#1
|
|||
|
|||
|
Hey, i have a question for all you pros. If you have the bathroom on a 20amp circuit breaker with 12-2 wire, does the outlets have to be 20 amp outlets or is it ok to use 15 amp outlets? I understand the 20 amp outlet has a horizontal added plug for 20 amp tools. Is it code or what?
Thanks Andy Bishop |
|
#2
|
||||
|
||||
|
Andy,
The National Electrical Code, in article 210.21 (B) 1, 2, and 3, describes the requirements of single and multiple receptacles on a circuit. The use of multiple 15 amp receptacles on a 20 amp circuit is permitted. A duplex receptacle is considered as multiple receptacles and is therefore permissible to use as the single, or one of several, multiple type receptacles on the circuit. Part of the UL listing for the 15 amp receptacles is that they are capable of feeding through the 20 amp circuit, the primary difference between 15 and 20 amp receptacles being the faceplate configuration. Receptacles rated higher than the circuit rating may not be used, so 20 amp receptacles are not permitted on a 15 amp circuit. |
|
#3
|
||||
|
||||
|
One 15 Amp receptacle on a 20 Amp circuit is a no-no.
|
|
#4
|
|||
|
|||
|
Thanks Dave, that helps. What about this ONE thing. So if you had a bathroom with one outlet, you can't have that on a 20 amp circuit? But can you run 12-2 and have a 15 amp breaker and 15 amp outlet?
I and some friends just wired up my buddies lower level/basement. I have 20 amp on the bathroom and wet bar, seperate circuits. We put the two bathroom outlets on the same circuit as the bedroom outlets. The lights are on a 15 amp circuit and also the outlets in the main living room and lights are 15 amp but seperate circuits. I think i did that right? Thanks Andy |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bathrooms, laundries and kitchens(pantry dining room etc) require 20 amp receptacle circuits with no other outlets. You can't serve other rooms from these circuits.
You can put a duplex 15a receptacle device on a 20a circuit. |
|
#6
|
||||
|
||||
|
Andy,
All set? |
|
#7
|
|||
|
|||
|
One confused piece is, can i or can i not have the bathroom outlets (2) on the same circuit as two bedrooms?
|
|
#8
|
||||
|
||||
|
No!
Bathrooms must be on their own circuit. |
|
#9
|
|||
|
|||
|
Quote:
Up a few posts, Greg said: "You can't serve other rooms from these circuits." |
|
#10
|
|||
|
|||
|
Yes, i heard that i just choose not to hear it.
Now i have to run another wire all the way accross to the other side of the house for the bedroom outlets! DAMN! You guys are the best. Thanks |
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You probably have to put that bedroom on an AFCI anyway (if you are on 1999 or later code and 210.12 (B) is not excluded) so it is not a total waste
|
|
#12
|
||||
|
||||
|
Keep in mind now you can have a single 20A circuit feeding ALL the bathrooms in the house....as long as it only feeds the bathroom receptacles...
So in closing...if you have a house with 3 bathrooms...you can have one 20A circuit feeding the first bathroom, then looping to the recept. in the next bathroom and so on to the 3rd bathroom....BUT only those recepts can be on that circuit.... Hope that clears that up for you. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#13
|
||||
|
||||
|
Quote:
|
|
#14
|
||||
|
||||
|
Please Note:
dspencer is a non-member guest and is in no way affiliated with InterNACHI or its members.
spa is deicated...also GFCI and the GFCI can not be within reach of tub!
|
|
#15
|
||||
|
||||
|
Richard....that is correct.....kinda in a nutshell without getting too specific and causing brain freeze.
Just for the record...Darren can you show me the code section on that reference? Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| ungrounded outlets! | gmaher | Electrical Inspections | 29 | 6/10/07 11:58 PM |
| Properly Testing GFCI Outlets | tchristopher | Electrical Inspections | 17 | 3/17/07 12:19 PM |
| Replacing 2-prong outlets with GFCI outlets | kshepard | Electrical Inspections | 7 | 6/24/06 7:58 AM |
| Two prong outlets and GFCI's | crichiii | Electrical Inspections | 8 | 3/15/06 11:41 PM |