#1
|
|||
|
|||
|
greetings...my stubborn inquisitive streak is adament. I don't understand no neutral in 220. I've done my homework and checked every electricity site I can find but all answers only seem to answer (paraphrased) that "thats the way it is" I don't even mind being considered ignorant if I can get an answer.
My understanding: electricity seeks to work in a circuit...120 utilizes a neutral to complete that circuit back to source (and ground)...220 doesn't 'need' neutral because each pulse uses the off phase of the other side for this purpose and AC back and forth but where is the circuit since the power is only looping back to the hot bars. seems like a closed system....the only thing i can imagine so far is that the earth ground provides the only circuit path which would seem to be to be only half the safety feature desired. (bear with my lack of technical jargon) ...then if the earth ground becomes broken there is no circuit at all. now any 220 appliance I touch...I become the one and only connection to earth and therefore fry on the spot. I realize I'm missing something....just want to know what it is. thanks for all the input I've recieved....its appreciated and valuable |
| Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I will try and explain this to you. Let's start with a question, do you remember my battery analogy from a thread a few weeks ago?
|
|
#3
|
||||
|
||||
|
BPI Certified Professional Building Analyst BPI Certified Envelope Professional Infraspection Institute Certified Level II Thermographer # 8510 www.dapkusinspections.com www.chicagoinfraredthermalimaging.com www.mychicagohomeinspector.com www.commercialbuildinginspectionchicago.com Professional Infrared Network Chicago Energy Audit Aerial Infrared Inspection Certified Infrared Thermal Imaging |
|
#4
|
|||
|
|||
|
hey robert...yes i remember the battery analogy, which I could see the series picture and winding up with 3volts when combining the two 1.5v...did not understand how 'the connection point represented the neutral' (I think you said) and neither the one nor two connected batteries do anything till a circuit is completed but ok.....Im listening
thanks |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
In the battery set up if you connect meter across the two ends you will measure 3 volts. Connect the meter across the center meeting point and either end and you'll measure 1.5 volts. For the 120/240 volt system it's exactly the same as the battery setup, if you connect you meter across the two ends you will measure 240 volts. Connect the meter across the center and either end and you'll measure 120 volts. So a two wire circuit can connect to both "ends" of the transformer secondary and you will have 240 volts. The midway point between the two ends (the neutral) requires no connection to get 240 volts with only two wires. Last edited by Robert Meier; 2/22/11 at 8:37 PM.. Reason: Added Clarification |
|
#6
|
|||
|
|||
|
Quote:
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#7
|
|||
|
|||
|
robert...thanks for hanging with me, some things take me 'baby steps' to get there....the battery setup doesn't seem 'exactly the same...' to me yet because two batteries hooked in a series still have a -side and a +side on the arrangement....kind of resembling hot and neutral to me, though I know nothing of DC which is probably a whole new ballgame. so you still get no action till some sort of circuit is complete. so far in my understanding a more accurate use of the battery analogy is taking two seperate 1.5 batteries and running a wire from the + side of each to some gizmo to get 3 v it still wont do anything because theres no - wire.
hey thanks....i dont feel too bad since virtually nobody takes this on I feel I'm not asking dumb questions but difficult to answer ones. I even asked an established electrician and he just answered because 220 uses both sides and 120 only uses one....hmmmmm....ok long as youre willing to keep trying im listening |
|
#8
|
||||
|
||||
|
Quote:
|
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Also think of the two batteries in series as a power source, the same way that you would think of the three wires coming into your house panel as a source. Having said that does it make any more sense? I'm not sure if you're quoting that electrician exactly but there is no system where you would have 120 volts and 220 volts. For the sake of discussion in a single phase system get used to using 120 and 240 volts. I'm still here if you want to ask more questions. |
|
#10
|
|||
|
|||
|
yes my bad on saying 220...saw that after posting but oops too late. well i dont want to take this to the point of being annoying...i know enough to remove a panel cover and do all I need to as an inspector...and Ive done extensive home wiring for ten years (my own) and still live to tell of it so I guess I have the basics well enough to survive.....its just that Im so darn inquisitive I tenaciously pursue detaily things I dont understand.
and I just cant understand (yet...my 'ah-haaa' moment will come one way or another) and I just cant understand why each of those two sides of 240 dont insist on going 'home' to the ground and theyre happy just to feed back to the hot source...while 120 needs to circuit back to the earth (again pardon the rhetoric) at the risk of appearing dense I can not rest when something like this gets lodged upstairs. I'm thankful for the input and read closely whatever replies I receive. |
|
#11
|
||||
|
||||
|
This might help.......
The 120V does not return to ground, it returns to the power companies center tap on the transformer. Yes, this center tap is also connected to the earth ground but does not have to be to operate. Grounding and bonding is another whole subject matter that trips up most all new inspectors. In the example using the two batteries, it might help to label each end of each battery as plus and minus both since this is basically what they do in an A/C circuit. They change directions during the 60 hertz cycle. A/C waveform's are another whole lesson. If you forget the ground and just think about the two hot legs and the center tap you will get it. The center tap transformer is the whole reason we have safer residential power here vs europe, it allows us to drop the actual 240V supply in half. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The current doesn't need to "go back to earth" in a 120 volt circuit, it goes back to the utility transformer and just happens to be grounded for other reasons. It will still yield 120 volts even if it's ungrounded. Again if you think back to the battery example, say the battery is 120 volts, if I measure the voltage at each end it 120 volts, put two batteries in series and each end now measures 240 volts. Grounding plays no role in how the voltage is measured.
|
|
#13
|
||||
|
||||
|
BPI Certified Professional Building Analyst BPI Certified Envelope Professional Infraspection Institute Certified Level II Thermographer # 8510 www.dapkusinspections.com www.chicagoinfraredthermalimaging.com www.mychicagohomeinspector.com www.commercialbuildinginspectionchicago.com Professional Infrared Network Chicago Energy Audit Aerial Infrared Inspection Certified Infrared Thermal Imaging |
| Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
all explanations presented to my inquiries are read carefully and pondered upon, even sites recommended, and its like a dimmer switch is being turned up....not a light bulb over the head like in cartoons....but the switch is going up (ie its moveing towards ahaa moment) maybe my concept of how electricity works in general is skewed.
Mikes concept of 'how electricity works'....at super basics: (look beyond any wrong wording here...I don't care so much about getting terminology correct as understanding the concept) I've always thought, and this concept was buttresed by my ITA elec instructor (and I must have missed 'the rest of the story')...that electric energy has one thing in mind and that is to somehow, eventually 'get home' which is in the earth where it can dissipate. I've been also presented with the analogy of a water filled hose with a pump on each end each pulsing on the others off cycle (AC) this makes sense too....but just leads me back to that darn ? of why the uninsulated neutral guy line on the supply line is not energized but wait...I didnt say that...don't want to go there yet. So anyway I have this thing in my head that elec is always seeking to get home and looks for the easist path....meaning I can become the short circuit by grabbing the wrong thing and providing that easier path. So If it can be pointed out where that mindset is incorrect...then I will have enough food for thought I believe to sort this thing out. Sure do appreciate all the input....Im 'getting' things I have not been able to in the past. You guys rock!! and hey I hate to sound like a guy sitting on a high stool wearing a dunce cap most other areas I have no problem with but this electric gig is just a sonofagun to me and i love learning. |
|
#15
|
||||
|
||||
|
The red wire acts as the black wire's neutral for half of the cycle and the black wire acts as the neutral for the red wire for the other half of one complete cycle.
You need to understand this concept on multi wire circuits like kitchen plugs where you only need one neutral wire for two hot wires. In this situation it is critical that the red and black wires are not on the same bus or the single neutral wire will be carrying double the amperage. Rick Strand, CPI CAHPI Associate Strand Home Inspections Inc. Calgary, Alberta, Canada Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Sump Pit/Pump Question | Joey D'Adamo | Plumbing Inspections | 4 | 11/26/08 1:04 PM |
| Sizing & Neutral Question? | thejnicki | Electrical Inspections | 18 | 2/15/07 7:00 PM |
| Plumbing vent Routing Question | kweiss | Plumbing Inspections | 7 | 11/1/06 9:57 PM |
| Answer to a common question about GFCI's | jtedesco1 | Electrical Inspections | 4 | 1/12/06 9:29 PM |