Default 2-Wire Service - 2 Hots, No Neutral

The outbuilding had its own 200 amp service panel (underground feed wires) mounted at the exterior on a pole. I could peek at the meter feed wires through a crack in the panel gutter... there were only two 4/0 aluminum wires in the gutter. The service panel had its own ground rod. There were 120 volt breakers in both the service panel and the sub panel. It appears that the only path back to the transformer for the neutral current is through the earth. The lights and outlets at the outbuilding were operational.

I see the following issues:

-Missing Neural at service feed
-Abandoned wires at service panel
-Combined grounds and neutrals at sub-panel

Does anyone see anything else. I have never seen a missing neutral before.
Attached Thumbnails
2-wire-service-2-hots-no-neutral-p1190249.jpg   2-wire-service-2-hots-no-neutral-p1190245.jpg   2-wire-service-2-hots-no-neutral-p1190246.jpg   2-wire-service-2-hots-no-neutral-p1190252.jpg  
Reply With Quote
  #2  
Old 8/8/06, 9:52 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-Wire Service - 2 Hots, No Neutral

That is a feed through meter main. The neutral is that bar along the right side. Just next to the vertical gutter.

The neutral connection is above in the meter section and the bar is the conductor down into the panel section.
That 200a breaker is for a feed out to another panel.
As you can see, there is only enough spaces for six single pole, or three double pole breakers so no single main is required.

This is a very common installation for new homes under construction. You can tap a few temp receptacle circuits off the panel and then just feed the full 200 amps out to the house when needed.
Reply With Quote
  #3  
Old 8/8/06, 9:55 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-Wire Service - 2 Hots, No Neutral

A real problem is the sub-panel.
Since a 4-wire feeder was run the neutral bar does NOT get bonded to the enclosure and a separate ground bar is required. The neutral bar remains isolated.
Reply With Quote
  #4  
Old 8/9/06, 3:33 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 327
Default Re: 2-Wire Service - 2 Hots, No Neutral

The service lateral wires come up from the ground through a 2" conduit and enter the panel gutter indicated by the arrows. I was able to look into the opening (circled) and confirm that there are only two service wires. There is no neutral wire coming from the transformer. Can the metal conduit be used as the neutral conductor? I am almost certain that it can't. This does not look right to me.
Attached Thumbnails
2-wire-service-2-hots-no-neutral-service-panel.jpg  
Reply With Quote
  #5  
Old 8/9/06, 11:37 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 2-Wire Service - 2 Hots, No Neutral

Howdy Fella's....

1.) If you are 100% certain that only (2) 4/0AL are entering into that combo unit then I would recommend a call to POCO for more clarrification on this as sometimes pictures just dont do something justice.

2.) Speedy is correct on the bonding issue at the "Remote Panel " as I believe you can see the green bonding screw within the enclosure on that image.

We do see alot of feed through panels here as well and not always for trailers....in some garage to house installations they are used as well.

My concern is.....and maybe it is just way to early in the AM for me to be thinking as I had a rough night last night.......If it is your belief they are using the conduit as the neutral to carry the unbalanced loads...that would be wrong......are you 100% sure their was no smaller wire behind the others because you know the neutral can be downsized per the NEC.

If you truly have 240V capacity their...and you KNOW this.......and only (2) SE Conductors.....Yes, I would say it is wrong but again you have to see REALLY into the gutter...

AS Speedy said....the bar on the right is the carry down for the Neutral.....and THIS is where the bonding should take place....notice the GEC....so all in all based on the issue with the "Remote Panel" and the LACK of what you dont see........mark it to be evaluated furthur because it does not conform to the NORMAL standards.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 8/9/06, 12:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2-Wire Service - 2 Hots, No Neutral

The other thing that bothers me a little is the neutral is connected to the grounding bus, not the neutral lugs on the right. You are sending neutral current through the bonding jumper. Not a real big deal with this design but easy to fix.
I agree with Pete. The grounded conductor from the service probably terminates in the meter base and is connected to the neutral bus on the right.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 3:40 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 6:21 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts