Is it acceptable to have 1/0 wire SE on a 200 amp entry breaker?
Reply With Quote
  #2  
Old 4/20/07, 8:09 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp panel with 1/0 wire

So Peter, are you saying that between the meter and the Main Disconnect you have 1/0? If so, that would be too small (2/0 Copper or 4/0 Aluminum----typically). Some times I see this where you have a 200 amp panel with a 200 amp disconnect but it is a Remote Distribution Panel with the "proper" size disconnect located at the Meter.
Reply With Quote
  #3  
Old 4/20/07, 8:18 PM
Peter Hughes Peter Hughes is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Garland, TX
Posts: 126
Default Re: 200 amp panel with 1/0 wire

Yes, That is my question, and I see it on home that were built in the 1990s.

I never see it after 2000.
Reply With Quote
  #4  
Old 4/20/07, 8:22 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp panel with 1/0 wire

In my area the nuetral can still be a 1/0. Did you check all the wires or just one?
Reply With Quote
  #5  
Old 4/20/07, 8:36 PM
Peter Hughes Peter Hughes is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Garland, TX
Posts: 126
Default Re: 200 amp panel with 1/0 wire

I checked all to be sure
Attached Thumbnails
200-amp-panel-1-0-wire-s_wilson-031.jpg  
Reply With Quote
  #6  
Old 4/20/07, 8:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp panel with 1/0 wire

I thought it might be useful to plop down a copy of Table 310.15(B)(6) from the NEC. This is the table that lists what gauge of conductor of copper and aluminium corresponds with what size residential service. Maybe you already have this stuff, but here it goes anyhow:



In the instance of this thread, if you see a 1/0 copper terminated on a service overcurrent protection device greater than 175 amps, you have a problem on your hands.

If that 1/0 copper has some other protective device at it's starting end, rated 175 amps or less, then it's okay. In that case, the 200 amp breaker would be nothing more than a disconnect that also happens to be a 200 amp breaker.
Reply With Quote
  #7  
Old 4/20/07, 9:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp panel with 1/0 wire

even better answer....can 1/0 be for 200A....simple answer is NO...because if it is SE ( not SER ) it would not have a disconnect ahead of it...unless they just SCREWED it all up....



Paul W. Abernathy
Reply With Quote
  #8  
Old 4/20/07, 10:57 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp panel with 1/0 wire

Quote:
Originally Posted by pabernathy
...because if it is SE ( not SER ) it would not have a disconnect ahead of it...
SE is the general class of cable, which includes many cable types such as SEU, SER, and SEA.
Reply With Quote
  #9  
Old 4/21/07, 12:43 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp panel with 1/0 wire

Yeah but I think he is talking about simple SE.....(3 conductors ) and not 4 as in remote distribution panel...could be wrong however



Paul W. Abernathy
Reply With Quote
  #10  
Old 4/21/07, 3:18 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 200 amp panel with 1/0 wire

Quote:
Originally Posted by pabernathy
even better answer....can 1/0 be for 200A....simple answer is NO...because if it is SE ( not SER ) it would not have a disconnect ahead of it...unless they just SCREWED it all up....
Quote:
Originally Posted by phughes
Is it acceptable to have 1/0 wire SE on a 200 amp entry breaker?
In my area home inspectors have no business checking the size of wire.
This is beyond the scope of a home inspector .
I wonder why a home inspector would even be probing in a section of the service to look at the cables .
This service was originally inspected and passed for usage.
Really why should I be doughting the original installation.
Where does this stop .
I do a visual inspection of all ready accesssable parts of the home .
The same I do not take an air conditioner apart to see if the AC mechanic has installed it correctly example did he use the correct solder lead or silver.
The same I do not check to see if the plumber used lead solder or lead free solder.
As a home Inspector I feel this is not my job and I do not check the size of feeders in a service.
Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #11  
Old 4/21/07, 5:47 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: 200 amp panel with 1/0 wire

Quote:
Originally Posted by rcooke
In my area home inspectors have no business checking the size of wire.
This is beyond the scope of a home inspector .
I wonder why a home inspector would even be probing in a section of the service to look at the cables .
This service was originally inspected and passed for usage.
Really why should I be doughting the original installation.
Where does this stop .
I do a visual inspection of all ready accesssable parts of the home .
The same I do not take an air conditioner apart to see if the AC mechanic has installed it correctly example did he use the correct solder lead or silver.
The same I do not check to see if the plumber used lead solder or lead free solder.
As a home Inspector I feel this is not my job and I do not check the size of feeders in a service.
Roy Cooke
You're joking right?

Are you telling us that you do not move the panel cover to;
1. look at the circuit breakers and wiring to see what kind of condition
they are in?
2. To see if they are any double tapps?
3. To see if a smaller gauge wire is inserted into a larger sized circuit
breaker?
4. To see if they has been any arcing?
5. To see if there has been any water seepage into the panel box?

I could go on and on, the list is endless!

I hope I have misread your statements and or miss understood your meaning!



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #12  
Old 4/21/07, 8:25 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 200 amp panel with 1/0 wire

Quote:
Originally Posted by fcarrio
You're joking right?

Are you telling us that you do not move the panel cover to;
1. look at the circuit breakers and wiring to see what kind of condition
they are in?
2. To see if they are any double tapps?
3. To see if a smaller gauge wire is inserted into a larger sized circuit
breaker?
4. To see if they has been any arcing?
5. To see if there has been any water seepage into the panel box?

I could go on and on, the list is endless!

I hope I have misread your statements and or miss understood your meaning!
Please read what I said unless our main panels are different then ours
the main breaker is still covered when the the lower section is opened .
No where did I talk about Double taps ,circuit breakers,smaller gauge wire,or water seepage ..
I was talking about the main feed and nothing else.
I again reiterate I do not think many if any home inspectors should be going into see what size the main feeds are.
I hope you have been reading some of the electrical questions on this BB and you have seen how little knowledge many home inspectors have on electricity.
I do think I have a reasonable electrical knowledge maybe more then you .
No I was not joking not a little bit.
Those in power in Canada are trying to stop HIs from even looking in the lower section of the panel.
Do you yourself really think all Home inspectors are qualified to throughly inspect the main electrical panel???????

Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #13  
Old 4/21/07, 9:01 AM
Peter Hughes Peter Hughes is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Garland, TX
Posts: 126
Default Re: 200 amp panel with 1/0 wire

The only reason I questioned the 1/0 was becasue on one inspection that I pointed this out their electrician said it was OK to go one size breaker larger than the rating of the wire.

So I wondered if anyone on NACHI had heard such a thing but based on the answers they have not.
Reply With Quote
  #14  
Old 4/21/07, 9:36 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp panel with 1/0 wire

2.7. Electrical
I. The inspector shall inspect:
A. The service line.
B. The meter box.
C. The main disconnect.
D. And determine the rating of the service amperage.
E. Panels, breakers and fuses.
F. The service grounding and bonding.
H. A representative sampling of switches, receptacles, light fixtures, AFCI receptacles
I. And test all GFCI receptacles and GFCI circuit breakers observed and deemed to be GFCI's during the inspection.
I. And report the presence of solid conductor aluminum branch circuit wiring if readily visible.
J. And report on any GFCI-tested receptacles in which power is not present, polarity is incorrect, the receptacle is not grounded, is not secured to the wall, the cover is not in place, the ground fault circuit interrupter devices are not properly installed or do not operate properly, or evidence of arcing or excessive heat is present.
K. The service entrance conductors and the condition of their sheathing.
L. The ground fault circuit interrupters observed and deemed to be GFCI's during the inspection with a GFCI tester.
M. And describe the amperage rating of the service.
N. And report the absence of smoke detectors.
O. Service entrance cables and report as in need of repair deficiencies in the integrity of the insulation, drip loop, or separation of conductors at weatherheads and clearances.

Roy, while the guy has a specific question on the rating I think it is VERY much an issue where they DO have to comment on the size of the service conductors......How would they comply to the SOP at the least if they did not forumulate the size of this service based on the important factors...Panel Rating, Conductor Size and OCPD size....and using them to define the service size...ignoring the size of the SE conductors would be simply put...wrong.



Paul W. Abernathy
Reply With Quote
  #15  
Old 4/21/07, 9:41 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 200 amp panel with 1/0 wire

I guess that is just another example of the differences between our two countries .
Thanks Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts