Default 220VAC Baseboard heaters no returning neutrals?

I understand that in some 220 VAC applications, the neutral can be sized smaller than the conductors supplying power to the device. But I must admit I've never seen this type of installation before.

100 Amp primary distribution panel with a 60 amp remote distribution panel below. The panels are bonded and the bonding screw on the remote neutral bar was removed. No equipment grounds or neutral conductors present in the remote panel. The label on the remote panel state the 220 VAC circuits supply power to the electric baseboard heaters on the second floor. The conduit was EMT. If neutrals are required, do they need to terminate in the same panel as the source?
Attached Thumbnails
220vac-baseboard-heaters-no-returning-neutrals-sam_2158.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/31/11, 9:10 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: 220VAC Baseboard heaters no returning neutrals?

Quote:
Originally Posted by gliebig View Post
I understand that in some 220 VAC applications, the neutral can be sized smaller than the conductors supplying power to the device. But I must admit I've never seen this type of installation before.

100 Amp primary distribution panel with a 60 amp remote distribution panel below. The panels are bonded and the bonding screw on the remote neutral bar was removed. No equipment grounds or neutral conductors present in the remote panel. The label on the remote panel state the 220 VAC circuits supply power to the electric baseboard heaters on the second floor. The conduit was EMT. If neutrals are required, do they need to terminate in the same panel as the source?
The neutral is not needed for a 220 volt circuit.

Phase to Neutral gives 120 volt.

L-1 to L-2 gives 220 volts.




You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI


Last edited by mlarson; 7/31/11 at 9:14 AM..
Reply With Quote
  #3  
Old 7/31/11, 9:20 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: 220VAC Baseboard heaters no returning neutrals?

That's what I thought, but what about the two 110 volt circuits on the right side of the panel? Still no neutrals... and the ground is the EMT?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 7/31/11, 9:33 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: 220VAC Baseboard heaters no returning neutrals?

Quote:
Originally Posted by gliebig View Post
That's what I thought, but what about the two 110 volt circuits on the right side of the panel? Still no neutrals... and the ground is the EMT?
I see your problem.

Need more info.

Does the EMT that goes out to feed the 120 circuits have any white wires in it?

If not they are likely using the EMT for the neutral return. That's a no go.

I'd call it as "requires repair by qualified persons".

It would be interesting to open the outlets on the 120 circuits to see what's being done. They would have had to tie the neutral on the receptacle to the metal box for it to work.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 7/31/11, 9:44 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 220VAC Baseboard heaters no returning neutrals?

Maybe a handle tie is missing for the two single pole breakers which feed a 240V heating element.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #6  
Old 7/31/11, 9:59 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: 220VAC Baseboard heaters no returning neutrals?

I thought about that. The branch circuits are two different colors and are routed through the main panel and different conduit. I did not pull apart the heater to verify the wiring (going above the SOP) or verify if the baseboard heaters are 220 VAC or 110 VAC. There are no neutrals in either case but it might be possible that the neutral(s) for these two circuits were terminated in the primary panel. That was the reason for the second half of my first question. Do the neutrals have to be terminated in the same panel as the source?
Attached Thumbnails
220vac-baseboard-heaters-no-returning-neutrals-sam_2153.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #7  
Old 7/31/11, 10:10 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: 220VAC Baseboard heaters no returning neutrals?

Greg they are all marked Electric Heat.

I think you may be missing a handle tie as in 4 220 circuits.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 7/31/11, 11:23 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 220VAC Baseboard heaters no returning neutrals?

Quote:
Originally Posted by gliebig View Post
The branch circuits are two different colors and are routed through the main panel and different conduit ... it might be possible that the neutral(s) for these two circuits were terminated in the primary panel.
If its a 240V circuit it needs a handle tie and both hot wires need to be in the same conduit. If its two 120V circuits the neutral wires for those circuits must extend to the sub-panel, and those neutral wires also have to be in the same conduit as the corresponding hot wires for the entire run. Let a sparky figure out which case applies and repair accordingly ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Baseboard Heaters bhartley Inspecting HVAC Systems 11 4/8/07 2:37 PM
Water heaters in attics phughes Plumbing Inspections 1 1/11/07 11:08 AM


All times are GMT -4. The time now is 5:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts