Have any of you ever seen this...

I was inspecting a condo the other day and found the following at an AFCI protected receptacle in a bedroom...

*3-prong tester indicated correct polarity and ground
*Idea analyzer indicated correct polarity with no ground (not a false ground)
*Idea analyzer successfully tripped the AFCI

Any idea what's going on?



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
  #2  
Old 2/5/09, 9:14 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 3-Prong vs. Idea Analyzer

If the 3-light tester has a dim ground indication that is a fault condition (high resistance). This may not be noticeable unless you are tuned into looking for it.

The other tester probably indicates "no ground" if the ground resistance is above a certain level.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 2/5/09, 9:16 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: 3-Prong vs. Idea Analyzer

Quote:
Originally Posted by dsorge View Post
Have any of you ever seen this...

I was inspecting a condo the other day and found the following at an AFCI protected receptacle in a bedroom...

*3-prong tester indicated correct polarity and ground

Any idea what's going on?
When is the last time you "tested" the "tester"?

I only use 3-prongs as a quick check to see if power is present, and when testing gfci/afci as a visual on multiple receps. Don't trust them for anything else. Seems like I had to replace them all the time. Stick with the analyzer.

Jeff
Reply With Quote
  #4  
Old 2/5/09, 10:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3-Prong vs. Idea Analyzer

Quote:
Originally Posted by bking View Post
The other tester probably indicates "no ground" if the ground resistance is above a certain level.
That's your answer. The SureTest is much more sensitive and much more accurate than the three-light tester.

A grounding connection is not needed for the AFCI testing feature to perform its function and trip the breaker.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
TPI 712 Flue Gas Analyzer bsmith Inspection Classifieds 1 3/31/09 6:54 AM
Two Prong Outlets jallingham Electrical Inspections 22 6/27/07 2:07 AM
2 prong and 3 prong? gbrasseur Electrical Inspections 4 3/2/07 4:50 PM
Two prong outlets and GFCI's crichiii Electrical Inspections 8 3/15/06 10:41 PM