Default 3-wire feeds to existing detached buildings

A code change for sub-panels in separate buildings where the feeder does not contain a grounding conductor.

2009 IRC E3607.3.2 Grounded conductor, existing premises.
This section shall apply only to existing premises wiring systems.
Where an equipment grounding conductor is not run with the
supply conductors to the building or structure, there are no continuous
metallic paths bonded to the grounding system in both
buildings or structures involved, and ground-fault protection of
equipment has not been installed on the supply side of the
feeder(s), the grounded conductor run with the supply to the
buildings or structure shall be connected to the building or
structure disconnecting means and to the grounding electrode(
s) and shall be used for grounding or bonding of equipment,
structures, or frames required to be grounded or bonded.
Where used for grounding in accordance with this provision,
the grounded conductor shall be not smaller than the larger of:

1. That required by Section E3704.3.
2. That required by Section E3908.12.

IRC Commentary
Where the feeder that supplies the separate building is
run without an equipment grounding conductor, the
rules of this sub-section apply. Note that this section
applies only to existing wiring systems. If, for example,
new wiring was to be installed to supply a building that
did not have power run to it, the code intends to require
the installation to comply with Section E3607.3.1. In
previous editions of the code, this section applied to
new and existing installations and this was considered
to be an unnecessarily risky practice. Recall that the
code recently underwent similar revisions regarding
the grounding of electric clothes dryers and ranges,
where the long-standing practice of grounding the appliance
frames to the grounded (neutral) conductor
was banned, except for existing installations.

The preferred method is covered in Section
E3607.3.1 and for new installations, there is no excuse
for not complying with the preferred safer method, thus
this section (E3607.3.2) was revised to apply only to
existing installations. Let’s assume that the panelboard
at the workshop discussed in the previous section
is served by an existing underground feeder cable
consisting of three conductors: two ungrounded and
one neutral conductor of the appropriate sizes. The
neutral or grounded conductor of the feeder is
grounded again at the separate building by a grounding
electrode conductor connected to the separate
building grounding electrode(s)
.

The panelboard cabinet of the separate building may have
one terminal bus for the grounded conductors and another for the
grounding conductors; if so, they must be bonded together
or bonded to the cabinet by a main bonding
jumper
. Or there may be only one terminal bus to connect
all grounded and grounding conductors. In this
case, the bonding screw supplied for the purpose of
bonding the neutral terminal strip to the metal cabinet
is installed
, and this bonding screw (with a green
head) is considered a main bonding jumper. The
grounding electrode is also bonded to the equipment-
grounding terminal, which is bonded to the metal
cabinet.

An important rule that applies where only a
three-conductor feeder is run to the separate building
and the feeder grounded conductor is bonded to the
grounding electrode system at the separate building is
that there must be no common continuous metallic
paths bonded to the grounding electrode system in
both buildings
. Bonding at both ends of such objects
as a metal water pipe or gas pipe that was run from the
house to the separate building could result in a parallel
path for neutral current as well as for fault current. If
the neutral were broken or became disconnected, the
return current could be through the metal pipe, which
would cause a dangerous potential on noncurrent carrying
metal surfaces (see Commentary Figure
E3607.3.2).



Related post: http://www.nachi.org/forum/f19/groun...28/#post719537



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/9/10 at 3:19 PM..
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/9/10, 2:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3-wire feeds to existing buildings

Unfortunately, it can be impossible for an inspector to determine if there is a connection between buildings. For this reason, it is prudent for a home inspector to "defer for further evaluation" any three-wire feed to a detached building, where the neutral has been grounded.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 12/9/10, 9:05 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-wire feeds to existing detached buildings

One other note, this was code compliant for the 2005 NEC and earlier versions. The 2008 NEC has removed the use of a 3 wire feeder in this instance.
Reply With Quote
  #4  
Old 12/9/10, 10:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by Robert Meier View Post
One other note, this was code compliant for the 2005 NEC and earlier versions. The 2008 NEC has removed the use of a 3 wire feeder in this instance.
Huh?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 12/9/10, 10:43 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-wire feeds to existing detached buildings

Quote:
One other note, this was code compliant for the 2005 NEC and earlier versions. The 2008 NEC has removed the use of a 3 wire feeder in this instance.
Quote:
Originally Posted by jfunderburk View Post
Huh?
RM was saying that prior to the 08 NEC that a 3 wire feeder was allowed as long as no other metallic paths between buildings existed. the panel was treated the same as service equipment with the neutrals and grounds bonded together. The 08 now requires a 4 wire feeder regardless.
Reply With Quote
  #6  
Old 12/9/10, 10:50 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by Jim Port View Post
The 08 now requires a 4 wire feeder regardless.
No it doesn't. Did you read the code quote and commentary above? Existing buildings with 3-wire feeds are acceptable provided they are properly grounded at the building and that the cabinet is properly bonded and provided there is no other continuous, bonded, metallic path between both buildings.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 12/10/10, 4:57 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by jfunderburk View Post
No it doesn't. Did you read the code quote and commentary above? Existing buildings with 3-wire feeds are acceptable provided they are properly grounded at the building and that the cabinet is properly bonded and provided there is no other continuous, bonded, metallic path between both buildings.
What if the existing building was built under the 2008 NEC? The exception to 250.32 would not apply unless the feeder was installed under an earlier code version. The 2008 rule is that you must install an EGC with the feeder unless the feeder is existing under a code version prior to the 2008 NEC.

Quote:
250.32(B) Grounded Systems. For a grounded system at the separate building or structure, an equipment grounding conductor as described in 250.118 shall be run with the supply conductors and be connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).
Exception: For existing premises wiring systems only, the grounded conductor run with the supply to the building or structure shall be permitted to be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded where all the requirements of (1), (2), and (3) are met:
(1) An equipment grounding conductor is not run with the supply to the building or structure.
(2) There are no continuous metallic paths bonded to the grounding system in each building or structure involved.
(3) Ground-fault protection of equipment has not been installed on the supply side of the feeder(s)
Reply With Quote
  #8  
Old 12/10/10, 5:15 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3-wire feeds to existing detached buildings

I read this part. Bold and underline by me.

Quote:
Let’s assume that the panelboard
at the workshop discussed in the previous section
is served by an existing underground feeder cable
consisting of three conductors: two ungrounded and
one neutral conductor of the appropriate sizes.
The change doesn't make you change the feeder already in existance. A new feeder would need to comply with the 4 wire requirement/
Reply With Quote
  #9  
Old 12/10/10, 8:21 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by Jim Port View Post
I read this part. Bold and underline by me.



The change doesn't make you change the feeder already in existance. A new feeder would need to comply with the 4 wire requirement/
Correct.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 1/21/11, 12:31 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing buildings

Quote:
Originally Posted by jpope View Post
Unfortunately, it can be impossible for an inspector to determine if there is a connection between buildings. For this reason, it is prudent for a home inspector to "defer for further evaluation" any three-wire feed to a detached building, where the neutral has been grounded.
Jeff, do you have any recommend language you'd like to share?

Mine below: please comment.

"While the main house was equipped with a Grounding Electrode System (GES), no GES (usually a ground rod) was apparent at the detached XXX. Today's commonly accepted electrical standards require a GES at all detached buildings. We recommend service by a licensed and competent electrician to install a GES at the detached structure. Note that if the feeder wire is only a 3-wire conductor the electrician should: 1) ensure that the grounding and grounded conductor buses are bonded together or bonded to the cabinet by a main bonding jumper; and, 2) also ensure that there are no common continuous metallic paths bonded to the GES at both the house and the detached XXX."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 1/21/11, 11:27 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3-wire feeds to existing detached buildings

As far as I know, the GES has always been required for detached buildings. However, there are several different conditions that may exist, so it depends on what I find. Here are some examples;

Quote:
Electrical panels at detached buildings require a separate grounding electrode, such as a ground rod or water line. We recommend installation of a grounding electrode system for reasons of safety.
Quote:
The panel is not equipped with a grounded conductor (neutral) supplied from the service panel, which is required in modern installations. You should have the system evaluated by a qualified electrician to verify that no other conductive connection exists between structures, or to have an isolated neutral installed to the panel.
Quote:
The panel is not equipped with an equipment grounding conductor supplied from the service panel, which is required and should be installed by a qualified electrician.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 1/21/11, 2:11 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing detached buildings

Thanks Jeff. Simple and to the point.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 1/22/11, 10:13 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by jpope View Post
The panel is not equipped with a grounded conductor (neutral) supplied from the service panel, which is required in modern installations. You should have the system evaluated by a qualified electrician to verify that no other conductive connection exists between structures, or to have an isolated neutral installed to the panel.

Jeff, how would a sub-panel even function without a neutral feeder? (Is that what you're saying?) I've seen plenty of 3-wire feeds w/o grounds, but never a missing neutral.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/22/11, 10:20 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 3-wire feeds to existing detached buildings

The EGC can (will) carry the load that would normally be carried on the neutral.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 1/24/11, 7:04 PM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,551
Default Re: 3-wire feeds to existing detached buildings

Quote:
Originally Posted by jpope View Post
The EGC can (will) carry the load that would normally be carried on the neutral.
It is all about bonding...

More importantly is bonding the neutral at the panel in the outbuilding so that there is no possibility of any potential between the incoming neutral and other local grounds within the building.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Grounding electrodes at outbuildings jfunderburk Electrical Inspections 18 12/13/10 7:18 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 5:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts