Default 220 breakers on 120 circuits?

I need an opinion from an electrician. I inspected a condo today and it had several 120 volt circuits that were attached to breakers designed for 220 circuits. For instance, one 220 breaker had the dishwasher on one leg and the disposal on the other.

I have not encountered this before and wondered if the breaker will trip properly if there is a problem on one of the circuits but the other is Okay.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #2  
Old 12/11/08, 9:55 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 220 breakers on 120 circuits?

Quote:
Originally Posted by rsole View Post
I need an opinion from an electrician. I inspected a condo today and it had several 120 volt circuits that were attached to breakers designed for 220 circuits. For instance, one 220 breaker had the dishwasher on one leg and the disposal on the other.

I have not encountered this before and wondered if the breaker will trip properly if there is a problem on one of the circuits but the other is Okay.
Rob are you sure those were on 240v breakers not on "mini twins" if you are correct then the use of a duel pole (tied handle) breaker would be wrong.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 12/11/08, 10:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: 220 breakers on 120 circuits?

Sounds like a multiwire circuit. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/11/08, 10:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 220 breakers on 120 circuits?

Depends Gerry.......could be a multiwire branch circuit with a dishwasher and disposal on a single duplex receptacle and the NEC would allow individual breakers with identified handle ties or a (2) pole breaker with common trip.

Really need more info to be sure what he is saying.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 12/11/08, 10:51 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: 220 breakers on 120 circuits?

Quote:
if you are correct then the use of a duel pole (tied handle) breaker would be wrong.
Gerry,

Around here, many electricians use a three wire with ground to power two separately protected circuits, via shared or common neutral. So, in these instances, the handles are tied also.
Reply With Quote
  #6  
Old 12/11/08, 10:53 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 220 breakers on 120 circuits?

Yeah, you know guys when I'm wrong I'm wrong, it could be correct .....


...... but I bet it isn't, pics would be real helpfull

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 12/11/08, 11:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 220 breakers on 120 circuits?

Quote:
Originally Posted by gbeaumont View Post
Yeah, you know guys when I'm wrong I'm wrong, it could be correct .....


...... but I bet it isn't, pics would be real helpfull

Regards

Gerry
Noo...Nooooo my friend...You are MOSTLY 100% right so chances are their is more to the eye then what is posted. It is easy for US to pick what if's...but you could be so correct and just think if it was a multiwire circuit for a dishwasher and a disposal actually on a tandom breaker on a single 120V buss....then he might have some REAL problems....

Sometimes Electricians are only ONE minded ( i know I am sometimes )......HI's think outside the box so keep it up brother.......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 12/12/08, 12:02 AM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 55
Default Re: 220 breakers on 120 circuits?

Robert,
Article 210.4(B) NEC. Where a multiwire branch circuit supplies more than one device or equipment (example: dishwasher/disposal) on the same yoke (duplex receptacale), a means shall be provided to disconnect simultaneously all ungrounded conductors (hot wires) supplying those devices or equipment at the point where the branch circuit originates(panel).
This protects anyone working on the circuit. If it was 2 single pole breakers ,the dishwasher circuit could be turned off, but the disposal on the same receptacle would still be energized which could cause injury to the worker.

Last edited by gevans2; 12/12/08 at 10:46 AM..
Reply With Quote
  #9  
Old 12/12/08, 8:53 AM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: 220 breakers on 120 circuits?

I may not have described the breakers properly. The panel is a Square D panel and had several breakers that have a single handle (not the type that have two handles that are tied together). A few were 220 circuits (Water heater, A/C etc) but 3 or 4 were for normal household circuits (bedroom receptacles, dishwasher, disposal etc.) and had two different circuits connected to the same breaker. The ratings on the breakers were in line with the wire sizes attached. The question is, is this acceptable ans will the breakers used this way trip properly in the event of an overload on one of the circuits.

I am attaching a photo of the type of breaker that was used (this is a different panel but the same type breaker. I am not used to seeing 110 circuits connected to breakers that are usually installed on 220 circuits.

The breakers in question are the larger ones on the left in the photo.
Attached Thumbnails
220-breakers-120-circuits-img_3337.jpg  



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #10  
Old 12/12/08, 11:03 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,116
Default Re: 220 breakers on 120 circuits?

Quote:
Originally Posted by rsole View Post
The question is, is this acceptable ans will the breakers used this way trip properly in the event of an overload on one of the circuits.

I am attaching a photo of the type of breaker that was used (this is a different panel but the same type breaker. I am not used to seeing 110 circuits connected to breakers that are usually installed on 220 circuits.

The breakers in question are the larger ones on the left in the photo.
Yes it will trip.

The code previously did not talk about disconnects for multi-wire ckts unless the two legs went to the same receptacle. You had to have the two breakers tied together or have a double pole breaker. Now, the 2008 code states that you need the origin breakers of the multi-wire ckt tied together(or two-pole) even if it's not on the same receptacle.

Judging by the dust and debris on the breakers, the ckts were probably tied in before the 2008 code came into effect. At that time it wasn't required to be on a two-pole breaker. Don't know why the person did that, maybe lack of single-pole breakers at the time.

If the two-pole breaker has its conductors sharing a neutral, it's fine. If they aren't sharing neutrals...it'll be fine, just an inconvenience if the breaker trips due to something in the bedroom and it takes out the fridge leg, also. Hope you follow.
Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook

Last edited by jwicklander; 12/12/08 at 11:50 AM.. Reason: adding info
Reply With Quote
  #11  
Old 12/12/08, 1:23 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: 220 breakers on 120 circuits?

Thanks for the information. As I mentioned, this is the first time I encountered this and at first couldn't figure out why they had so many 220 circuits and so few 110 circuits. I then noticed the labeling of the panel door and opened the panel again for a second look. I knew that this would provide 110 if wired correctly but was not sure if the single trip would work this way.

Thanks again.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #12  
Old 12/12/08, 3:11 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 220 breakers on 120 circuits?

Quote:
Originally Posted by jwicklander View Post
Yes it will trip.


Jeff
Providing that double breaker is rated correctly, probably should be 15A in this case?

John Kogel
www.allsafehome.ca
Reply With Quote
  #13  
Old 12/12/08, 4:14 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,116
Default Re: 220 breakers on 120 circuits?

Quote:
Originally Posted by jkogel View Post
Providing that double breaker is rated correctly, probably should be 15A in this case?

John Kogel
www.allsafehome.ca

If there is more than one receptacle on a 20 amp breaker, the receptacles may be rated at 15 amp or 20 amp.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Article 240 : Overcurrent Protection Article pabernathy Electrical Inspections 0 5/23/07 12:40 PM


All times are GMT -4. The time now is 1:05 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts