Why/what would the purpose be of installing a 200 AMP breaker/disconnect in the garage on the main supply when there is also a 200 AMP breaker in the Main panel? Would this cause a problem?
Possible scenario, I believe the garage is an add-on to the house and the local AHJ required the disconnect be installed because the main service now runs through the building down to the basement where the "old" panel is. The house is about 8 years old, I don't know how old the garage is. Thoughts? Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
No It is premissible to feed a panel as large or even larger than the service as long as the feeders are large enough to carry the total load
|
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I suspect since the panel was only 8 years old when the garage was added they simply added the main disconnect outside and made the panel into a sub-panel.
Nothing wring with a sub-panel with a main breaker. |
|
#4
|
||||
|
||||
|
Possibly adding the garage forced the builder relocated the meter. And when the meter was relocated, a main disconnect switch had to be added near the meter. Isn't there some type of rule where you have to have a main disconnect within 8 feet of the electrical meter? So maybe the meter was moved too far away from the panel, and a disconnect had to be installed in between the relocated meter and panel.
Huh? My brain hurts. BEN GROMICKO InterNACHI's Director of Education and Training NACHI.TV: Author, Director, Editor of Training Videos: Stairway Inspection Electrical Inspection Egress Inspection Inspecting Water Tanks Infrared Thermography Bored Holes Cuts Notches Crawlspace Inspection Mold SOP Home Inspection Electrical Wall of Defects HVAC Training Your Best Inspection Author of Online Courses: Plumbing Inspection Mold Training Wood Destroying Organism 25 Standards Inspectors Should Know Moisture Intrusion |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yup Ben, that was exactly my point, that I didn't make very well.
The rule is the disconnect must be "nearest the point of entrance of the service conductors". This can vary from zero feet to as much as fifteen feet. Most places it is 5'-6'. I would assume when the garage was added it put the main breaker way too far into the house. I have had to do this many times. |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sticking a garage on the end necessitates the main disconnect outside just so all that cable between the outdoors and the panel indoors will be fused (ie, have overcurrent protection). There are rules of thumb used from jurisdiction to jurisdiction, but very few will permit as much as 8 feet of unfused service cable indoors. Some allow none, others allow 3 feet, and others permit up to 6 feet if you put it in rigid metal conduit. The NEC does not spell out any particular dimensional maximum, but only contains verbage that requires unfused service conductors to be very short. When this can't be accomplished, such as would be the case when a garage is slapped on the end, then you're in a position of putting a main disconnect outdoors next to the meter, or immediately indoors in the garge on the back side of the meter.
|
|
#7
|
||||
|
||||
|
I'm trying to understand the rule of running 4 wires to the panel in a detached garage. Is that because the panel in the garage is required to be a sub panel, and therefore you have two hots (black and red) one white for the neutral bus bar and another (green i suppose) going to the grounding bus bar? 4 wires for four buses? Is that the reason for the 4 wire rule to the detached garage?
BEN GROMICKO InterNACHI's Director of Education and Training NACHI.TV: Author, Director, Editor of Training Videos: Stairway Inspection Electrical Inspection Egress Inspection Inspecting Water Tanks Infrared Thermography Bored Holes Cuts Notches Crawlspace Inspection Mold SOP Home Inspection Electrical Wall of Defects HVAC Training Your Best Inspection Author of Online Courses: Plumbing Inspection Mold Training Wood Destroying Organism 25 Standards Inspectors Should Know Moisture Intrusion |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
ben...the reason is primarily because the 4th conductor in question is the Equipment Grounding Conductor needed to aid in the clearing of the breaker feeding that 'Sub-Panel"
Remember now...in the case that is proposed....the grounding electrode system will need to be established the detached structure.....as again grounding electrode systems have no effect on clearing any overcurent protection device. Now....prior to 2008 NEC.....Three conductors are allowed as long as the conditions are met....they are specific and listed in 250.32(B)(2) if you would like some late night reading material....lol... Basically the concept of sharing the grounded (Neutral ) conductor is going by the wayside for new installations because of the potential of objectionable currents (250.6(A)) and so on....... I believe the 2008 NEC makes so nice.....but thats my opinion. Paul W. Abernathy,CMI,CEI,CEPE Electrical Plans Examiner/Engineer I NEC Code Expert & Consultant - ICC & IAEI Certified Electrical Inspector - DHCD Virginia Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - DHCD Virginia Certified Electrical Plans Examiner - DPOR Virginia CE Provider - Electricians - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series. |
|
#10
|
||||
|
||||
|
Quote:
An SER is a 4-wire cable. Yes? BEN GROMICKO InterNACHI's Director of Education and Training NACHI.TV: Author, Director, Editor of Training Videos: Stairway Inspection Electrical Inspection Egress Inspection Inspecting Water Tanks Infrared Thermography Bored Holes Cuts Notches Crawlspace Inspection Mold SOP Home Inspection Electrical Wall of Defects HVAC Training Your Best Inspection Author of Online Courses: Plumbing Inspection Mold Training Wood Destroying Organism 25 Standards Inspectors Should Know Moisture Intrusion |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
SE is the generic reference to any type of Service Entrance cable. Type SEU is the "flat" stuff that is made in 3-wire, and that stands for Service Entrance, Unarmored (there was armored SE once upon a time, and it's a bitch to strip out). The 4-wire and 5-wire stuff is SER, for Service Entrance, Round.
Your service entrance could just as easily be conductors in conduit, or in a commercial application for a subpanel, type MC cable. With certain caveats, the service entrance and the feeders to the subpanels can be pretty much any wiring method. In the East, we'd see mostly type SE cable, and in the West you'd see mostly conductors in conduit. |
|
#12
|
||||
|
||||
|
Thats Correct......SE Cable is generally the (2) ungrounded conductors with a third grounded conductor. The SER like marc said has (2) ungrounded conductors,(1) Grounded and (1) Grounding ( equipment grounding conductor that is )
for the most part....... Paul W. Abernathy,CMI,CEI,CEPE Electrical Plans Examiner/Engineer I NEC Code Expert & Consultant - ICC & IAEI Certified Electrical Inspector - DHCD Virginia Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - DHCD Virginia Certified Electrical Plans Examiner - DPOR Virginia CE Provider - Electricians - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series. |
![]() |
| Tags |
| breaker , electric |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main Breaker | sfalvey | Electrical | 16 | 1/26/08 10:38 PM |
| main Breaker | vriverajr | Electrical | 5 | 1/2/08 11:52 AM |
| Arching Causes Main Breaker To Trip? | msylvester | Electrical | 10 | 10/22/07 4:57 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |