Default 240 volt check, Question.

As Home Inspector how do we check the 240 volt dryer outlet ?

Is there a tester similar to the device we stick into the 120 volt outlet

to check for correct wiring ?


David
Reply With Quote
  #2  
Old 1/13/09, 2:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: 240 volt check, Question.

Use your NCVD to verify two 120 volt contacts.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 1/13/09, 3:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 240 volt check, Question.

I use a Wiggy




"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 1/13/09, 3:55 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: 240 volt check, Question.

Quote:
Originally Posted by mlarson View Post
I use a Wiggy

Same Here...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #6  
Old 1/13/09, 4:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: 240 volt check, Question.

The wiggy (or similar device) is certainly more reliable and accurate, but the NCVD is quick and simple for determining if voltage is even present. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 1/13/09, 4:16 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: 240 volt check, Question.

Quote:
Originally Posted by jpope View Post
The wiggy (or similar device) is certainly more reliable and accurate, but the NCVD is quick and simple for determining if voltage is even present. . .
Agreed.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 1/13/09, 4:23 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: 240 volt check, Question.

Quote:
Originally Posted by jpope View Post
The wiggy (or similar device) is certainly more reliable and accurate, but the NCVD is quick and simple for determining if voltage is even present. . .
it certainly is and probably all that is necessary for Our purpose...I just happen to have had the wiggy for a couple thousand years so i use it....just habit.....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #9  
Old 1/13/09, 4:35 PM
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 267
Default Re: 240 volt check, Question.

Thanks everybody....
Reply With Quote
  #10  
Old 1/14/09, 9:57 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 240 volt check, Question.

With a Wiggy you will be able to verify grounding, with a NC tester you will not.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Procedural Inspection Checklist bgromicko Electrical 11 3/9/08 12:47 AM
Procedural Inspection Checklist bgromicko General Inspection Discussion 0 3/8/08 11:40 AM
inspection procedural checklist bgromicko Electrical 24 3/2/08 11:00 AM
Let's talk ESOP rcooke General Inspection Discussion 231 2/22/08 9:55 PM


All times are GMT -4. The time now is 10:49 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts