Default 2 prong receptacles

Is it a good idea to recommend to clients to update electrical receptacles to a 3 prong grounded outlet in living spaces such as family rooms, iving rooms, etc... to meet modern electrical requirements for cable,electronics,computers, etc... Also, has anyone used the Ideal circuit analyzer 61-165. i'd like to get some feedback. Thanks

Paul Wancata
Inspections Unlimited
Reply With Quote
Find an InterNACHI certified New Hampshire Home Inspector (and anywhere else in North America)
  #2  
Old 4/23/09, 9:15 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: 2 prong receptacles

I call them out dated and recommend upgrade.
Also a good clue to look for those cloth covered wires.
Reply With Quote
  #3  
Old 4/23/09, 9:51 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: 2 prong receptacles

Unless you are absolutely sure that each receptacle is able to be grounded, don't recommend a replacement with a three pronged recept. An electrician may be needed to upgrade each branch circuit where a ground is needed.


Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #4  
Old 4/23/09, 11:14 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: 2 prong receptacles

Home inspectors call out defects. This system, unless observed in a new construction or addition, is not a defect.

Home inspectors do not recommend remedies to the defects that they point out in their reports. They recommend that they be repaired or replaced by a qualified contractor.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 4/23/09, 11:24 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: 2 prong receptacles

But you guys do mention the system as outdated....Yes?
Reply With Quote
  #6  
Old 4/23/09, 11:31 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 2 prong receptacles

Quote:
Originally Posted by pwancata View Post
Also, has anyone used the Ideal circuit analyzer 61-165. i'd like to get some feedback. Thanks
I don't leave home without it, in fact, I have three.

The three-light tester does not give enough information and should not be your only tool for receptacle testing.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 4/23/09, 11:48 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: 2 prong receptacles

Quote:
Originally Posted by relliott View Post
But you guys do mention the system as outdated....Yes?
I don't.

I will include a narrative that the two prong system is perfectly safe, will accommodate GFCI receptacles, and does not need to be replaced. I will mention the dangers caused by "adapters" and the possible inconvenience this system poses when using most modern day electrical appliances.

"Outdated" infers the need for replacement, which I do not recommend for anything that is not defective (with the exception of GFCI in wet areas).



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #8  
Old 4/23/09, 11:52 AM
jrivera's Avatar
jrivera jrivera is offline
Active Poster
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,339
Please Note: jrivera is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 prong receptacles

Quote:
Originally Posted by jbushart View Post
I don't.

I will include a narrative that the two prong system is perfectly safe, will accommodate GFCI receptacles, and does not need to be replaced. I will mention the dangers caused by "adapters" and the possible inconvenience this system poses when using most modern day electrical appliances.

"Outdated" infers the need for replacement, which I do not recommend for anything that is not defective (with the exception of GFCI in wet areas).
Good verbiage.

Mic
Reply With Quote
  #9  
Old 4/23/09, 12:13 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: 2 prong receptacles

http://www.nachi.tv/episode42


Scroll to 4:45, Joe covers this nicely, and taught me allot.
Reply With Quote
  #11  
Old 4/23/09, 12:32 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: 2 prong receptacles

Quote:
Originally Posted by jbushart View Post
I don't.

I will include a narrative that the two prong system is perfectly safe, will accommodate GFCI receptacles, and does not need to be replaced. I will mention the dangers caused by "adapters" and the possible inconvenience this system poses when using most modern day electrical appliances.

"Outdated" infers the need for replacement, which I do not recommend for anything that is not defective (with the exception of GFCI in wet areas).
So the whole idea of grounding was never needed?
Reply With Quote
  #12  
Old 4/23/09, 1:43 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: 2 prong receptacles

Quote:
Originally Posted by relliott View Post
So the whole idea of grounding was never needed?
2-prong outlets are not a defect. It is errant and misleading, on our part, to state or to infer otherwise.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #13  
Old 4/23/09, 2:52 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,281
Default Re: 2 prong receptacles

Quote:
Originally Posted by jbushart View Post
2-prong outlets are not a defect. It is errant and misleading, on our part, to state or to infer otherwise.

Home inspectors call out defects. This system, unless observed in a new construction or addition, is not a defect.

2-prong outlets are not a defect. It is errant and misleading, on our part, to state or to infer otherwise.

I agree with James on both quotes! Unless you are licensed to make that call and never worry about liability issues, I would stick with what a home inspector should report.
I often tell folks:

I am like the General Practitioner and the Plumber, Electrician, etc is like the Surgeon.

Everyone can separate the Doctor at the clinic and and the Surgeon at the hospital.
Reply With Quote
Find an InterNACHI certified New Hampshire Home Inspector (and anywhere else in North America)
  #14  
Old 4/23/09, 2:56 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: 2 prong receptacles

You guys may notice I used the term out of date.
Anybody catch me saying defect.?

Hmm it is a defect only in new construction.?

Want to take that statement back after someone please defines defect for me?
Reply With Quote
  #15  
Old 4/23/09, 3:09 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,281
Default Re: 2 prong receptacles

Quote:
Originally Posted by relliott View Post
You guys may notice I used the term out of date.
Anybody catch me saying defect.?

Hmm it is a defect only in new construction.?

Want to take that statement back after someone please defines defect for me?
Not disagreeing with you Bob. Just saying I stick with more along the line of James's approach. Never thought you said "defect" and yes it can be a defect in more than just new construction. I have wrote them up when they were defective but never simply because they were two pronged.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two prong receptacles. dryerson Electrical Inspections 20 6/27/08 3:01 AM
3 prong receptacle w/out equipment ground wire mbrown5 Electrical Inspections 4 8/24/07 1:55 AM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
2 Prong Receptacles dnasser Electrical Inspections 5 2/26/07 11:24 AM
open ground on 3 garage receptacles dnasser Electrical Inspections 14 10/30/06 5:53 PM


All times are GMT -4. The time now is 5:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts