Default 200 amp service question

I'm doing an inspection Sunday for a client who has a 200 amp service meter but has one 200 amp and one 100 amp panel in the basement. Is this allowed?
Reply With Quote
  #2  
Old 4/11/08, 7:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 200 amp service question

Quote:
Originally Posted by ekartal
I'm doing an inspection Sunday for a client who has a 200 amp service meter but has one 200 amp and one 100 amp panel in the basement. Is this allowed?
How is the 100 Amp panel fed?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 4/11/08, 7:11 PM
Erol Kartal Erol Kartal is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Schaumburg, Illinois
Posts: 699
Default Re: 200 amp service question

I'll have to wait until I get there. Another scud crud I'm sure..
Reply With Quote
  #4  
Old 4/11/08, 7:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 200 amp service question

Quote:
Originally Posted by ekartal
I'll have to wait until I get there. Another scud crud I'm sure..
Should be interesting. Come back and post your pics.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 4/11/08, 7:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

Sure. You can have 10 panels hung off one 200 amp service if you want to. People do this all the time to get more "spaces". Matter of fact, a house I'm wiring right now I intend to hang a 200 and a 100 off a 200 amp meter can. My demand load is fine for a 200 amp service, but I need more spaces.

If you get there and something rubs you the wrong way about how they have both panels spliced into the 200 amp can (there are several compliant ways to do this, and many that aren't), take pictures and post them for evaluation. This would be the main thing you'd need to concern yourself with when evaluating such a situation.
Reply With Quote
  #6  
Old 4/11/08, 7:16 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

Quote:
Originally Posted by ekartal
I'm doing an inspection Sunday for a client who has a 200 amp service meter but has one 200 amp and one 100 amp panel in the basement. Is this allowed?
Yes it is allowed .
In a large home it can save multiple runs of wire to the other end of the home .
Reply With Quote
  #7  
Old 4/11/08, 7:16 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 200 amp service question

Marc,

I PMed you a few days ago. did you get it?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 4/11/08, 7:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

Quote:
Originally Posted by mlarson
Marc,

I PMed you a few days ago. did you get it?
Nope.
Reply With Quote
  #9  
Old 4/11/08, 7:18 PM
Shane Aldworth Shane Aldworth is offline
New User
 
Join Date: Apr 2008
Location: havelock Ontario
Posts: 10
Please Note: Shane Aldworth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

I have come across several times a 100amp service coming from the street into a 200amp break and panel, I have found out that it is ok to do this in ontario but I still avdvise against this and note this in my report. check to verify if the service comes into the 200amp panel 1st and then runs to the 100amp, and does the 100amp panel have it's own breaker in the panel or is there a breaker for this panel in the 200amp. Aso check to verify that you have the proper sized wires going into the panel. Check to see if you have just 1 or also a 2nd meter maybe hidden somewhere (indicates 2 separate services). I did perform an inspection on 1 place that did have a set up like this, turned out they were stealing hydro for a grow house, the 2nd panel by passed the meter.


sorry i ment to state coming into the main breaker not from the street

Last edited by Shane Aldworth; 4/11/08 at 7:51 PM..
Reply With Quote
  #10  
Old 4/11/08, 7:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 200 amp service question

Quote:
Originally Posted by Marc D. Shunk
Nope.
I'll try agian

There is a limit to how many you can store on the site. Maybe your's is full.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #11  
Old 4/11/08, 7:19 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

Quote:
Originally Posted by Shane Aldworth
I have come across several times a 100amp service coming from the street...
I humbly submit that you have no idea what you were looking at. The power companies work to a totally different set of rules. What might look like a "100 amp" drop by NEC style guidelines can do 200 amp. They use #2 aluminium for a 200 amp drop.
Reply With Quote
  #12  
Old 4/11/08, 7:20 PM
Erol Kartal Erol Kartal is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Schaumburg, Illinois
Posts: 699
Default Re: 200 amp service question

Thanks for the prompt feedback buys.
Reply With Quote
  #13  
Old 4/11/08, 7:20 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 amp service question

Quote:
Originally Posted by mlarson
I'll try agian

There is a limit to how many you can store on the site. Maybe your's is full.
Yeah, it gets full pretty regularly, and it pisses me off. I just let it run full for a few weeks till I get over myself.
Reply With Quote
  #14  
Old 4/11/08, 7:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 200 amp service question

Quote:
Originally Posted by Marc D. Shunk
Yeah, it gets full pretty regularly, and it pisses me off. I just let it run full for a few weeks till I get over myself.
LOL...LOL...LOL



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
question on electrical service Coral Chesney Electrical 6 2/24/07 10:35 AM
Help Determining Reportable Service Size cbarrows Electrical 8 7/19/06 8:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical 16 6/27/06 11:41 PM
Main service disonnect question jmichalski Electrical 5 1/29/06 5:32 PM


All times are GMT -4. The time now is 2:04 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts