Default 3 prong plug how do I write it up?

I often see 3 prong plugs wrongly installed. but yet have to do a proper written report as a certified residential building inspector.
I need clarification.
Sorry but the photo examples did not come up right.
The photo is correct in this image.
I see the opposite 50 percent of the time.

[ATTACH]Attachment 40059[/ATTACH]



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:37 PM..
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/9/10, 4:46 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3 prong plug how do I write it up?

Not sure about Canada but here if you're saying that the ground on the top (up) is incorrectly installed then you're mistaken. There is no NEC wording that dictates the orientation of the ground prong on a receptacle. Is this what you want to write up or is it something else?
Reply With Quote
  #3  
Old 11/9/10, 5:52 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by Robert Meier View Post
Not sure about Canada but here if you're saying that the ground on the top (up) is incorrectly installed then you're mistaken. There is no NEC wording that dictates the orientation of the ground prong on a receptacle. Is this what you want to write up or is it something else?
Thank you Mr.Meire
I know the right way is to have the ground up as to avoid contact from any ( conducting ) object falling down the wall plate and would be moved and somewhat unable to touch both bottom connections simultaneously.
If not installed correctly it might case a short or worse injury and death.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #4  
Old 11/9/10, 6:35 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by ryoung7 View Post
Thank you Mr.Meire
I know the right way is to have the ground up as to avoid contact from any ( conducting ) object falling down the wall plate and would be moved and somewhat unable to touch both bottom connections simultaneously.
If not installed correctly it might case a short or worse injury and death.
As Robert stated, there is nothing in the NEC regarding orientation.
The theory that the ground prong will stop shorts, is good, providing that you are using a three prong plug.

For two prong plugs, it doesn't really matter.
Reply With Quote
  #5  
Old 11/9/10, 6:36 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: 3 prong plug how do I write it up?

Robert
I think it is a preference, In commercial you often find the ground on top and residential on the bottom



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 11/9/10, 7:17 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: 3 prong plug how do I write it up?

Thank you Mr. Van De Ven.
I have to look because its my understanding that homes of a certain age must be fitted with 3 prong.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #7  
Old 11/9/10, 8:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3 prong plug how do I write it up?

If it was sideways, as on many cabinet back-splashes, would that be wrong also???



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 11/9/10, 8:17 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by jfunderburk View Post
If it was sideways, as on many cabinet back-splashes, would that be wrong also???
I am asking a civil question.
Like to here and have read sensible ones SIR.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 11/9/10, 8:29 AM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by jfunderburk View Post
If it was sideways, as on many cabinet back-splashes, would that be wrong also???
See my answer above.
Also, the OP is in Canada. Canadas codes vary from the NEC in several areas.

As for grounded receptacles, I'd have to look that up Robert.
1975 NEC section 210-7, was the first year that all 15 and 20 amp receptacles in residential occupancies, were required to be the grounding type.
Reply With Quote
  #10  
Old 11/9/10, 9:08 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: 3 prong plug how do I write it up?

Thank you Mr.Van De VEN.
That is what I am asking for.
I have a code book and more questions to ask the RBQ before I set out on my new carrier.
Ontario code and going out this week to ask the government how up to date it is.
Mr.R Coole was kind to give it to me.
He is a class act.
Thanks all.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 11/9/10, 10:15 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: 3 prong plug how do I write it up?

Robert,

Time was that the ground being on the top was indicated on the receptacle itself, with the word "top" at the end that the manufacturer recommended be unstalled skywards. In time, the word was removed from the pressing.

As to Joe Funderbunk's question, although tounge-in-cheek...it is a valid one.

No need to have such a large chip on your shoulder.
Reply With Quote
  #12  
Old 11/9/10, 10:27 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3 prong plug how do I write it up?

In new construction, the one receptacle in a room where the grounding pin is on top, is the receptacle controlled by a wall-switch.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 11/9/10, 10:29 AM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by jpope View Post
In new construction, the one receptacle in a room where the grounding pin is on top, is the receptacle controlled by a wall-switch.
I see that a lot here.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/9/10, 10:48 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by jfunderburk View Post
If it was sideways, as on many cabinet back-splashes, would that be wrong also???
If the receptacle was posidioned sideways then the neutral should be up. In Gatineau, most receptacles are positioned with the ground up.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #15  
Old 11/9/10, 11:27 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: 3 prong plug how do I write it up?

Quote:
Originally Posted by jfarsetta View Post
Robert,

Time was that the ground being on the top was indicated on the receptacle itself, with the word "top" at the end that the manufacturer recommended be unstalled skywards. In time, the word was removed from the pressing.

As to Joe Funderbunk's question, although tounge-in-cheek...it is a valid one.

No need to have such a large chip on your shoulder.
I worked several different construction projects in the same hospital over 2 decades.

Depending on the date of the new building project, they were installed one way or the other.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
HELP! What do you call a 3 prong male plug with a cord. gromicko Electrical Inspections 5 1/9/09 12:33 AM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 10:41 PM


All times are GMT -4. The time now is 5:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts