I have an 800 amp MDP. out of this 800 amp MDP, a 200 amp breaker feeds a 200 amp secondary main lug MDP, in this 200 amp SMDP I have TWO, 200 amp breakers feeding separate 200 amp sub panels.
This is a previous installation, and I have to make changes to the facility this is installed in. Will this configuration create an issue with the inspector for the changes I need to make on my work in the existing 800 amp main MDP? Thank you Last edited by Russ Stacey; 1/5/11 at 10:39 PM.. |
| Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
You might want to consult an electrical engineer and pull a permit.
David Hays All Points Home Inspections LLC Denver, CO 720-670-0366 allpointshomeinspect@yahoo.com www.allpointshomeinspections.org |
|
#3
|
|||
|
|||
|
Please Note:
Russ Stacey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why would I need to consult an EE to ask about existing equipment?, this is an inspection question.
Since I have already stated that my issue was with this EXISTING equipment conflicting with my NEW inspection on MY changes to the service it should be obvious,.... I already pulled a permit. That was nothing more than a "I have no clue what this person is asking, but I MUST say something",... comment. Anyone with some real answers like to respond? Thank you |
|
#4
|
||||
|
||||
|
Quote:
Though they will never likely draw their maximum capacity, the 200 amp breakers still act as disconnects for the panels they serve. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I think that he's questioning having one 200 amp OCPD protecting 2-200 amp panels:
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Russ Stacey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
200amp X TWO panels, or 200 amps across both panels? Thanks |
|
#7
|
||||
|
||||
|
The biggest problem you might encounter would be possible nuisance tripping if you have heavy loads. It all depends on what you are planning on running out of those two subpanels. If you plan on running a few RTU's, a lot of exhaust fans, a Liebert and a sh*tload of lighting, you might have something to worry about. If it's just normal everyday application loads, I wouldn't worry about it.
Where do you reside? Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Subpanel Unsafe? | dshewell | General Inspection Discussion | 4 | 10/25/10 7:28 PM |
| underamped subpanel?? | wstafford | Electrical Inspections | 12 | 5/13/09 5:08 PM |
| Neutral/ground bond in subpanel | gkeene | Electrical Inspections | 2 | 1/23/09 10:14 PM |
| Discolored service conductor, bonded subpanel | dalvares | Electrical Inspections | 3 | 11/6/08 9:44 PM |