Default 2-prong outlets: Narrative examples?

I'd like to see examples of narratives describing home electrical systems with ungrounded 2-prong outlets if anyone would like to share them. -Kent
Reply With Quote
  #2  
Old 6/23/06, 1:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: 2-prong outlets: Narrative examples?

Courtesy of InspectVue (Keith Swift). . .

Quote:
The ungrounded and obsolete outlets should be upgraded to include more modern and safer ones, which provide a pathway for the current to travel harmlessly to ground.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 6/23/06, 2:04 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-prong outlets: Narrative examples?

I'm assuming here that the 2 prong outlets are on a 2 wire electrical system.

I understand the safety issue involved.

Going by the quote, I should be recommending that all 2 wire outlets be replaced with grounded ones?

How is that expressed to the buyer?

Most of the time on a two wire system, wouldn't that require totally rewiring the outlet?

I would also like a narrative of how to explain a 2 wire system to clients.
Reply With Quote
  #4  
Old 6/23/06, 2:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-prong outlets: Narrative examples?

"Ungrounded 2-prong electrical outlets do not provide an effective pathway for equipment grounding procedures. The recommendation is to consult a licensed electrical contractor for your options."



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 6/23/06, 2:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-prong outlets: Narrative examples?

CC.....as I stated the electrical contractor will give them these options:



(3) Non–grounding-Type Receptacles.
Where grounding
means does not exist in the receptacle enclosure, the installation
shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).

(a) A non–grounding-type receptacle(s) shall be permitted
to be replaced with another non–grounding-type receptacle(s).

(b) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a ground-fault circuit interrupter type
of receptacle(s). These receptacles shall be marked
"No Equipment Ground." An equipment grounding conductor
shall not be connected from the ground-fault circuitinterrupter-
type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a grounding-type receptacle(s)
where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the groundfault
circuit interrupter shall be marked "GFCI Protected"
and "No Equipment Ground." An equipment grounding
conductor shall not be connected between the groundingtype
receptacles.

Hope this explains the options they have....





Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 6/23/06, 2:17 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-prong outlets: Narrative examples?

Also....figured I would throw in....Yes, the circuit can also be protected by a GFCI Breaker as well....labeling still applies.......



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 6/23/06, 4:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: 2-prong outlets: Narrative examples?

Paul,

Is GFCI protection required when three-prong (grounding-type) receptacles are palced on two-wire (ungrounded) branch circuits?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 6/23/06, 4:53 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-prong outlets: Narrative examples?

I think I get it, Paul.

Let me know if I'm off here.

So per (D)(3)(C)

If you had five 2 prong receptacles on 1 circuit, you could replace the first receptacle in the circuit with a GFCI (labeled no ground) then replace the 4 downstream receptacles with standard 3 prong receptacles (labeled no ground & GFCI protected)

Makes sense in my head. Am I understanding correctly? Would this be legal?

If this is the case, Jeff, then not all 2 prong receptacle would need to be replaced with GFCI, just the first receptacle in the circuit.

RIGHT???!!!
Reply With Quote
  #9  
Old 6/23/06, 6:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-prong outlets: Narrative examples?

CC,

You are correct. If you choose to replace the 2 prong with 3 prong receptacles...you can ONLY do it as listed in my example of # 2 and # 3....option # 1 is simply to replace existing 2 Prong with 2 prong replacements only...

Jeff, that is correct....IF someone wishes to use 3 prong on an existing 2-wire circuit.....replacing with 3 prong itself is WRONG unless they use the options shown in my previous statement which at that point the NEC makes the allowance for.

Hope that answers it...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 6/23/06, 8:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: 2-prong outlets: Narrative examples?

Many receptacles were 2-prong ungrounded receptacles. While acceptable, this older wiring method limits the use of some modern appliances such as refrigerators, washing machines, computers, etc., that require a grounding conductor. Dedicated circuits may have to be run to properly use such appliances.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 6/23/06, 8:38 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: 2-prong outlets: Narrative examples?

http://www.cpsc.gov/cpscpub/pubs/524.html



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #12  
Old 6/23/06, 8:41 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: 2-prong outlets: Narrative examples?

...and for three-prong outlets on a two-wire system...

The use of three-slot grounded type outlets gives the impression that safety protection is present in the circuit, when in reality it is not. Older style two-slot outlets are still available and should be installed to eliminate this false sense of security. Three-slot outlets are more convenient and are often installed without consideration to this situation.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #13  
Old 6/23/06, 9:02 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: 2-prong outlets: Narrative examples?

Another determining factor is the cost of the two prong versus the cost of the 3 prong. Checking for myself I found the replacement 2 prongs were about 5 times more expensive than buying a standard 3 prong "grounded" outlet. Many folks will just buy the new cheaper 3 prong to "solve the problem" and figure it is okay.
Reply With Quote
  #14  
Old 6/23/06, 9:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-prong outlets: Narrative examples?

This is why these two options are the best.....and option (b) being the less expensive of the two....BUT does require some HOMEWORK to ensure the FIRST receptacle in the chain is found.

let us also remember that a GFCI receptacle has listed in it's manual how many receptacles it can protect downstream...the number is not INFINITY...lol
Quote:
(b) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a ground-fault circuit interrupter type

of receptacle(s). These receptacles shall be marked
"No Equipment Ground." An equipment grounding conductor
shall not be connected from the ground-fault circuitinterrupter-
type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.

(c) A non–grounding-type receptacle(s) shall be permitted
to be replaced with a grounding-type receptacle(s)
where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the groundfault
circuit interrupter shall be marked "GFCI Protected"
and "No Equipment Ground." An equipment grounding
conductor shall not be connected between the groundingtype
receptacles.
Here is something from the 1999 NEC...but still rings true for the 2002 NEC...just the article numbers have changed a bit...but a nice illustration to go with the things I listed earlier....




Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/23/06 at 11:18 PM..
Reply With Quote
  #15  
Old 6/24/06, 12:32 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-prong outlets: Narrative examples?

Quote:
Originally Posted by jfunderburk
Many receptacles were 2-prong ungrounded receptacles. While acceptable, this older wiring method limits the use of some modern appliances such as refrigerators, washing machines, computers, etc., that require a grounding conductor. Dedicated circuits may have to be run to properly use such appliances.
Joe, this is the most sensible statement I have seen regarding 2 wire receptacles. After all, most household lamps and appliances are 2 wire. I do not believe it is wise to inform a buyer/seller that a two wire system should be completely replaced which can certainly cause panic on their part. It can be updated as needed like you advise in your statement.

Be aware that while GFCI protection is a legal way to install a 3 wire recep on a two wire system, it is still a code violation to plug an appliance into that GFCI if the manufacturer states that the appliance requires a grounded circuit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two Prong Outlets jallingham Electrical 22 6/27/07 3:07 AM
Properly Testing GFCI Outlets tchristopher Electrical 17 3/17/07 12:19 PM
Two Prong Outlets sboyd2 Electrical 79 9/4/06 8:05 PM
Two prong outlets and GFCI's crichiii Electrical 8 3/15/06 11:41 PM


All times are GMT -4. The time now is 2:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147