Can anyone tell me why a 20 amp receptacle (t-shaped neutral) can't be used on a 15 amp service (14AWG)?
I can understand why a 15 amp receptacle shouldnt be used on a 20 amp (12AWG) service but a 20 amp receptacle should be able to handle the load safely. Is this just a misleading issue for a 20 amp appliance that may lead to a nuisance trip? |
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#3
|
||||
|
||||
|
Please Note:
Mark Nicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
http://ecatalog.squared.com/pubs/Cir...ers/910-04.pdf |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
If there is more than one "receptacle" on a circuit, and a duplex receptacle is considered two in this case, then you CAN use 15A receptacles on a 20A circuit. Simple as that. |
|
#6
|
||||
|
||||
|
Attached is a copy of the NEC table on receptacle ratings. Note that as previously mentioned for a 20A circuit you can install either 20A receptacles, or 15A receptacles as long as there is more than one. But for a 15A circuit, only 15A receptacles should be installed ...
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#7
|
||||
|
||||
|
Hey Robert,
Haven't seen you in a while. Always appreciate you inputs. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What do you think? Can this work for you? | jtedesco1 | Electrical Inspections | 21 | 2/26/11 2:00 PM |
| Where is it written.... | bgromicko | General Inspection Discussion | 21 | 1/19/08 9:02 PM |