Hey Guys-

The two double-pole 30 amp breakers on the left share a neutral for two of the AC units. Under the 2008 code, these should be tied together, correct? This house was in 1997 so in that case would you call it as an electrical upgrade? The data plate also said max breaker size of 25 amp and these were on 30 amps.

Thanks

Kenny
Attached Thumbnails
240v-shared-neutral-gedc4522.jpg   240v-shared-neutral-gedc4512.jpg   240v-shared-neutral-gedc4526.jpg   240v-shared-neutral-gedc4524.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/16/11, 1:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 240V Shared Neutral

Those units should not require a neutral so it's likely that the white conductor is actually an EGC (would need to see terminations on both ends). Also since this in is not the service disconnect the neutral and grounds require separation. The 30 amp OCPD is no good with a MaxOCPD of 25 amps. Not sure what you're asking about the MWBC's.
Reply With Quote
  #3  
Old 10/16/11, 1:52 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: 240V Shared Neutral

There are no neutrals in 240vac hvac circuits.

Now that 120vac circuit that is double tapped is another issue. It is using equipment ground as a neutral. You call it as you see fit.

I see irrigation equipment added on like this all the time.
I call them back and tell them to add a neutral if they want to use the HVAC service. That means they need to add a neutral buss to separate the ground buss because there is none in those panels.

What is the chance for the ground to be utilized on an HVAC service?
100% when any component fails electrically.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 10/16/11, 1:59 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 240V Shared Neutral

As long as the panel neutral is connected to the neutral bus ahead of the feeder that part of the installation is OK. The EGC can be the metallic offset nipple. That means that a separate bus for the EGC's is needed, bonded to the enclosure. That re-identified black conductor, with the white tape, is required to be #4 or larger or it needs white insulation. Looks like a #8.

Reply With Quote
  #5  
Old 10/16/11, 2:45 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: 240V Shared Neutral

Quote:
Originally Posted by Robert Meier View Post
Those units should not require a neutral so it's likely that the white conductor is actually an EGC (would need to see terminations on both ends).
Thanks Robert and Dave. The inside panel had MWBCs and when I saw this I was thinking the same. I didn't think about the fact that the white conductor was a EGC since the ACs wouldn't have a neutral.

But yes, I had called it out anyway because of the double-tapped breaker and lack of separation. Thanks!



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Shared neutrals Ian Gills Electrical Inspections 17 1/8/08 12:22 AM
Shared Neutral rgallahorn Electrical Inspections 10 1/6/08 1:39 PM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 5:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts