Default 200 main breaker X 2

Why/what would the purpose be of installing a 200 AMP breaker/disconnect in the garage on the main supply when there is also a 200 AMP breaker in the Main panel? Would this cause a problem?

Possible scenario, I believe the garage is an add-on to the house and the local AHJ required the disconnect be installed because the main service now runs through the building down to the basement where the "old" panel is. The house is about 8 years old, I don't know how old the garage is.

Thoughts?



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 10/8/08, 9:27 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful Mike Whitt is almost always very helpful
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

Quote:
Originally Posted by sfalvey View Post
Would this cause a problem?
No It is premissible to feed a panel as large or even larger than the service as long as the feeders are large enough to carry the total load
Reply With Quote
  #3  
Old 10/8/08, 10:01 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

I suspect since the panel was only 8 years old when the garage was added they simply added the main disconnect outside and made the panel into a sub-panel.
Nothing wring with a sub-panel with a main breaker.
Reply With Quote
  #4  
Old 10/8/08, 10:40 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 589
Ben J. Gromicko is often very helpful Ben J. Gromicko is often very helpful
Default Re: 200 main breaker X 2

Possibly adding the garage forced the builder relocated the meter. And when the meter was relocated, a main disconnect switch had to be added near the meter. Isn't there some type of rule where you have to have a main disconnect within 8 feet of the electrical meter? So maybe the meter was moved too far away from the panel, and a disconnect had to be installed in between the relocated meter and panel.
Huh? My brain hurts.




BEN GROMICKO
InterNACHI's Director of Education and Training

NACHI.TV: Author, Director, Editor of Training Videos:
Stairway Inspection
Electrical Inspection
Egress Inspection
Inspecting Water Tanks
Infrared Thermography
Bored Holes Cuts Notches
Crawlspace Inspection
Mold
SOP Home Inspection
Electrical Wall of Defects
HVAC Training
Your Best Inspection

Author of Online Courses:
Plumbing Inspection
Mold Training
Wood Destroying Organism
25 Standards Inspectors Should Know

Moisture Intrusion
Reply With Quote
  #5  
Old 10/8/08, 10:46 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

Yup Ben, that was exactly my point, that I didn't make very well.

The rule is the disconnect must be "nearest the point of entrance of the service conductors". This can vary from zero feet to as much as fifteen feet.
Most places it is 5'-6'.

I would assume when the garage was added it put the main breaker way too far into the house.
I have had to do this many times.
Reply With Quote
  #6  
Old 10/8/08, 10:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

Sticking a garage on the end necessitates the main disconnect outside just so all that cable between the outdoors and the panel indoors will be fused (ie, have overcurrent protection). There are rules of thumb used from jurisdiction to jurisdiction, but very few will permit as much as 8 feet of unfused service cable indoors. Some allow none, others allow 3 feet, and others permit up to 6 feet if you put it in rigid metal conduit. The NEC does not spell out any particular dimensional maximum, but only contains verbage that requires unfused service conductors to be very short. When this can't be accomplished, such as would be the case when a garage is slapped on the end, then you're in a position of putting a main disconnect outdoors next to the meter, or immediately indoors in the garge on the back side of the meter.
Reply With Quote
  #7  
Old 10/8/08, 10:56 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 589
Ben J. Gromicko is often very helpful Ben J. Gromicko is often very helpful
Default Re: 200 main breaker X 2

I'm trying to understand the rule of running 4 wires to the panel in a detached garage. Is that because the panel in the garage is required to be a sub panel, and therefore you have two hots (black and red) one white for the neutral bus bar and another (green i suppose) going to the grounding bus bar? 4 wires for four buses? Is that the reason for the 4 wire rule to the detached garage?




BEN GROMICKO
InterNACHI's Director of Education and Training

NACHI.TV: Author, Director, Editor of Training Videos:
Stairway Inspection
Electrical Inspection
Egress Inspection
Inspecting Water Tanks
Infrared Thermography
Bored Holes Cuts Notches
Crawlspace Inspection
Mold
SOP Home Inspection
Electrical Wall of Defects
HVAC Training
Your Best Inspection

Author of Online Courses:
Plumbing Inspection
Mold Training
Wood Destroying Organism
25 Standards Inspectors Should Know

Moisture Intrusion
Reply With Quote
  #8  
Old 10/8/08, 11:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

Quote:
Originally Posted by bgromicko View Post
I'm trying to understand the rule of running 4 wires to the panel in a detached garage. Is that because the panel in the garage is required to be a sub panel, and therefore you have two hots (black and red) one white for the neutral bus bar and another (green i suppose) going to the grounding bus bar? 4 wires for four buses? Is that the reason for the 4 wire rule to the detached garage?
You're s'zackly right. Subpanel means 4 conductors (or 5 if you're dealing with 3-phase). There were some exceptions for certain detached buildings up until the 2008 NEC that would permit some detached structures to be fed with 3-wire and not wired like a subpanel. Those permissions disappear as the 2008 NEC becomes adopted.
Reply With Quote
  #9  
Old 10/8/08, 11:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 200 main breaker X 2

ben...the reason is primarily because the 4th conductor in question is the Equipment Grounding Conductor needed to aid in the clearing of the breaker feeding that 'Sub-Panel"

Remember now...in the case that is proposed....the grounding electrode system will need to be established the detached structure.....as again grounding electrode systems have no effect on clearing any overcurent protection device.

Now....prior to 2008 NEC.....Three conductors are allowed as long as the conditions are met....they are specific and listed in 250.32(B)(2) if you would like some late night reading material....lol...

Basically the concept of sharing the grounded (Neutral ) conductor is going by the wayside for new installations because of the potential of objectionable currents (250.6(A)) and so on.......

I believe the 2008 NEC makes so nice.....but thats my opinion.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #10  
Old 10/9/08, 1:49 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 589
Ben J. Gromicko is often very helpful Ben J. Gromicko is often very helpful
Default Re: 200 main breaker X 2

Quote:
Originally Posted by pabernathy View Post
.Basically the concept of sharing the grounded (Neutral ) conductor is going by the wayside for new installations because of the potential of objectionable currents (250.6(A)) and so on.......
That's an SE cable. 3-wires.

An SER is a 4-wire cable.

Yes?




BEN GROMICKO
InterNACHI's Director of Education and Training

NACHI.TV: Author, Director, Editor of Training Videos:
Stairway Inspection
Electrical Inspection
Egress Inspection
Inspecting Water Tanks
Infrared Thermography
Bored Holes Cuts Notches
Crawlspace Inspection
Mold
SOP Home Inspection
Electrical Wall of Defects
HVAC Training
Your Best Inspection

Author of Online Courses:
Plumbing Inspection
Mold Training
Wood Destroying Organism
25 Standards Inspectors Should Know

Moisture Intrusion
Reply With Quote
  #11  
Old 10/9/08, 6:54 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200 main breaker X 2

Quote:
Originally Posted by bgromicko View Post
That's an SE cable. 3-wires.

An SER is a 4-wire cable.

Yes?
SE is the generic reference to any type of Service Entrance cable. Type SEU is the "flat" stuff that is made in 3-wire, and that stands for Service Entrance, Unarmored (there was armored SE once upon a time, and it's a bitch to strip out). The 4-wire and 5-wire stuff is SER, for Service Entrance, Round.

Your service entrance could just as easily be conductors in conduit, or in a commercial application for a subpanel, type MC cable. With certain caveats, the service entrance and the feeders to the subpanels can be pretty much any wiring method. In the East, we'd see mostly type SE cable, and in the West you'd see mostly conductors in conduit.
Reply With Quote
  #12  
Old 10/10/08, 12:31 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 200 main breaker X 2

Quote:
Originally Posted by bgromicko View Post
That's an SE cable. 3-wires.

An SER is a 4-wire cable.

Yes?
Thats Correct......SE Cable is generally the (2) ungrounded conductors with a third grounded conductor. The SER like marc said has (2) ungrounded conductors,(1) Grounded and (1) Grounding ( equipment grounding conductor that is )

for the most part.......



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
Reply

Tags
breaker , electric

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Breaker sfalvey Electrical 16 1/26/08 10:38 PM
main Breaker vriverajr Electrical 5 1/2/08 11:52 AM
Arching Causes Main Breaker To Trip? msylvester Electrical 10 10/22/07 4:57 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 4:39 PM.


Popular Sections

: