Default 2 Questions for The Price of One

Alright got to questions.

#1) Did a reinspection to day where I noted double taps in a panel. There solution, which is pictured, was to remove the double taps, wirenut them together and pig tail them with one single wire back to the breaker. Comments needed..

#2) On an inspection today found a panel (find a lot of them in this particular neighborhood) that had no ground wire from the panel or meter that attached to a ground rod. The realtor made the comment "Was it code at the time it was built?" Anyother time I have called this out they have fixed it without question. When did the NEC require a ground wire and what would be a good replay next time some realtor makes that comment.

Thanks in advance!
Attached Thumbnails
2-questions-price-one-look.jpg  



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #2  
Old 4/25/06, 11:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 2 Questions for The Price of One

#1) Perfectly acceptable, although sloppy.

#2) I have a 1940 NEC that shows a requirement for a grounding electrode.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 4/26/06 at 12:21 AM..
Reply With Quote
  #3  
Old 4/26/06, 6:30 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by psmothers
The realtor made the comment "Was it code at the time it was built?" Anyother time I have called this out they have fixed it without question. When did the NEC require a ground wire and what would be a good replay next time some realtor makes that comment.
There's a fine line between Code and Safety. Safety features (to any home) need immediate attention and do not get grandfathered in because it wasn't code at the time.

Complete safety (of my clients) override any code in my book.

Let's say that the GEC just recently got adopted in 2003 due to related deaths. A building that was built in 1998, does not require a GEC?Attachment 3120

Last edited by dvalley; 10/7/07 at 4:41 PM..
Reply With Quote
  #4  
Old 4/26/06, 8:01 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: 2 Questions for The Price of One

I'd just recommend the grounding electrode for enhanced safety and let them do what they will. It leaves the code out of it.
Reply With Quote
  #5  
Old 4/26/06, 8:30 AM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

[quote=jpope]#1) Perfectly acceptable, although sloppy.

I don't understand this. I was under the impression that if you double tap you are most likely allowing more than 12 devices per circuit. Sooooo, if a double tap is not allowed for this reason, how would pigtailing 2 circuits to the same breaker be "perfectly acceptable"
Larry
Reply With Quote
  #6  
Old 4/26/06, 9:04 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 2 Questions for The Price of One

Larry,

Maybe it is a canada thing...BUT the NEC does not mandate the number of outlets or luminaries on a given circuit. That MATH is left to the electrical contractor to use CORRECT wisdom......WE hope anyway.

Doing the SPLICE removes the issue of double tapping..and as you mentioned you still have all the items on that circuit on the same OCPD...just not in a double tap situation......

Hope that helps any...



Paul W. Abernathy
Reply With Quote
  #7  
Old 4/26/06, 12:20 PM
James D Mosier James D Mosier is offline
New User
 
Join Date: Jan 2004
Posts: 7
Please Note: James D Mosier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

Pigtailing two circuits inside the panel is little different than connecting them in a junction box one foot away (or anywhere really).
Reply With Quote
  #8  
Old 4/26/06, 1:28 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by James D Mosier
Pigtailing two circuits inside the panel is little different than connecting them in a junction box one foot away (or anywhere really).
Right, but the problem of double tapping is that the lug on the breaker isn't (usually) designed for accepting two wires, so this solution takes care of the problem. Just think of the enclosure as a junction box.
Reply With Quote
  #9  
Old 4/26/06, 10:58 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

so basicly the double tap issue isn't for the number of items possible on a circuit (let's face it, we all have a power strip with at least 4 things plugged into on outlet, or one of those 6 into 2 boxes) but for the fact that the screw on the breaker isn't designed for it.
Reply With Quote
  #10  
Old 4/26/06, 11:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by Jay Moge
so basicly the double tap issue isn't for the number of items possible on a circuit (let's face it, we all have a power strip with at least 4 things plugged into on outlet, or one of those 6 into 2 boxes) but for the fact that the screw on the breaker isn't designed for it.
You got it

ding, ding, ding. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 4/26/06, 11:15 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

yeeeeeee haaaaaaaa. you can mail me my cash prize.
Reply With Quote
  #12  
Old 5/2/06, 7:22 PM
dspencer's Avatar
dspencer dspencer is offline
Active Poster
 
Join Date: Dec 2004
Location: Marengo, Oh
Posts: 178
Please Note: dspencer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Exclamation Re: 2 Questions for The Price of One

# 1 a solution.. No. The service box may not be used as a junction box. Recommend a mini double breaker installed is the proper fix if no room permits an additional breaker..
Reply With Quote
  #13  
Old 5/2/06, 7:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by dspencer
# 1 a solution.. No. The service box may not be used as a junction box.
Do you have a reference to support that statement?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 5/2/06, 7:50 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by dspencer
# 1 a solution.. No. The service box may not be used as a junction box. Recommend a mini double breaker installed is the proper fix if no room permits an additional breaker..
Not in Tn, it is acceptable.. And I believe the nec allows it also.........
Reply With Quote
  #15  
Old 5/2/06, 11:30 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2 Questions for The Price of One

Quote:
Originally Posted by dspencer
# 1 a solution.. No. The service box may not be used as a junction box. Recommend a mini double breaker installed is the proper fix if no room permits an additional breaker..
Dude you're way off base with that statement. Splicing is allowed in panels and limited only by conductor fill area. It's in the NEC. Also, many panels are not listed to support "mini twins" and the ones that are usually only allow a limited section of them, and are usually so small they are already full up on twins.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale Sidekick 3 For A Cheap Price Of ...$180usd tonystores Structural Inspections 3 10/31/06 3:17 PM
For Sale Sidekick 3 For A Cheap Price Of ...$180usd tonystores Interior Inspections 6 10/29/06 5:35 PM
For Sale Nokia N95 At Just $300usd tonystores Electrical Inspections 8 10/28/06 3:39 PM
For Sale Nokia N80 For A Cheap Price Of $150usd tonystores General Inspection Discussion 1 10/27/06 11:34 PM
For Sale Sidekick 3 For A Cheap Price Of ...$180usd tonystores Legislation, Licensing & Legal Issues for Inspectors 1 10/27/06 11:31 PM


All times are GMT -4. The time now is 4:33 AM.