| Electrical Inspections Contains discussions about electrical systems. This includes receptacles, panels, wiring, etc. |
![]() |
|
|
LinkBack | Thread Tools |
|
#1
|
||||
|
||||
|
Is this bad?......
![]() This is the only picture I could get to show the temperature of the "Wire" just before the breaker. Damn new camera!...didn't get the macro figured out before it got dark (flash city). I had readings up to 215 degrees on the wire, which has visibly burnt insulation. Connected to the top leg of a 30 Amp breaker feeding a heat pump. The breaker was 65 degrees, it was 54 degrees outside about an hour ago. Loose wire? |
|
#2
|
||||
|
||||
|
Yikes.
|
|
#3
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
![]() |