Default 3 light tester?

Most, not all, 3-prong receptacles, showed correct using two different 3 light testers. Problem they were only wired with 12-2, no ground connection at receptacle. I opened one and it appears there is a ground clipped off at entrance. There are only 2 grounds at 1 of 2 panels, they are marked for AC. Most GFCI's tested open ground as did a few rec.

Pics are of each panel and rec. in question.
Attached Thumbnails
3-light-tester-hpim8105.jpg   3-light-tester-hpim8129.jpg   3-light-tester-hpim8209.jpg   3-light-tester-hpim8212.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/30/10, 2:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 light tester?

It's likely that the cut of EGC in the metal box is making contact with the box so when the recpetacle is screwed to the box the tester shows that it is grounded. Technically it is grounded just not properly or to code. Also the white conductors used as ungrounded conductors in the raceway are a violation. There are a few other visible problems here as well.
Reply With Quote
  #3  
Old 10/30/10, 2:58 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: 3 light tester?

Reason 23 why I think Romex sucks.
At least with conduit you have ground built in.

I did Will county yesterday and the stuff was piled up in a ball in the attic but it would take some fancy bending to mess it up with pipe that way.

How do they get ground in now, Chris?
Reply With Quote
  #4  
Old 10/30/10, 3:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3 light tester?

Metal screw through the receptacle to the grounded metal box = a grounded outlet according to the three-light tester.

If you were using a real tester, you would likely have found the "ground" to be inadequate.

A SureTest will give an "open-ground" indication if there is too much impedance on the grounding connection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/30/10, 3:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 light tester?

Quote:
Originally Posted by jpope View Post
A SureTest will give an "open-ground" indication if there is too much impedance on the grounding connection.
How sensitive is that tester? I would seem that if the clamp were screwed tightly against the bare EGC and the device mounting screws were tight the test would pass. Am I correct? I've never used the SureTest.
Reply With Quote
  #6  
Old 10/30/10, 3:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3 light tester?

Possibly. Anything over 3 ohms resistance on the egc will register as an open-ground. A solid connection will register as a proper ground.

If resistance is too low (less than 0.01 ohms) on the neutral, it will indicate a false ground.

The SureTest is not "fool-proof," but it is a far superior tool than the dummy-lights.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 10/30/10, 3:14 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 light tester?

Quote:
Originally Posted by jpope View Post
Possibly. Anything over 3 ohms resistance on the egc will register as an open-ground. A solid connection will register as a proper ground.

If resistance is too low (less than 0.01 ohms) on the neutral, it will indicate a false ground.

The SureTest is not "fool-proof," but it is a far superior tool than the dummy-lights.

Thanks for the info.
Reply With Quote
  #8  
Old 10/30/10, 3:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3 light tester?

Correction - I just looked at the specs and it will register an open-ground as anything above 1.5 ohms resistance on the egc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 10/30/10, 3:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 3 light tester?

Quote:
Originally Posted by Robert Meier View Post
It's likely that the cut of EGC in the metal box is making contact with the box so when the recpetacle is screwed to the box the tester shows that it is grounded. Technically it is grounded just not properly or to code. Also the white conductors used as ungrounded conductors in the raceway are a violation. There are a few other visible problems here as well.
What other problems? I'm aware of white not properly identified, and a few double taps. Here is a better pic of panel #2. There are 2 panels each fed separately from meter. Note in other panel, in first post, there are no grounding conductors, yet I tested most all rec. and most tested correct. I wish I would have pulled more. Is it possible all metal boxes are connected with a grounding conductor?
Attached Thumbnails
3-light-tester-hpim8121.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 10/30/10 at 3:41 PM..
Reply With Quote
  #10  
Old 10/30/10, 3:46 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 light tester?

Photo 1 has an EGC and neutral under one screw. Photo 2 the aforementioned white ungrounded conductors in a raceway. Is the panel in photo 2 a subpanel or a service? If it's a service I can't see the main bonding jumper between the neutral and the enclosure. Many unsecured cables.
Reply With Quote
  #11  
Old 10/30/10, 3:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3 light tester?

Quote:
Originally Posted by ccurrins View Post
Is it possible all metal boxes are connected with a grounding conductor?
Very unlikely.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 10/30/10, 4:02 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 3 light tester?

Quote:
Originally Posted by Robert Meier View Post
Photo 1 has an EGC and neutral under one screw. Photo 2 the aforementioned white ungrounded conductors in a raceway. Is the panel in photo 2 a subpanel or a service? If it's a service I can't see the main bonding jumper between the neutral and the enclosure. Many unsecured cables.
each panel is wired as a seperate service panel. Unless ther is a disconnect in the box above panel, first time I've seen this.

I noted EGC and neutral/one screw, loose cables, and rust in panel. Regarding age of panel, defects I've posted, would you as an electrician warrant for further inspection and repair?
Attached Thumbnails
3-light-tester-hpim8166.jpg   3-light-tester-hpim8168.jpg   3-light-tester-hpim8092.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #13  
Old 10/30/10, 4:03 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 3 light tester?

My trester, which is an ideal brand, occasionally will show a weak ground light in this scenario. I can sometimes wiggle loose plugs and the light will fade in and out.
Other times I actually had a faint light, and when I removed the outlet from curiosity, found that the box itself was causing the light to come on very dim. There was no grounding wire, but the metal box was providing the tester with a faint source of ground.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/30/10, 4:06 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 3 light tester?

Quote:
Originally Posted by jpope View Post
Very unlikely.
Thanks, that was I'm thinking. I noticed a few EGC's at panel 2, none in panel 1. Home built in 1969, original service. With defects I've posted would you recommend replace/repair by an electrical contractor?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #15  
Old 10/30/10, 4:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 light tester?

Quote:
Originally Posted by ccurrins View Post
each panel is wired as a seperate service panel. Unless ther is a disconnect in the box above panel, first time I've seen this.

I noted EGC and neutral/one screw, loose cables, and rust in panel. Regarding age of panel, defects I've posted, would you as an electrician warrant for further inspection and repair?

Wow, after looking at the new photo's I would say that this service is a nightmare.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flickering CFL jallingham Electrical Inspections 34 12/5/08 2:40 PM
Trouble Shooting the Simple Light Bulb mcyr Electrical Inspections 20 1/6/08 3:47 AM
End of the light bulb as we know it!! mcyr General Inspection Discussion 3 12/19/07 3:42 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
How many forum members to change a light bulb? kshepard Miscellaneous Discussion for Inspectors 9 8/2/06 9:56 AM


All times are GMT -4. The time now is 5:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts