Is it acceptable to have 1/0 wire SE on a 200 amp entry breaker?
|
|
#2
|
||||
|
||||
|
Please Note:
cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
So Peter, are you saying that between the meter and the Main Disconnect you have 1/0? If so, that would be too small (2/0 Copper or 4/0 Aluminum----typically). Some times I see this where you have a 200 amp panel with a 200 amp disconnect but it is a Remote Distribution Panel with the "proper" size disconnect located at the Meter.
|
|
#3
|
|||
|
|||
|
Yes, That is my question, and I see it on home that were built in the 1990s.
I never see it after 2000. |
|
#4
|
||||
|
||||
|
Please Note:
bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
In my area the nuetral can still be a 1/0. Did you check all the wires or just one?
|
|
#5
|
|||
|
|||
|
I checked all to be sure
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I thought it might be useful to plop down a copy of Table 310.15(B)(6) from the NEC. This is the table that lists what gauge of conductor of copper and aluminium corresponds with what size residential service. Maybe you already have this stuff, but here it goes anyhow:
![]() In the instance of this thread, if you see a 1/0 copper terminated on a service overcurrent protection device greater than 175 amps, you have a problem on your hands. If that 1/0 copper has some other protective device at it's starting end, rated 175 amps or less, then it's okay. In that case, the 200 amp breaker would be nothing more than a disconnect that also happens to be a 200 amp breaker. |
|
#7
|
|||
|
|||
|
even better answer....can 1/0 be for 200A....simple answer is NO...because if it is SE ( not SER ) it would not have a disconnect ahead of it...unless they just SCREWED it all up....
Paul W. Abernathy |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
|||
|
|||
|
Yeah but I think he is talking about simple SE.....(3 conductors ) and not 4 as in remote distribution panel...could be wrong however
Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Quote:
Quote:
This is beyond the scope of a home inspector . I wonder why a home inspector would even be probing in a section of the service to look at the cables . This service was originally inspected and passed for usage. Really why should I be doughting the original installation. Where does this stop . I do a visual inspection of all ready accesssable parts of the home . The same I do not take an air conditioner apart to see if the AC mechanic has installed it correctly example did he use the correct solder lead or silver. The same I do not check to see if the plumber used lead solder or lead free solder. As a home Inspector I feel this is not my job and I do not check the size of feeders in a service. Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#11
|
||||
|
||||
|
Quote:
Are you telling us that you do not move the panel cover to; 1. look at the circuit breakers and wiring to see what kind of condition they are in? 2. To see if they are any double tapps? 3. To see if a smaller gauge wire is inserted into a larger sized circuit breaker? 4. To see if they has been any arcing? 5. To see if there has been any water seepage into the panel box? I could go on and on, the list is endless! I hope I have misread your statements and or miss understood your meaning! Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#12
|
||||
|
||||
|
Quote:
the main breaker is still covered when the the lower section is opened . No where did I talk about Double taps ,circuit breakers,smaller gauge wire,or water seepage .. I was talking about the main feed and nothing else. I again reiterate I do not think many if any home inspectors should be going into see what size the main feeds are. I hope you have been reading some of the electrical questions on this BB and you have seen how little knowledge many home inspectors have on electricity. I do think I have a reasonable electrical knowledge maybe more then you . No I was not joking not a little bit. Those in power in Canada are trying to stop HIs from even looking in the lower section of the panel. Do you yourself really think all Home inspectors are qualified to throughly inspect the main electrical panel??????? Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#13
|
|||
|
|||
|
The only reason I questioned the 1/0 was becasue on one inspection that I pointed this out their electrician said it was OK to go one size breaker larger than the rating of the wire.
So I wondered if anyone on NACHI had heard such a thing but based on the answers they have not. |
|
#14
|
|||
|
|||
|
2.7. Electrical
I. The inspector shall inspect:A. The service line. Paul W. Abernathy |
|
#15
|
||||
|
||||
|
I guess that is just another example of the differences between our two countries .
Thanks Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |