sure there will some disagree but CYA
It will be between the seller and buyer to decide not your Worry.
Reply With Quote
  #4  
Old 6/8/09, 9:24 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 502
Default Re: 2 prong outlets and computer equipment

The answer to the question can be found by plugging in the computer and trying it. Most modern units will likely work ok. However, in the larger scheme of things, whoever owns the house will eventually have to face the need for some fairly costly upgrades (unless the original wiring was done with conduit).



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 6/8/09, 9:27 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,409
Default Re: 2 prong outlets and computer equipment

I also Suggest a whole panel Surge protector to Protect the bigger equipment < they run about 200 Bucks . and mount on the panel.

Last edited by wwilson3; 6/8/09 at 9:33 AM..
Reply With Quote
  #6  
Old 6/8/09, 10:00 AM
Tim C. Howell Tim C. Howell is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: New Liberty, IA
Posts: 35
Default Re: 2 prong outlets and computer equipment

Thanks everyone
Reply With Quote
  #7  
Old 6/8/09, 10:19 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 274
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 prong outlets and computer equipment

There would not be a need to upgrade the entire house. A new grounded circuit could be installed where the computer will be located.

Please also read Article 250.114 in the NEC.
Reply With Quote
  #8  
Old 6/8/09, 12:18 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,525
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by fnewman View Post
The answer to the question can be found by plugging in the computer and trying it.
How do you plug a 3-prong plug into a 2-prong receptacle?

Quote:
Originally Posted by thowell View Post
Do 2 prong outlets pose a problem for computers a/d electronic equipment?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #9  
Old 6/8/09, 12:31 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,694
Default Re: 2 prong outlets and computer equipment

You're silly Rick. Everybody knows to remove the third (round) prong from the cord.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #10  
Old 6/8/09, 5:07 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by rmaday View Post
How do you plug a 3-prong plug into a 2-prong receptacle?
http://www.asihome.com/ASIshop/produ...oducts_id=2913

I keep one of these in my computer bag for doing reports in older homes. The computer isn't protected, but it works.
Reply With Quote
  #11  
Old 6/8/09, 5:27 PM
Andrew Rook Andrew Rook is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 199
Default Re: 2 prong outlets and computer equipment

Plugging a 3 prong plug for a computer into a 2 prong outlet can void the warranty on the computer. Same is true for TV's with 3 prong plug, Microwaves, etc.

If a computer, TV, Microwave, etc. has a 3 prong plug, the manufacturer wants it plugged into a 3 prong grounded outlet.

So I would NOT plug a 3 prong plug into an ungrounded outlet.



Andrew Rook
NJ Home Inspector
License # 24GI00063600

Rook Home Inspections LLC
Hamilton NJ
(609) 588 - 0125
www.RookInspections.com
www.MercerCountyHomeInspection.com

Be Smart, Be Sure, Be Inspected TM
Reply With Quote
  #12  
Old 6/8/09, 5:30 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,525
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by mnahrgang View Post
http://www.asihome.com/ASIshop/produ...oducts_id=2913

I keep one of these in my computer bag for doing reports in older homes. The computer isn't protected, but it works.
Would you recommend your clients use those for their high dollar electronics (or any appliance that had a 3-prong plug)?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector

Last edited by rmaday; 6/8/09 at 5:43 PM..
Reply With Quote
  #13  
Old 6/8/09, 5:38 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,813
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jjonas View Post
You're silly Rick. Everybody knows to remove the third (round) prong from the cord.
Uh...Jeffrey......there are some folks reading these threads that..ah...well, you know...maybe you shouldn't say things like that.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Find an InterNACHI certified South Dakota Home Inspector (and anywhere else in North America)
  #14  
Old 6/8/09, 6:26 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,694
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jwilliams4 View Post
Uh...Jeffrey......there are some folks reading these threads that..ah...well, you know...maybe you shouldn't say things like that.
Yes, you're right, my bad... guess I'll have to go spend $0.29 on one of those adapter thingy's. Sorry for the poor advice everyone!



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #15  
Old 6/8/09, 7:02 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,743
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by rmaday View Post
Would you recommend your clients use those for their high dollar electronics (or any appliance that had a 3-prong plug)?
\

Nope... I tell them about running a ground wire, re-wiring with 3 wire, and GFCI as options. I use the the adapter with my laptop to get a job done. I know it's a risk, and I understand the possible consequences. It's a risk I'm willing to take every now and then to get the job done.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 prong receptacles pwancata Electrical 144 5/2/09 4:31 PM
reverse polarity?? Scott Schultz Electrical 33 10/24/07 2:50 PM
Two Prong Outlets jallingham Electrical 22 6/27/07 3:07 AM
Two Prong Outlets sboyd2 Electrical 79 9/4/06 8:05 PM


All times are GMT -4. The time now is 8:39 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts