Exclamation 200a Subpanel feeds

I have an 800 amp MDP. out of this 800 amp MDP, a 200 amp breaker feeds a 200 amp secondary main lug MDP, in this 200 amp SMDP I have TWO, 200 amp breakers feeding separate 200 amp sub panels.

This is a previous installation, and I have to make changes to the facility this is installed in.

Will this configuration create an issue with the inspector for the changes I need to make on my work in the existing 800 amp main MDP?

Thank you

Last edited by Russ Stacey; 1/5/11 at 10:39 PM..
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/6/11, 1:13 AM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: 200a Subpanel feeds

You might want to consult an electrical engineer and pull a permit.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #3  
Old 1/6/11, 6:25 AM
Russ Stacey Russ Stacey is offline
New User
 
Join Date: Jan 2011
Posts: 3
Please Note: Russ Stacey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200a Subpanel feeds

Why would I need to consult an EE to ask about existing equipment?, this is an inspection question.

Since I have already stated that my issue was with this EXISTING equipment conflicting with my NEW inspection on MY changes to the service it should be obvious,.... I already pulled a permit.

That was nothing more than a "I have no clue what this person is asking, but I MUST say something",... comment.

Anyone with some real answers like to respond?

Thank you
Reply With Quote
  #4  
Old 1/6/11, 10:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 200a Subpanel feeds

Quote:
Originally Posted by Russ Stacey View Post
Will this configuration create an issue with the inspector for the changes I need to make on my work in the existing 800 amp main MDP?
There are really no "issues" with the 200 amp breakers on the load-side of the service disconnect. I'm not to sure of what your concern is.

Though they will never likely draw their maximum capacity, the 200 amp breakers still act as disconnects for the panels they serve.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/6/11, 3:33 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200a Subpanel feeds

I think that he's questioning having one 200 amp OCPD protecting 2-200 amp panels:

Quote:
...200 amp breaker feeds a 200 amp secondary main lug MDP, in this 200 amp SMDP I have TWO, 200 amp breakers feeding separate 200 amp sub panels
There is no problem if the calculated load is 200 amps or less.
Reply With Quote
  #6  
Old 1/6/11, 9:55 PM
Russ Stacey Russ Stacey is offline
New User
 
Join Date: Jan 2011
Posts: 3
Please Note: Russ Stacey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 200a Subpanel feeds

Quote:
Originally Posted by Robert Meier View Post
I think that he's questioning having one 200 amp OCPD protecting 2-200 amp panels:

There is no problem if the calculated load is 200 amps or less.
That is correct! Now we are getting somewhere.

200amp X TWO panels, or 200 amps across both panels?

Thanks
Reply With Quote
  #7  
Old 1/6/11, 11:25 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: 200a Subpanel feeds

The biggest problem you might encounter would be possible nuisance tripping if you have heavy loads. It all depends on what you are planning on running out of those two subpanels. If you plan on running a few RTU's, a lot of exhaust fans, a Liebert and a sh*tload of lighting, you might have something to worry about. If it's just normal everyday application loads, I wouldn't worry about it.

Where do you reside?

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel Unsafe? dshewell General Inspection Discussion 4 10/25/10 7:28 PM
underamped subpanel?? wstafford Electrical Inspections 12 5/13/09 5:08 PM
Neutral/ground bond in subpanel gkeene Electrical Inspections 2 1/23/09 10:14 PM
Discolored service conductor, bonded subpanel dalvares Electrical Inspections 3 11/6/08 9:44 PM


All times are GMT -4. The time now is 5:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts