Default 25 Amp Breaker

Are 25A breakers readily available. The reason I ask is that the A/C I looked at today had a name plate that said max fuse/breaker size 25A but there was a 30A breaker in the panel.
Here's one answer I found but I don't know that I believe it.
http://en.allexperts.com/q/Electrica...elp-C-Unit.htm
Reply With Quote
  #2  
Old 9/24/08, 4:55 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 25 Amp Breaker

John,

25 amp breakers are available, but are generaly a "non-prefered" size, that is to say that few electricians would have them on the truck so they commonly use a 30 amp.

Guess what it's still wrong, if the manufacturer calls for a 25, then it should have a 25, the NEC clearly states that it has to be installed in accordance with the manufacturers instructions.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 9/24/08, 4:59 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: 25 Amp Breaker

Are you calling out the wrong size breaker per manufacturer specs? 25 MAX? If so, then you are right, let someone else say its cool to put a 30 on it. It may not be a big deal but let the electrician tell them that. State what you see. IMO, you done good! I probably get at least 3 oversized breakers each week.

I didn't read the entire post you posted but it sounds like you are comparing apples to oranges. They are referencing wire sizes not MAX allowable breaker by manufacturer. I will go back and re-skim through it



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #4  
Old 9/24/08, 5:29 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 25 Amp Breaker

I cite it on about 50% of every house I inspect. I'm in the habit when I look at a condensing coil data plate to state into my voice recorder the max breaker size. Here's what I say:

"A *XXX* amp breaker provided over-current protection to an air conditioner which is rated for a maximum *xxx* amp breaker. This circuit is thought to be "over-fused" and needs service. Failure to correct the issue may damage the unit and/or result in a fire."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 9/24/08, 9:57 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 25 Amp Breaker

Quote:
Originally Posted by jallingham View Post
Are 25A breakers readily available. The reason I ask is that the A/C I looked at today had a name plate that said max fuse/breaker size 25A but there was a 30A breaker in the panel.
Here's one answer I found but I don't know that I believe it.
http://en.allexperts.com/q/Electrica...elp-C-Unit.htm

Was there also a fused disconnect?
Reply With Quote
  #6  
Old 9/24/08, 10:17 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: 25 Amp Breaker

The size is too large, but once again it says the MAXIMUM sized breaker is 25, is the minimum 20 amp by chance?
Reply With Quote
  #7  
Old 9/25/08, 10:03 AM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: 25 Amp Breaker

There was a disconnect but not a fused disconnect.
I didn't notice a minimum breaker size listed.
Reply With Quote
  #8  
Old 9/25/08, 10:25 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 25 Amp Breaker

Quote:
Originally Posted by rhensel View Post
The size is too large, but once again it says the MAXIMUM sized breaker is 25, is the minimum 20 amp by chance?
I would suspect that that compressor would be quite happy on a 20 amp breaker, as when running normally it should only be drawing around 75% or less of the maximum, which would be 18.75 amps.

Start up loads should trip a 20 either as the load doesn't (or shouldn't) last long enough.

More info is really needed as to the RLA of the unit.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 9/25/08, 11:03 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 25 Amp Breaker

I agree with the Coon Hat Fellow........if the nameplate says 25A Max then that is what should be installed. The NEC clearly lists a 25A breaker as a standard breaker size based on 240.6

240.6 Standard Ampere Ratings.
(A) Fuses and Fixed-Trip Circuit Breakers.
The standard
ampere ratings for fuses and inverse time circuit
breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50,
60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300,
350, 400, 450, 500, 600, 700, 800, 1000, 1200, 1600, 2000,
2500, 3000, 4000, 5000, and 6000 amperes. Additional
standard ampere ratings for fuses shall be 1, 3, 6, 10, and
601. The use of fuses and inverse time circuit breakers with
nonstandard ampere ratings shall be permitted.

So call it out and let the electrician take care of it. What we dont want to do is assume it is ok when it could have been placed on the circuit because of a problem with a piece of equipment that had to be increased to a 30A for some reason we as HI's are not aware of during our brief inspection process.




Paul W. Abernathy
Reply With Quote
  #10  
Old 9/25/08, 11:21 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 25 Amp Breaker

Quote:
What we dont want to do is assume it is ok when it could have been placed on the circuit because of a problem with a piece of equipment that had to be increased to a 30A for some reason we as HI's are not aware of during our brief inspection process.
Agreed, the braker MAY have been replaced due to a worn out compressor motor that was overdrawing and tripping the breaker, however it is more likely that a more modern replacement AC was installed requiring a smaller breaker, and that was over looked.

I as others have said see that a lot.

Regards

Gerry

BTW, Leave the Racoon out of this fella



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #11  
Old 9/25/08, 12:02 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,391
Default Re: 25 Amp Breaker

I don't give opinions on anything electrical, and Gerry knows why. Just for the record, that not a racoon hat but a picture of Gerry with long hair and a pony tail taken in the 70's.
Reply With Quote
  #12  
Old 9/25/08, 7:41 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: 25 Amp Breaker

Thanks for all your help guys.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 5:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts