Default 220v neutrals

Should the 220 volt neutrals be on the same buss as 110v neutrals in a sub-panel?

220v-neutrals-086.jpg
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/30/10, 9:08 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 220v neutrals

One you go past the service disconnect the grounded and grounding conductor must be separate, this applies to the sub panel. This would apply to both 120 volt and 240 volt circuits.
Reply With Quote
  #3  
Old 10/30/10, 9:17 AM
Calvin D. Cowles's Avatar
Calvin D. Cowles Calvin D. Cowles is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newnan, Ga
Posts: 46
Default Re: 220v neutrals

So how do I tell if the "white" wires on the 240 are neutrals or grounds or needed at all?
Reply With Quote
  #4  
Old 10/30/10, 9:20 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 220v neutrals

Just wondering, since it's hard to tell from the photo but where does that white conductor originate? Does it come from a cable or is it a pigtail from a circuit breaker?

The white conductor should never be a grounding conductor and should terminate on the neutral bus in a sub panel.
Reply With Quote
  #5  
Old 10/30/10, 9:22 AM
Calvin D. Cowles's Avatar
Calvin D. Cowles Calvin D. Cowles is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newnan, Ga
Posts: 46
Default Re: 220v neutrals

There are 3 240v circuits and 3 white conductors (black and reds connected to breakers) connected to the ground buss.
Reply With Quote
  #6  
Old 10/30/10, 9:45 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 220v neutrals

Since this a subpanel the neutrals must be connected to the neutral bus in the panel not the equipment grounding bus. By connecting them to the EGC bus neutral current is now flowing on the EGC of the subpanel feeder back to its source. Under normal conditions current should never flow on the EGC.
Reply With Quote
  #7  
Old 10/30/10, 10:30 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: 220v neutrals

Quote:
Originally Posted by Robert Meier View Post
Since this a subpanel the neutrals must be connected to the neutral bus in the panel not the equipment grounding bus. By connecting them to the EGC bus neutral current is now flowing on the EGC of the subpanel feeder back to its source. Under normal conditions current should never flow on the EGC.

Robert's got it...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 10/30/10, 11:08 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 220v neutrals

Robert is correct, but to help clarify -

The neutral conductor of a 240V circuit can/will carry current from the unbalanced circuit. So even in a 240V circuit, the neutral is a current-carrying conductor and must remain "ungrounded" until it has returned to the service equipment.

Most 240V circuits installed today will require four conductors - H+H+N+G.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/30/10 at 3:05 PM..
Reply With Quote
  #9  
Old 10/30/10, 11:35 AM
Calvin D. Cowles's Avatar
Calvin D. Cowles Calvin D. Cowles is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newnan, Ga
Posts: 46
Default Re: 220v neutrals

Thanks everyone!!!
Reply With Quote
  #10  
Old 10/30/10, 11:53 AM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: 220v neutrals

In your picture I see other nuetrals and grounds and the terminal it's on looks green in the picture. So it looks like they are sending the white wire to ground since in subpanel the nuetral and ground should not be bonded. It is ok to have 115 and 240 terminate in the same place. You don't say what it's running but things like stoves and dryers now require a 4 wire system since they have 115v controls and with a 3 wire it would have a false ground. Either way in your picture it looks like there is at least one issue going on.
Reply With Quote
  #11  
Old 10/30/10, 8:06 PM
Calvin D. Cowles's Avatar
Calvin D. Cowles Calvin D. Cowles is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newnan, Ga
Posts: 46
Default Re: 220v neutrals

House built in 1990. Do you recommend to your clients upgrading old 3 wire (3 prong plugs for dryer and stove) to 4 wire systems? The 3 circuit is the AC condenser.
Reply With Quote
  #12  
Old 10/30/10, 11:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 220v neutrals

No, I do not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring for 220v. circuits? Unregistered AskNACHI.org Inspection Questions Forum 30 9/6/09 11:05 AM
Main panel grounds & neutrals jfrederick Electrical Inspections 15 3/1/09 10:04 AM
pole on double tapped neutrals rdemott Electrical Inspections 10 11/16/08 10:49 PM
Neutrals nbhi Electrical Inspections 8 8/9/08 1:10 AM
Electrician signs off 'ganged neutrals'...now what? mgault Electrical Inspections 16 6/2/07 11:09 PM


All times are GMT -4. The time now is 5:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts