I just inspected one unit of a 300 unit condo. There were no smoke detectors in the bedrooms, but there was a sprinkler system. There was one smoke detector in the hallway. Is that okay?
In the master bedroom closet there was an exposed incandescent light. I know in clothes closets they must be covered but this closet had no door. Is that a way around this requirement? I appreciate all input |
For the smoke detector you'll have to check with the AHJ--rules vary from here to there...
The bare bulb in the closet in not necessarily a problem--if there are no clothes or anything flammable within a couple of feet. Again, check with the AHJ. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
I don't do Smokes and CO detectors...
I just love the Massachusetts Smoke detector and Carbon Monoxide Regulations Fire departments are currently required to inspect smoke alarms when one-five unit homes are being sold and transferred. Sellers are responsible for obtaining a compliance certificate from their local fire dept. Starting last March 31, 2006 fire departments will be required to inspect all residences upon sale and transfer for carbon monoxide detectors. Maximum fees for separate or joint inspecting of CO alarms and smoke detectors are $50.00 for single-family homes or units (i.e. condo), $100.00 for 2-family dwellings, $150.00 for 3-6 unit dwellings and $500.00 for 6 or more unit buildings. |
David - I dont inspect them either, but it is good to know the requirements.
Here is a history of smoke detecor requirments. SMOKE DETECTORS 1973 The National Fire Protection Association recommends that smoke detectors be placed in each bedroom and home hallway. They also recommend that smoke detectors over 10 years of age be replaced as smoke detectors lose their sensitive and at 15 years 50% will have failed in place. The test button merely ensures that the battery and horn are functioning." , Detectors must be installed in hallways serving a sleeping room. Also, must be located a top of stairways where sleeping rooms are on an upper level. Must sound an alarm. (Section 1413) 1976, Added guest room of a lodging house, no other changes 1979, Requires a smoke detector when alterations, repairs or additions having a valuation of $1000.00 or more are made to an existing dwelling. Required that smoke detectors in new construction must be served by commercial power. In existing buildings the detector may be battery operated. (section 1413) 1982, Required that a smoke detector be placed in a basement with a stairway into the dwelling unit. The detector must sound an alarm audible in the sleeping areas. (Section 1210) 1982, No changes. (Section 1210) 1988, Specifically required smoke detectors on each level having a sleeping room. Where the ceiling height from the hall to sleeping room differs by 24 inches or more, then the detector must also be installed in the sleeping room. The alarm must be audible in all sleeping rooms. (Section 1210) 1991, Smoke detectors must be installed in the sleeping room as well as the hallway or area serving the sleeping room. Required battery backup when detectors are served by commercial power and low-battery signal must be included. (Section 1210) 1994, No changes, except exterior changes DO NOT require additional smoke detectors. (Section 310.9.1.4) P21. Section 316.1 Smoke detectors required. Smoke detectors shall be installed in each sleeping room, outside of each separate sleeping area in the immediate vicinity of the bedrooms and on each additional story of the dwelling, including basements and cellars but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels, a smoke detector need be installed only on the upper level, provided the lower level is less than one full story below the upper level, except that if there is a door between levels, then a detector is required on each level. All detectors shall be interconnected such that the actuation of one alarm will actuate all the alarms in the individual unit and shall provide an alarm which will be audible in all sleeping areas. All detectors shall be approved and listed and shall be installed in accordance with the manufacturer's instructions. 1994 B905.2 AUTOMATIC FIRE DETECTION - B905.2.1 Single-station or multiple-station smoke detectors shall be installed within every dwelling and every dwelling unit within an apartment house, condominium or townhouse, and every guest or sleeping room in a motel, hotel or dormitory shall be provided with an approved listed smoke detector, installed in accordance with NFiPA 74. Where more than one detector is required to be installed within an individual dwelling unit, the detectors shall be wired in such a manner that the actuation of one alarm will actuate all of the alarms in the individual unit. - B905.2.2 In dwellings and dwelling units, a smoke detector shall be mounted on the ceiling or wall at a point centrally located in the corridor or area giving access to each group of rooms used for sleeping purposes. Where the dwelling or dwelling unit contains more than one story, detectors are required on each story including basements, but not including uninhabitable attics, and shall be located in close proximity to the stairway leading to the floor above. - B905.2.3 In dwelling units with split levels and without an intervening door between the adjacent levels, a smoke detector installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level. - B905.2.4 Smoke detectors connected to a fire protective signaling alarm system shall be installed in accordance with NFiPA 72 and 72E. - B905.2.5 In dwelling and dwelling units, smoke detectors shall be hardwired into an AC electrical power source and shall be equipped with a monitored battery backup in all new construction. A monitored battery power source shall be permitted in existing construction. 2006 IRC SECTION R313 SMOKE ALARMS R313.1 Smoke detection and notification. All smoke alarms shall be listed in accordance with UL 217 and installed in accordance with the provisions of this code and the household fire warning equipment provisions of NFPA 72. Household fire alarm systems installed in accordance with NFPA 72 that include smoke alarms, or a combination of smoke detector and audible notification device installed as required by this section for smoke alarms, shall be permitted. The household fire alarm system shall provide the same level of smoke detection and alarm as required by this section for smoke alarms in the event the fire alarm panel is removed or the system is not connected to a central station. R313.2 Location. Smoke alarms shall be installed in the following locations: 1. In each sleeping room. 2. Outside each separate sleeping area in the immediate vicinity of the bedrooms. 3. On each additional story of the dwelling, including basements but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level. When more than one smoke alarm is required to be installed within an individual dwelling unit the alarm devices shall be interconnected in such a manner that the actuation of one alarm will activate all of the alarms in the individual unit. |
Wow....William provided some GREAT information their so I will just address the light in the closet...lol.....
You stated it had no door but you did not state the proximity of the shelves and so on to the exposed light in the closet...are their cloth hangers or hanging rods for such items....... But either way open bulb lampholders are not allowed in cloth closets....so if you have a cloth hanging rod inside......then open bulb lampholder is not supposed to be in there...period. Ala...410.8(c)....of the infamous minimum safety code.. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
Paul--I agree that the NEC says no uncovered bulbs. I also agree with the possibility of a safety factor. However, in my travels around SW Ohio I have found many AHJs who don't consider it to be unsafe if there is an adequate space between the bulb and combustibles. If an inspector questions the safety of the bulb in the report, and the client wants the seller to do something about it...the inspector has placed himself squarely between the two--not a really good thing. I might mention the possibilty of an unsafe condition, but defer to the AHJ for a final determination. I'd rather the AHJ had the liability. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
You don't need to get in the code fight. A compliant luminaire is less than $10. Note it as a concern and move on, the same way you would with GFCIs in a house that predates the requirement.
Agreed....having an AHJ worry about this is not solving the potential issue as the NEC is a minimum safety standard....and it is clear that no open bulbs are to be in the cloth closets.....as greg stated you can get a simple mason jar fixture for less than $ 10.00 bucks to reduce the safety concern.
AS for the AHJ.....simple statement I would use is..." You can't fix stupid ".. Actually thats the sad thing.....hard to know WHAT to enforce when as you say some municples overlook things based on their own opinion. Interpretation is one thing....choosing to ignore the violation is another. I would agree...if you are going to suggest GFCI's it would not hurt to suggest the open bulb be covered....and if you did get any FLACK from the AHJ on that.....tell him to re-read his NEC....but then again you are the one who needs to err on the side of safety for your client. Just some suggestions fella.....thats all......don't kill the messengers... ![]() Here ya go.....I get these round ones for $ 3.99 a light.... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 3/23/07 at 1:24 AM.. |
Thanks for the info guys. I called the dept of building and they told me that they don't need smoke alarms if there is a sprinkler system. Personally, I think that is very stupid. As for the light, it is good distance away from the top shelf. The contractor didn't want me to touch anything so I was looking for every little thing to break there balls.
In the spirit of safety and to cover my own but, I always check all fire and or smoke heads. If they dont work I transfer them to my inopperable items page.
I'm a New member this is one reason I joined to be better inform on the inspection world Thanks
Welcome!!
Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
And how do you clean up when they DO operate? |
| Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America) |
Again I may be wrong as I dont have my IBC or IRC handy right now but i dont see where in regards to the dwelling aspect that a sprinkler system removes that single or multiple station smoke detectors. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
Does the current standard on transfer of sale require the detectors to be in bedrooms as well as hallways/stairways? I know this is true for Mobile/Manufactured homes but have had alot of push back when I call them out for residential homes.
| FetchReport Questions for NIck | lcapaul | Miscellaneous Discussion for Inspectors | 51 | 6/12/07 1:53 PM |
| standard questions | rbyrd | General Inspection Discussion | 16 | 11/25/06 1:24 PM |
| Some good questions that always need answers | jtedesco1 | Electrical Inspections | 5 | 6/16/06 10:10 PM |
| Crawlspace questions?? | dmacy | Structural Inspections | 12 | 3/9/06 10:12 PM |