Default 200 amp service?

Take a look at this panel and the meter. What would you state the amperage to be on this installation the buyers contract was for 300A service the breakers are 2@150 the meter says 200.
Attached Thumbnails
200-amp-service-100_4170.jpg   200-amp-service-100_4165.jpg   200-amp-service-100_4169.jpg   200-amp-service-100_4168.jpg  
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/14/11, 4:05 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: 200 amp service?

200 meter. IMO, should have 400 for 2-150 mains. Suggest to the owner to check with utility company for verification of meter size and fuse size behind the meter itself, if any. Appears to be a possible double-tap behind the meter.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #3  
Old 12/14/11, 4:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service?

IMO it's 150 + 150 or 300 amps. The meter really has nothing to do with the service size. If it's too small then it's the POCO's problem. However that doesn't mean that there aren't other potential issues visible in the photo.

Last edited by Robert Meier; 12/14/11 at 4:35 PM..
Reply With Quote
  #4  
Old 12/14/11, 4:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 200 amp service?

It looks like a paralell 150A service - essentially, two separate 150 amp service-circuits. It appears that one breaker feeds the breakers within the service equipment, while the other feeds an additional panel.

Regardless of the rest of the equipment, the meter rating has no bearing on the capacity of the system. Meters are the responsibility of the utility company, and their rating should be ignored by home inspectors.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 12/14/11, 5:47 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: 200 amp service?

I state the amp service on every report, because most insurance companies always ask. Never missed in 10 years, 3,800 inspections. Inspectors are different.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #6  
Old 12/14/11, 6:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service?

Quote:
Originally Posted by gfarnsworth View Post
I state the amp service on every report, because most insurance companies always ask. Never missed in 10 years, 3,800 inspections. Inspectors are different.
So based on the photo's what size service would you call this?

A few other observations. If you take a look at photo #1 you'll see a graphic depiction of a double lug at the meter. Since everything on the line side of the two CB's is factory installed I would rule out the possibility of a double tap. The label says for underground service entrance only so I would note that if it were overhead. Also the entrance of the SER cables is somewhat suspect. Is that a raceway in the upper right corner? If so how long is it since more than 24" would bring about derating. Also depending on the code cycle, derating issue and the conductor size the SER maybe undersized for 150 amps.
Reply With Quote
  #7  
Old 12/14/11, 6:37 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: 200 amp service?

Quote:
Originally Posted by bhoagland View Post
Take a look at this panel and the meter. What would you state the amperage to be on this installation the buyers contract was for 300A service the breakers are 2@150 the meter says 200.

What you have there is a 300 amp service. The 200 on the meter means nothing as to the size of the service.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #8  
Old 12/14/11, 8:04 PM
Chad Norlen, CPI's Avatar
Chad Norlen, CPI Chad Norlen, CPI is offline
InterNACHI Member
 
Join Date: Nov 2011
Location: American Falls, ID
Posts: 232
Default Re: 200 amp service?

From NACHI's Online Education: How To Inspect Residential Electrical Inspections

Calculating Available Amperage


In many cases, the listing information about a home is incorrect regarding the service amperage because brokers or owners rely solely on the size of the main breaker or fuse. Many people are also under the mistaken impression that the available amperage is the total of the individual breakers or fuses in the service panel.

The correct way to determine the available amperage is to determine the ampacity of the lowest-rated or the weakest link of the following components:
  • service supply;
  • electric meter and socket;
  • service entrance conductors;
  • service disconnect; or
  • distribution panel.
Here are a couple of examples:
Example #1:
A 200-amp service lateral,
a 200-amp meter and base,
a 175-amp-rated SEC,
a 150-amp-rated panel, and
+ a 125-amp service disconnect
= A 125-amp reportable service supply

Example #2:
A 150-amp service drop,
a 60-amp meter and base,
a 150-amp SEC,
a 100-amp-rated panel, and
+ a 100-amp service disconnect
= A 60-amp reportable service supply

A home inspector getting this wrong could potentially end up paying for a service upgrade costing several thousand dollars.



Chad Norlen
SEI Inspections
InterNACHI Member

Certified Professional Inspector
HVAC Journeyman - State of Idaho
EPA Certified Universal Technician
Reply With Quote
  #9  
Old 12/14/11, 8:17 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service?

Quote:
Originally Posted by cnorlen View Post
From NACHI's Online Education: How To Inspect Residential Electrical Inspections

Calculating Available Amperage


In many cases, the listing information about a home is incorrect regarding the service amperage because brokers or owners rely solely on the size of the main breaker or fuse. Many people are also under the mistaken impression that the available amperage is the total of the individual breakers or fuses in the service panel.

The correct way to determine the available amperage is to determine the ampacity of the lowest-rated or the weakest link of the following components:
  • service supply;
  • electric meter and socket;
  • service entrance conductors;
  • service disconnect; or
  • distribution panel.
Here are a couple of examples:
Example #1:
A 200-amp service lateral,
a 200-amp meter and base,
a 175-amp-rated SEC,
a 150-amp-rated panel, and
+ a 125-amp service disconnect
= A 125-amp reportable service supply

Example #2:
A 150-amp service drop,
a 60-amp meter and base,
a 150-amp SEC,
a 100-amp-rated panel, and
+ a 100-amp service disconnect
= A 60-amp reportable service supply

A home inspector getting this wrong could potentially end up paying for a service upgrade costing several thousand dollars.
I would disagree that the amperage of the utility meter has anything to do with the size of a service.
Reply With Quote
  #10  
Old 12/14/11, 8:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 200 amp service?

Quote:
Originally Posted by gfarnsworth View Post
I state the amp service on every report, because most insurance companies always ask. Never missed in 10 years, 3,800 inspections. Inspectors are different.
I'm not sure I understand your point with this post. The OP is not asking whether or not to report the service capacity, he is asking for clarification on how to determine the capacity.
Quote:
Originally Posted by Robert Meier View Post
I would disagree that the amperage of the utility meter has anything to do with the size of a service.
As would I.

The meter rating is irrelevant - period.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 12/14/11, 8:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp service?

And I would disagree that in terms of Home Inspectors it does indeed have some relevance but not really a sizing factor you hang your hat on...as it could simply be an error. You use it to confirm things sometimes but that's all. However, as stated in my course as well as others the meter is one of the things you can THROW OUT in your equation if you have enough elements to support your basic findings.

My eyes are not doing well here as i can't see the 150A on those mains....I just assume it can be up to 200A each per the nomenclature provided. However, if they are 150A then you indeed have a 300A service based on the Main Circuit Breaker, The Size of the Conductors. However, there is one important point I would like to make beyond this...

If these are the service disconnects (which I am sure they are) and the SER cable running from each of these panels to their respective remote distribution panels are not serving "all loads" that are part of or associated with the dwelling would not be allowed to use allowance of Section 310.15(B)(7) and the associated table.

Just a tidbit of information....



Paul W. Abernathy
Reply With Quote
  #12  
Old 12/14/11, 8:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 200 amp service?

Los Angeles Department of Water & Power (LADWP) has thousands of "15 amp" meters still in use on services from 60 to 400 amps.

Meter ratings are not a limiting factor for determining service capacity.
Attached Thumbnails
200-amp-service-m1.jpg   200-amp-service-m2.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 12/14/11, 8:39 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp service?

Quote:
Originally Posted by jpope View Post
Los Angeles Department of Water & Power (LADWP) has thousands of "15 amp" meters still in use on services from 60 to 400 amps.

Meter ratings are not a limiting factor for determining service capacity.
True....however if you are using a meter for example on a service you believe is 200A...you see 4/0 AL, you see 200A main....but lets say you can't see the panel enclosures rating....the meter being a CL200 may just help you confirm what your suspected....but again never rely on a meter....the power company will throw anything in those as long as it fits.

Now....knowing the meter cabinets sizes, shapes and so on WILL assist you in some cases....but that is what we mean when we say meters...not the meter itself....but the meters enclosure more correctly.



Paul W. Abernathy
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/14/11, 8:41 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 200 amp service?

Quote:
Originally Posted by pabernathy View Post
Now....knowing the meter cabinets sizes, shapes and so on WILL assist you in some cases....but that is what we mean when we say meters...not the meter itself....but the meters enclosure more correctly.
Agreed.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 12/14/11, 8:44 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp service?

Quote:
Originally Posted by cnorlen View Post
From NACHI's Online Education: How To Inspect Residential Electrical Inspections

Calculating Available Amperage


In many cases, the listing information about a home is incorrect regarding the service amperage because brokers or owners rely solely on the size of the main breaker or fuse. Many people are also under the mistaken impression that the available amperage is the total of the individual breakers or fuses in the service panel.

The correct way to determine the available amperage is to determine the ampacity of the lowest-rated or the weakest link of the following components:
  • service supply;
  • electric meter and socket;
  • service entrance conductors;
  • service disconnect; or
  • distribution panel.
Here are a couple of examples:
Example #1:
A 200-amp service lateral,
a 200-amp meter and base,
a 175-amp-rated SEC,
a 150-amp-rated panel, and
+ a 125-amp service disconnect
= A 125-amp reportable service supply

Example #2:
A 150-amp service drop,
a 60-amp meter and base,
a 150-amp SEC,
a 100-amp-rated panel, and
+ a 100-amp service disconnect
= A 60-amp reportable service supply

A home inspector getting this wrong could potentially end up paying for a service upgrade costing several thousand dollars.
For example...in Example #2 the issue was the 60A meter and base. Not so much the meter...but really the BASE you are calling out because it is typical of an upgrade with no permits...issues your client will indeed need to know about. also due to poor bending radius in those smaller meters and so on...it is indeed a weak link in this example......you call it out......let them decide. however, place the issue on the base really...not the meter itself.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service size acox Electrical Inspections 6 9/5/09 2:40 PM
Infrared Inspection Service jwarner Thermal Imaging, Infrared Cameras & Energy Audits 25 7/28/09 7:32 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 5:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts