Default 20 amp breaker for water heater

20 amp breaker, with 10 gauge wire, installed on 50 gal. Whirlpool heater (upper left breaker).

Comments?

Thanks in advance.
Attached Thumbnails
20-amp-breaker-water-heater-img_8884.jpg  
Reply With Quote
Need a home inspection in Georgia? Check out InterNACHI's listing of Georgia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/2/12, 8:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,136
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 20 amp breaker for water heater

Probably too small but what is the heater wattage?
Reply With Quote
  #3  
Old 10/2/12, 8:08 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 2,348
Send a message via AIM to jfrederick
Default Re: 20 amp breaker for water heater

Quote:
Originally Posted by Robert Meier View Post
Probably too small but what is the heater wattage?
I'm assuming 4500, no? Isn't that typical for newer, 50 g electric? Not 100% sure, though.
Reply With Quote
  #4  
Old 10/2/12, 8:38 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,136
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 20 amp breaker for water heater

If it's 4500 then the 20 amp will work but it won't be code compliant. A water heater of this type is required to be considered a continuous load meaning that the branch circuit needs to be calculated at 125% of the heater's rated ampacity.

4500/240 = 18.75 amps, will work on a 20 amp OCPD but,
18.75*125% = 23.4 amps, requires a 25 or 30 amp circuit.
Reply With Quote
  #5  
Old 10/2/12, 2:53 PM
Mary Ann Chiquete's Avatar
Mary Ann Chiquete Mary Ann Chiquete is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Buckeye, Arizona
Posts: 227
Default Re: 20 amp breaker for water heater

Quote:
Originally Posted by Robert Meier View Post
If it's 4500 then the 20 amp will work but it won't be code compliant. A water heater of this type is required to be considered a continuous load meaning that the branch circuit needs to be calculated at 125% of the heater's rated ampacity.

4500/240 = 18.75 amps, will work on a 20 amp OCPD but,
18.75*125% = 23.4 amps, requires a 25 or 30 amp circuit.
Great information Robert, thanks.





Mary Ann Chiquete
Serving the entire Phoenix Metro Area
623-399-7962
www.benchmarkazinspect.com

benchmarkaz@gmail.com

Reply With Quote
  #6  
Old 10/2/12, 3:10 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,787
Default Re: 20 amp breaker for water heater

Here's a good link, I like it anyway.

How to figure Volts-Amps-Watts for residential water heater






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #7  
Old 10/2/12, 3:30 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,136
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 20 amp breaker for water heater

Quote:
Originally Posted by mchiquete View Post
Great information Robert, thanks.

You're welcome, here's a few NEC sections to accompany my last post:

Quote:
422.11 Overcurrent Protection. Appliances shall be pro-
tected against overcurrent in accordance with 422.11(A)
through (G) and 422.10.
(E) Single Non–motor-Operated Appliance. If the branch
circuit supplies a single non–motor-operated appliance,
the rating of overcurrent protection shall comply with the
following:
(1) Not exceed that marked on the appliance.
(2) Not exceed 20 amperes if the overcurrent protection
rating is not marked and the appliance is rated
13.3 amperes or less; or
(3) Not exceed 150 percent of the appliance rated current if
the overcurrent protection rating is not marked and the
appliance is rated over 13.3 amperes. Where 150 per-
cent of the appliance rating does not correspond to a
standard overcurrent device ampere rating, the next
higher standard rating shall be permitted.
Quote:
422.13 Storage-Type Water Heaters. A fixed storage-type
water heater that has a capacity of 450 L(120 gal) or less shall
be considered a continuous load for the purposes of sizing
branch circuits.
Reply With Quote
  #8  
Old 10/3/12, 6:38 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 600
Default Re: 20 amp breaker for water heater

My 40 gallon has been on a two pole 20 for more than 5 years with no problem.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #9  
Old 10/3/12, 9:23 AM
James T. McGrail's Avatar
James T. McGrail James T. McGrail is offline
InterNACHI Member
 
Join Date: Jul 2012
Location: Alabama
Posts: 562
Default Re: 20 amp breaker for water heater

Great link !
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
I cant even guess what this is jjimenez Plumbing Inspections 11 4/6/12 8:38 AM
What wire size and breaker for heater??? Dan Bolton Inspecting HVAC Systems 3 12/17/10 8:51 PM
Water heater breaker sizing rgallahorn Electrical Inspections 15 9/8/07 2:57 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 10:36 AM

All times are GMT -4. The time now is 5:15 AM.
no new posts