A code change for sub-panels in separate buildings where the feeder does not contain a grounding conductor.
2009 IRC E3607.3.2 Grounded conductor, existing premises. This section shall apply only to existing premises wiring systems. Where an equipment grounding conductor is not run with the supply conductors to the building or structure, there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved, and ground-fault protection of equipment has not been installed on the supply side of the feeder(s), the grounded conductor run with the supply to the buildings or structure shall be connected to the building or structure disconnecting means and to the grounding electrode( s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. Where used for grounding in accordance with this provision, the grounded conductor shall be not smaller than the larger of: 1. That required by Section E3704.3. 2. That required by Section E3908.12. IRC Commentary Where the feeder that supplies the separate building is run without an equipment grounding conductor, the rules of this sub-section apply. Note that this section applies only to existing wiring systems. If, for example, new wiring was to be installed to supply a building that did not have power run to it, the code intends to require the installation to comply with Section E3607.3.1. In previous editions of the code, this section applied to new and existing installations and this was considered to be an unnecessarily risky practice. Recall that the code recently underwent similar revisions regarding the grounding of electric clothes dryers and ranges, where the long-standing practice of grounding the appliance frames to the grounded (neutral) conductor was banned, except for existing installations. The preferred method is covered in Section E3607.3.1 and for new installations, there is no excuse for not complying with the preferred safer method, thus this section (E3607.3.2) was revised to apply only to existing installations. Let’s assume that the panelboard at the workshop discussed in the previous section is served by an existing underground feeder cable consisting of three conductors: two ungrounded and one neutral conductor of the appropriate sizes. The neutral or grounded conductor of the feeder is grounded again at the separate building by a grounding electrode conductor connected to the separate building grounding electrode(s). The panelboard cabinet of the separate building may have one terminal bus for the grounded conductors and another for the grounding conductors; if so, they must be bonded together or bonded to the cabinet by a main bonding jumper. Or there may be only one terminal bus to connect all grounded and grounding conductors. In this case, the bonding screw supplied for the purpose of bonding the neutral terminal strip to the metal cabinet is installed, and this bonding screw (with a green head) is considered a main bonding jumper. The grounding electrode is also bonded to the equipment- grounding terminal, which is bonded to the metal cabinet. An important rule that applies where only a three-conductor feeder is run to the separate building and the feeder grounded conductor is bonded to the grounding electrode system at the separate building is that there must be no common continuous metallic paths bonded to the grounding electrode system in both buildings. Bonding at both ends of such objects as a metal water pipe or gas pipe that was run from the house to the separate building could result in a parallel path for neutral current as well as for fault current. If the neutral were broken or became disconnected, the return current could be through the metal pipe, which would cause a dangerous potential on noncurrent carrying metal surfaces (see Commentary Figure E3607.3.2). Related post: http://www.nachi.org/forum/f19/groun...28/#post719537 “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com Last edited by jfunderburk; 12/9/10 at 3:19 PM.. |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Unfortunately, it can be impossible for an inspector to determine if there is a connection between buildings. For this reason, it is prudent for a home inspector to "defer for further evaluation" any three-wire feed to a detached building, where the neutral has been grounded.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
One other note, this was code compliant for the 2005 NEC and earlier versions. The 2008 NEC has removed the use of a 3 wire feeder in this instance.
|
|
#4
|
||||
|
||||
|
Huh?
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
||||
|
||||
|
No it doesn't. Did you read the code quote and commentary above? Existing buildings with 3-wire feeds are acceptable provided they are properly grounded at the building and that the cabinet is properly bonded and provided there is no other continuous, bonded, metallic path between both buildings.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
I read this part. Bold and underline by me.
Quote:
|
|
#9
|
||||
|
||||
|
Correct.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#10
|
||||
|
||||
|
Quote:
Mine below: please comment. "While the main house was equipped with a Grounding Electrode System (GES), no GES (usually a ground rod) was apparent at the detached XXX. Today's commonly accepted electrical standards require a GES at all detached buildings. We recommend service by a licensed and competent electrician to install a GES at the detached structure. Note that if the feeder wire is only a 3-wire conductor the electrician should: 1) ensure that the grounding and grounded conductor buses are bonded together or bonded to the cabinet by a main bonding jumper; and, 2) also ensure that there are no common continuous metallic paths bonded to the GES at both the house and the detached XXX." “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
As far as I know, the GES has always been required for detached buildings. However, there are several different conditions that may exist, so it depends on what I find. Here are some examples;
Quote:
Quote:
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
||||
|
||||
|
Thanks Jeff. Simple and to the point.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#13
|
||||
|
||||
|
Quote:
Jeff, how would a sub-panel even function without a neutral feeder? (Is that what you're saying?) I've seen plenty of 3-wire feeds w/o grounds, but never a missing neutral. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
The EGC can (will) carry the load that would normally be carried on the neutral.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
||||
|
||||
|
Quote:
More importantly is bonding the neutral at the panel in the outbuilding so that there is no possibility of any potential between the incoming neutral and other local grounds within the building. "A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn Certified Master Inspector (2007) Member, International Assoc of Certified Home Inspectors (InterNACHI) Member, International Code Council (ICC) - Certified Residential Combination Inspector Square-One Inspection "Assurance begins here"
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Grounding electrodes at outbuildings | jfunderburk | Electrical Inspections | 18 | 12/13/10 7:18 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |