Default 2008 NEC AFCI requirements

210.12(B)Dwelling Units. (Thanks to Joe Tedesco for this info)

All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, recreation rooms, closets, hallways , or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type installed to provide protection of the branch circuit.




www.buildingcenter.org

Quickly determine the date of manufacture, age or production of most HVAC and Water Heating equipment
Reply With Quote
  #2  
Old 4/28/07, 11:35 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

John
I see that you are from NY. NY will not be following the 2008 version of the NEC for some years to come. In August of 2007, we will most likely be going to the new State Code.

This new State Code as it stands (a slight chance this may change) is complex to follow in Residential wiring.



As it stands for adoption of August 2007:
Residential buildings with a service of 400 amps or less will follow the Residential Code of NYS. Any items not covered in Chapters 32-43 will be referencing the 2002 NEC to "fill in those gaps".
Remember that the electrician and the inspector will have to be aware of when to apply the RBCNYS and when to reference the NEC version 2002 or 2005.


Residential buildings with a service larger than 400 amps will reference the 2005 NEC in its entirety. Also Multifamily buildings (3 or more family) will reference the 2005 NEC in its entirety.

All other building types (occupancies) will reference the 2005 NEC in its entirety.

I say mass confusion will begin in a few months...leading to most installers using the 2005 NEC as there installation reference.

GOOD LUCK!!!!!
Reply With Quote
  #3  
Old 4/28/07, 12:57 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Florida is talking about skipping the 2008 too.
Personally I think the whole NEC process should be stretched out to 6-10 years between cycles. It is stupid to come out with new codes faster than AHJs can evaluate and adopt them. It certainly sells a lot of books and seminars and makes NFPA rich.
Reply With Quote
  #4  
Old 4/29/07, 1:05 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by Pierre Belarge
As it stands for adoption of August 2007:
Residential buildings with a service of 400 amps or less will follow the Residential Code of NYS. Any items not covered in Chapters 32-43 will be referencing the 2002 NEC to "fill in those gaps".
Remember that the electrician and the inspector will have to be aware of when to apply the RBCNYS and when to reference the NEC version 2002 or 2005.
I am on the electrical board of my local village. We casually discussed this last meeting.
Like you said, it's going to be fun (read: chaos) for quite a while after August! IF it even happens.

I don't even think I want to waste my time buying a 2008 Handbook & CD.
Reply With Quote
  #5  
Old 4/29/07, 1:08 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by jbowman
210.12(B)Dwelling Units. ...........
John, this topic is currently being discussed on several electrical boards. It is a contentious topic to say the least. Many different opinions and standings.
Reply With Quote
  #6  
Old 4/29/07, 1:15 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

How about the "tamper resistant receptacle" requirement. Why aren't we hearing about that? I bet that one causes more problems than the AFCI once people really read it. So long 43 cent receptacle. I doubt the quality will actually be any better but they will still cost more than heavy duty commercial.
Reply With Quote
  #7  
Old 4/29/07, 1:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 2008 NEC AFCI requirements

In CA, we haven't even adopted the 2005 NEC yet. We're still working with the '02.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/29/07, 2:29 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by jpope
In CA, we haven't even adopted the 2005 NEC yet. We're still working with the '02.
Jeff, is that the whole state of Ca? Here in AZ each municipality adopts separately, one township may be on one code cycle, and a few miles away could be on one or two cycles different.
Reply With Quote
  #9  
Old 4/29/07, 4:55 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by Pierre Belarge
John
I see that you are from NY. NY will not be following the 2008 version of the NEC for some years to come. In August of 2007, we will most likely be going to the new State Code.

This new State Code as it stands (a slight chance this may change) is complex to follow in Residential wiring.



As it stands for adoption of August 2007:
Residential buildings with a service of 400 amps or less will follow the Residential Code of NYS. Any items not covered in Chapters 32-43 will be referencing the 2002 NEC to "fill in those gaps".
Remember that the electrician and the inspector will have to be aware of when to apply the RBCNYS and when to reference the NEC version 2002 or 2005.


Residential buildings with a service larger than 400 amps will reference the 2005 NEC in its entirety. Also Multifamily buildings (3 or more family) will reference the 2005 NEC in its entirety.

All other building types (occupancies) will reference the 2005 NEC in its entirety.

I say mass confusion will begin in a few months...leading to most installers using the 2005 NEC as there installation reference.

GOOD LUCK!!!!!
No confusion at all.

New York Code in 2008 will be Sub Standard to the National Code?

Good to know......



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #10  
Old 4/29/07, 4:58 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: 2008 NEC AFCI requirements

Deference to Electrical Code is cost related only OR is there some other issue?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 4/29/07, 5:51 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by jhagarty
No confusion at all.

New York Code in 2008 will be Sub Standard to the National Code?

Good to know......
The "National" code is NOT national unless it is adopted.
From what I have seen a majority of the country has not yet even adopted the 2005 NEC in it's entirety.
So your statement applies to WAY more places than just NYS.
Reply With Quote
  #12  
Old 4/29/07, 5:58 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

In Tucson we have normally adopted the previous code just as the newest code comes out, in other words we were always 3 years behind. Now we have a new program and the inspectors have told me we will be more pro active in code adoption, adopting the newer ones shortly after they come out. We also have local amendments which are available online.

I know there are at least a couple of you here in Tucson, thought you might like to know.
Reply With Quote
  #13  
Old 4/29/07, 8:15 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by Speedy Petey
The "National" code is NOT national unless it is adopted.
From what I have seen a majority of the country has not yet even adopted the 2005 NEC in it's entirety.
So your statement applies to WAY more places than just NYS.
If the majority has not adpted the 2005 Code as you allege, what weight should be placed upon the 2008 NEC or even the NEC in general?

Is the NEC merely Representative of the Minimum Code or the Electrical Code that no one follows?

Interesting.....



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #14  
Old 4/29/07, 8:33 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2008 NEC AFCI requirements

Quote:
Originally Posted by jhagarty
Is the NEC merely Representative of the Minimum Code or the Electrical Code that no one follows?.
The NEC is a model code, no different than the dozens and dozens of model codes that have existed for many decades, such as the "U" codes, all the "I" codes, tons of ANSI stuff, along with the NEC and the other NFPA code books. It is up to the state or local jurisdiction to adopt it in whole or in part, and with or without amendments, in order for any of them to have the force of law. Lacking that, it's just a document that many regard as a set of minimum safety standards related to electrical wiring. The existence of a code or standard does not automatically mean that it applies to the jurisdiction in which a certain installation is made. Get in your car, and drive an hour in any direction, and you're likely to pass through jurisdictions with 50 different sets of codes that have the force of law. I would add that the NEC seems to be pretty universal, with some amendments in some areas, but the exact revision year that is in force is what's always different from area to area. Some notable areas highly modify the NEC or make their own electrical code. Places like Chicago, New York City, and San Francisco are such notable places.

Last edited by Marc D. Shunk; 4/29/07 at 8:36 PM..
Reply With Quote
  #15  
Old 4/29/07, 8:49 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: 2008 NEC AFCI requirements

Marc,

If the NEC is a Minimum standard, how is it that municipalities may elect to subscribe to a "Less than Minimum Standard" Standard.

Not looking to enter into a Code debate....

... but what weight should be placed upon the "NEC Standard" if no one subscribes to their minimum standard recommendations or believes their minimum to be excessive?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 4/29/07 at 8:56 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
AFCI Controversy rcooke Electrical Inspections 11 9/10/07 2:14 PM
AFCI Requirements jbowman4 Electrical Inspections 7 5/20/07 11:27 AM


All times are GMT -4. The time now is 5:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts