Default 3-Wire Feeder to Distribution Panel

Hey Guys-

This was in a home built in 1991. The service panel was located on the exterior of the home with a 175 amp breaker. The interior distribution panel was located on the opposite side of the home in the basement. It was fed by a 3-wire feeder, not in a metallic raceway. So the EGCs and the grounded conductors were not isolated from each other and they connected the two together in the same lugs.

My question: Is it possible to correctly bond and ground a distribution panel with only a 3-wire feeder? Thanks.

Kenny
Attached Thumbnails
3-wire-feeder-distribution-panel-gedc0550.jpg   3-wire-feeder-distribution-panel-gedc0551.jpg   3-wire-feeder-distribution-panel-gedc0674.jpg   3-wire-feeder-distribution-panel-gedc0675.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/23/11, 2:22 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-Wire Feeder to Distribution Panel

Where does the panel to the right of the meter get's its supply from?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 3/23/11, 2:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-Wire Feeder to Distribution Panel

Discounting the exterior panel to the right, I would call the panel to the left simply a disconnect with OCP for the long feeder to the main panel in the basement. Therefore the basement panel would be wired correctly (with the exception of double-tapped neutrals). That's my opinion. We'll see what others think.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/23/11, 2:31 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: 3-Wire Feeder to Distribution Panel

Quote:
Originally Posted by jfunderburk View Post
Where does the panel to the right of the meter get's its supply from?
I don't know. It appeared that it was tapped into the meter...but that's only speculation. The other feeder on the main distribution panel went to an attached garage distribution panel. The first pic below is the distribution to the right of the meter. The second pic is the distribution panel in the garage.
Attached Thumbnails
3-wire-feeder-distribution-panel-gedc0556.jpg   3-wire-feeder-distribution-panel-gedc0712.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 3/23/11 at 2:35 PM..
Reply With Quote
  #5  
Old 3/23/11, 2:34 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-Wire Feeder to Distribution Panel

Quote:
Originally Posted by krigler View Post
I don't know. It appeared that it was tapped into the meter.
Probably so. If that's the case, flipping the disconnect to the left and the 2 or 3 breakers to the right would kill all the power to the home and I don't see a problem with that.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 3/23/11, 2:35 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 3-Wire Feeder to Distribution Panel

Quote:
Originally Posted by jfunderburk View Post
Discounting the exterior panel to the right, I would call the panel to the left simply a disconnect with OCP for the long feeder to the main panel in the basement. Therefore the basement panel would be wired correctly (with the exception of double-tapped neutrals). That's my opinion. We'll see what others think.
With the service disconnect being at exterior the panel in basement is a remote distribution (sub) panel, and should be wired as such with neutrals isolated.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 3/23/11, 3:12 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-Wire Feeder to Distribution Panel

The 3 wire cable to the interior panel is incorrect. It should have been 4 wires. The disconnect to the left of the meter is the service equipment.

The only way that would have been proper would be if it were in a detached building from the service with no metallic paths between the two buildings.
Reply With Quote
  #8  
Old 3/23/11, 3:53 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-Wire Feeder to Distribution Panel

Wow, if I had all day I could give you a list of all of the visible violations in this group of photo's.
Reply With Quote
  #9  
Old 3/23/11, 4:03 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 3-Wire Feeder to Distribution Panel

Quote:
Originally Posted by Robert Meier View Post
Wow, if I had all day I could give you a list of all of the visible violations in this group of photo's.
Hey it's been this way since 1991.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 3/23/11, 4:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3-Wire Feeder to Distribution Panel

The answer to your question (as others have indicated) is no.

The EGC to the interior sub panel is now a current-carrying conductor (as a neutral), and to make matters worse, it's a bare conductor. Where does the additional set of feeders go to or come from?

The panel to the right of the meter is (apparently) tapped directly to the SEC's in the meter cabinet. So this panel is essentially part of the service equipment. I'd be curious to see the connections.

Quite a mess you've got there.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 3/23/11, 6:35 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: 3-Wire Feeder to Distribution Panel

Then the panel in the garage is also incorrect. needs four wire feed.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #12  
Old 3/23/11, 7:47 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: 3-Wire Feeder to Distribution Panel

Quote:
Originally Posted by jpope View Post
Where does the additional set of feeders go to or come from?
Jeff, the second set of feeders in the main (big) distribution panel goes to one of the smaller distribution panels in the garage. The second picture in my second post above.

Thanks for all the feedback guys. It's amazing how something so cleanly done can be so wrong.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #13  
Old 3/23/11, 8:33 PM
mwolff mwolff is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Kodak, Tennessee
Posts: 47
Default Re: 3-Wire Feeder to Distribution Panel

Square D QO..... top of the line equipment. Electrician.....not so much..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire Nuts in the Main Panel Owen Brennan AskNACHI.org Inspection Questions Forum 15 2/3/10 3:38 AM
Distribution panel? nbhi Electrical Inspections 9 4/12/09 7:49 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts