Quote:
Never read that in the codes. (about the using a breaker size one larger tan the rating of the wire) I think your electrician was misinformed. Roy I was surprised to find out that in Canada the HI's don't inspect the electrical panel with the deadfront cover removed. Here I find so many home owner produced safety hazards inside panels that it is unreal. Especially when it comes to home owner installed distribution panels. If I were a home buyer I would want to know if these conditions existed in the home I am about to purchase and move my family into. Just the day before yesterday I found where a homeowner wanted some more space in a panel for outlets in a garage. The owner removed the 10-2 cable from a 30 amp breaker and double tapped it to a 50 amp breaker, and then proceeded to install the garage outlets (14-2 cable) two circuits, on the 30 amp breaker. Might as well have just double tapped everything at the SEC lugs....it is just about the same result. Last edited by hmiller; 4/21/07 at 9:46 AM.. |
|
#17
|
|||
|
|||
|
Strange because I thought all NACHI members had to follow the SOP atleast to the minimum of the standard.
I just happen to find it very important that if an HI is going to comply with the SOP that they need to understand that the Conductors must be sized properly for the service in question. The OCPD's should not be oversized for the conductors to which it is protecting and so on. I did not know that concept was different in Canada.....I think quite possibly that Nick and Deanna ( if they are reading this ) should consider dropping me from the speaking list in Canada...I most certainly do not mind not going..... I will preach this day in and day out....so if this is not the case in Canada I think people will be wasting their time listening to me at the convention and I have better things to do with my time..... Paul W. Abernathy Last edited by pabernathy; 4/21/07 at 10:23 AM.. |
|
#18
|
||||
|
||||
|
Quote:
Yes My home has A Stablok service Roy Cooke Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#19
|
||||
|
||||
|
Roy,
Actually if they could keep the homeowners out of the panels, there would be a lot less for us to report on. BTW the way I don't think anyone is concerned with the newer Stay-Loks, just the old ones. |
|
#20
|
||||
|
||||
|
Quote:
Quote:
We have 93 members in our state chapter. I don't know about "all" home inspectors but I do know that our chapter members are certainly qualified. We are “top-heavy” with engineers, electricians, certified HVAC technicians, certified plumbers, past and present code officials, etc., etc.. We provide three hours of continuing education on different subject matter each and every month. One of our members taught Home Inspection classes at the local community college. We have a very highly trained and educated group of people.
Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
|
#21
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The "next higher breaker size" rule only refers to rounding up when the ampacity falls between two standard sizes. Since 175a IS a standard size you can't round up.
|
|
#22
|
|||
|
|||
|
Thank you
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |