  #1  
Old 3/2/09, 2:41 PM
Bruce L. Treacy Bruce L. Treacy is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Flamborough, ON
Posts: 45
Cool 200 amp sub panel

What size of breaker would be required in the main distribution panel to supply a 2oo amp sub panel located in a garage.
Reply With Quote
  #2  
Old 3/2/09, 4:36 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 200 amp sub panel

Depends....If the load in the sub-panel in the Garage is only lets say 75A then the panel in the garage could be 200A if they wish but the OCPD feeding the panel would be more than likely 80 Amps.

Remember the panel itself could be larger....but the load will be limited to that panel by the protection for that panels feeders in the main distribution panel.

What size is the Main Distribution Panel and have they determined WHY they would need a 200A panel in the garage other than maybe thats the size they bought because they had no idea they really did not need that much.

Is this a detached to attached garage.....for asking sake.



Paul W. Abernathy
Reply With Quote
  #3  
Old 3/9/09, 6:14 PM
Dennis DiVito Dennis DiVito is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Fairfield, VA
Posts: 38
Default Re: 200 amp sub panel

the circuit breaker for the sub-panel should be sized according to the feeder cables that are going to the sub-panel. The only relevance as to which panel is used for the sub-panel is that it be rated for the amperage fed to it. You can use a 200 amp panel for the sub-panel but it a waste of money.

Electrical loads are beyond the scope of a home inspection. Recommend a licensed electrician evaluate the load.

Last edited by ddivito; 3/9/09 at 6:18 PM..
Reply With Quote
  #4  
Old 3/9/09, 6:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 200 amp sub panel

Quote:
Originally Posted by btreacy View Post
What size of breaker would be required in the main distribution panel to supply a 2oo amp sub panel located in a garage.
A "main distribution panel" IS a sub-panel. I believe you mean to say service equipment panel.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 3/9/09, 7:48 PM
Bruce L. Treacy Bruce L. Treacy is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Flamborough, ON
Posts: 45
Default Re: 200 amp sub panel

Thanks for the replys
Reply With Quote
  #6  
Old 3/9/09, 9:55 PM
ecolclasure ecolclasure is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Hibbing Mn
Posts: 26
Default Re: 200 amp sub panel

Hello I am an electrician and i just though you should know there are also codes about sequence of opperation that basically say that the panel in the garage should trip first then the house
Reply With Quote
  #7  
Old 3/9/09, 11:43 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 200 amp sub panel

Quote:
Originally Posted by ecolclasure View Post
Hello I am an electrician and i just though you should know there are also codes about sequence of opperation that basically say that the panel in the garage should trip first then the house
The house should trip? Can you be a little less technical?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 3/9/09 at 11:46 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts