Quote:
Originally Posted by thowell View Post
Do 2 prong outlets pose a problem for computers a/d electronic equipment? I have a client that's about to walk away from a house because of the 2 wire system. I suggested asking a qualified electrician. Is there an issue here?
Tim
Be careful trying to persuade a client as to what is a problem. If they think a two wire system is a problem, it's a problem to them. Maybe when you do their next inspection it will have more wires.
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #17  
Old 6/9/09, 2:15 AM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 303
Default Re: 2 prong outlets and computer equipment

I would just break the third ground prong off a 3 prong power strip so I can plug multiple 3 prong items in a 2 prong outlet>> yea thats the ticket!!



please dont follow this advise



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #18  
Old 6/14/09, 10:22 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by bkelly2 View Post
Be careful trying to persuade a client as to what is a problem. If they think a two wire system is a problem, it's a problem to them. Maybe when you do their next inspection it will have more wires.
If asked that question specifically, I would explain the situation to the clinet and advise them to make certain that they use their appliances in accordance with the manufacturer's recommendations. However, I also would probably say that having two-prong outlets in a home of that age is not prohibited, but would stop short of describing how to 'bypass' the situation.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #19  
Old 6/14/09, 10:36 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: 2 prong outlets and computer equipment

There is nothing inherently wrong with a two-wire system, but the way we use it may be. Today’s electrical appliance needs are far greater than they were 40 or 50 years ago, and using yesterday’s supply to satisfy today’s demand may often become very dangerous.

The use of three-hole ground-type receptacles on a two-wire electrical system gives the impression that safety protection is present in the circuit, when in reality it is not. Older style two-hole receptacles are still available and should be installed to eliminate this false sense of security. Three-hole receptacles may be more convenient (and often less expensive), but are often installed without giving consideration to this situation.
The use of a three-pronged plug in an ungrounded receptacle can be a safety concern. The plug has the grounding provision for a reason and electrical appliances should always be used for the function they were intended to perform.

All such installations should be labeled “No Equipment Ground” on each receptacle that applies. Grounding of all “three-pronged” receptacles or protection with a Ground Fault Circuit Interrupter (GFCI) on each is recommended for safety reasons.

“Two-hole” outlets are not grounded and should never be used with a “three-pronged” plug. Adapters have been devised for this usage, but there is still no adequate ground and such adapters are not always safe. Until the electrical system is upgraded for “three-pronged” usage, it would be prudent to not use adapters, extension cords, or “three-pronged” plugs in any way. Consider that “three-pronged” plugs have been engineered for use with a “three-hole” grounded receptacle.

http://www.cpsc.gov/cpscpub/pubs/524.html



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #20  
Old 6/14/09, 10:57 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: 2 prong outlets and computer equipment

Quote:
“Two-hole” outlets are not grounded and should never be used with a “three-pronged” plug. Adapters have been devised for this usage, but there is still no adequate ground and such adapters are not always safe.


This statement is a load of crap.

You're kidding me, right?
Reply With Quote
  #21  
Old 6/14/09, 11:02 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: 2 prong outlets and computer equipment

Consider that “three-pronged” plugs have been engineered for use with a “three-hole” grounded receptacle.

The manufacturer requires a three-hole receptacle, and that's what I work with.

Somehow, I don't believe the manufacturer consulted you before making their determination, so I'll stick with what they say.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #22  
Old 6/14/09, 11:04 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: 2 prong outlets and computer equipment

Time after time, licensed electricians have agreed with me (I suppose there were some who didn't, but that was never presented to me.) It is possible they agreed because it meant work for them...but I doubt it.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #23  
Old 6/14/09, 11:09 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: 2 prong outlets and computer equipment

To the point:

"The house is wired with 2-prong ungrounded receptacles. While common years ago and still acceptable today, the lack of a grounding conductor will limit the use of certain appliances such as refrigerators, washing machines, computers, etc. that require a ground. Dedicated circuits may have to be run to properly and safely use such appliances. You should consult with a licensed electrician about the limitations of this older wiring system."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #24  
Old 6/14/09, 11:41 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: 2 prong outlets and computer equipment

Quote:
The house is wired with 2-prong ungrounded receptacles.
No. This statement may or may not be correct.
Quote:

The house is wired using older 2-prong receptacles. While the receptacle itself may, indeed, be grounded, it lacks the ability to extend the system ground to a device which may require it. An upgrade to 3-prong GROUNDING receptacles may be warranted, if the existing system supports this configuration, and if the need arises.
You are both assuming that a two-wire receptacle is ungrounded. This is simply not true. the ONLY way that a receptacle (ANY receptacle) is UNGROUNDED is if there is nothing extending the system ground to the receptacle.

Two-wire armor-sheathed cable and 3-wire non-metallic cable may extend the ground to the receptacle box. The mounting screws for the receptacle (at the upper and lower tabs) mechanically and electrically bond the receptacle to the gronded receptacle box; thusly GROUNDING the receptacle.

A cheater plug may indeed be UL listed and LEGAL for the purpose of extending the system ground to a 3-prong device that calls for it.

The ONLY way to detwemine if a receptacle is ungrounded is to examine the system and distribution cables associated with it.

Absent of this effort, the rest is hoopla, balderdash, and poppycock.

Stop getting hung up on what the receptacle looks like or doesnt look like! INSPECT the SYSTEM!

The SYSTEM will determine what is going on, and provide you with the datum needed to convey ACCURATE information, so your client can make an INFORMED decision.

Last edited by jfarsetta; 6/14/09 at 11:46 PM..
Reply With Quote
  #25  
Old 6/15/09, 12:13 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,489
Default Re: 2 prong outlets and computer equipment

The two wire system is neither a defect nor is it, by itself, unsafe. It should not be called out as a defect in a home inspection.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #26  
Old 6/15/09, 12:19 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jbushart View Post
The two wire system is neither a defect nor is it, by itself, unsafe. It should not be called out as a defect in a home inspection.
A Material defect is a problem with a residential real property or any portion of it that would have a significant adverse impact on the value of the property or that involves an unreasonable risk to people on the property.


????????



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #27  
Old 6/15/09, 12:22 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is online now
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jfarsetta View Post
Two-wire armor-sheathed cable and 3-wire non-metallic cable may extend the ground to the receptacle box. The mounting screws for the receptacle (at the upper and lower tabs) mechanically and electrically bond the receptacle to the gronded receptacle box; thusly GROUNDING the receptacle.
Joe , in the above situation, does the receptacle box need to be metal or can it be plastic in order to bond the receptacle to the box?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #28  
Old 6/15/09, 12:50 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,930
Default Re: 2 prong outlets and computer equipment

If you plug a 3-prong adapter (cheater plug) into a 2-prong outlet and then plug in a 3-prong tester and first it reads open ground and then you connect the metal tab to the plate cover screw and it now reads correct circuit.

Would this identify the 2-prong outlet as being grounded? Or could this be giving a false reading to the tester?



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #29  
Old 6/15/09, 3:40 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jbushart View Post
The two wire system is neither a defect nor is it, by itself, unsafe. It should not be called out as a defect in a home inspection.
I didn't say it was a defect. My statement simply informs the client that the house has an older system that probably is not grounded and advises them to consult with an electrician about the limitations. I would think a client would be pretty angry if I failed to do so.

Similarly, I let them know that these older houses do not have as many outlets s new homes and they may need to add more.

I do not add these informational items to the Summary section (a section in my state relegated to items that need service or further investigation).

Regarding your statement about the receptacle box being grounded, in my experience that it rare. Mose 2 wire systems I see have no ground conductor at all. That is apparent by looking inside the panel.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #30  
Old 6/15/09, 8:29 AM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: 2 prong outlets and computer equipment

Quote:
Originally Posted by jfarsetta View Post
You are both assuming that a two-wire receptacle is ungrounded. This is simply not true. the ONLY way that a receptacle (ANY receptacle) is UNGROUNDED is if there is nothing extending the system ground to the receptacle
And you are assuming that a more dilligent inspection was not made. In so much as I cannot recall you having been looking over my shoulder during an inspection, I feel safe in assuming that you were not present. In which case, keep you assumptions of my inspection ability to yourself.

I take strong exception to your claim:

"This statement is a load of crap."



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 prong receptacles pwancata Electrical Inspections 144 5/2/09 4:31 PM
reverse polarity?? Scott Schultz Electrical Inspections 33 10/24/07 2:50 PM
Two Prong Outlets jallingham Electrical Inspections 22 6/27/07 3:07 AM