Default 3 wire feeds to sub panels

Does anyone know when 4 wire conductors were required for the feed between the service panel and the sub panel. I inspected a home today that was built in 1974. It has one service panel with a 225 AMP breaker and 3 sub panels fed from the main with a 100 AMP, a 125 AMP and a 150 AMP breaker. All three panels are fed with only 3 conductors so the neutrals and grounds are connected to the same buss in the panels.

I know this is not permitted now but was it then?

Appreciate any help.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #2  
Old 11/6/09, 7:59 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: 3 wire feeds to sub panels

I have never seen a 4 wire single phase panel feed. When did they come out with that?
Reply With Quote
  #3  
Old 11/6/09, 8:11 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 372
Default Re: 3 wire feeds to sub panels

That is what I am not sure about. Now the neutrals and grounds are only permitted to be connected together at the service panel. Otherwise you run the risk of the panel being energized. That is why you should not see a bonding screw installed in a distribution panel.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #4  
Old 11/6/09, 10:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 3 wire feeds to sub panels

I believe it was '96 when a four-wire feed became the norm, but don't quote me on that. However, the requirement for isolating the neutral has always been there. You cannot ground the neutral past the service equipment - period (some exceptions do apply ).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 11/6/09, 11:12 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 372
Default Re: 3 wire feeds to sub panels

Thanks Jeffrey but how do you isolate the neutrals and grounds without the 4th conductor?



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #6  
Old 11/7/09, 11:04 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 3 wire feeds to sub panels

The three conductors should be H+H+N, with the conduit used as the EGC or ground. If the panel is wired with two hots (120V ea) and a ground, it's wrong. The third conductor should be insulated (not bare) and land on an isolated bus in the downstream panels (i.e sub panels).

All egc's should simply terminate in the downstream panels. If the sub panels are not bonded to the service equipment by metallic conduit (essentially the fourth conductor), then the three-wire feed is wrong.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/7/09, 11:59 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 3 wire feeds to sub panels

Questions that would be related to the original post:

1. If the subpanel is non-metallic (a few are) does that change anything?

2. If an older subpanel is in a separate building, should a separate ground be driven for that panel?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 11/7/09, 12:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 3 wire feeds to sub panels

1) The only change is in regards to the equipment-grounds from circuits supplied by the sub panel. There needs to be a means to ground them at the sub panel without using the neutral. This can be done by adding a bus bar that is bonded to the metallic (assuming) conduit supplying the sub panel.

2) Older or not, separate buildings require their own GES.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 11/7/09, 2:19 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 3 wire feeds to sub panels

1) understood, but in this part of the country if there is any conduit at all it will rarely be metallic.

2) If the sub panel in a separate building is fed by a 4 wire circuit, no additional GES would be required (other than via the ground conductor feeding the panel)?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #10  
Old 11/7/09, 3:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: 3 wire feeds to sub panels

If the conduit does not serve as a means to bond the equipment, a four-wire feed would be necessary.

Regardless of the feed (3-wire or 4-wire), a separate building requires its own grounding electrode system (GES) via ground-rod, water pipe, ufer, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 11/7/09, 5:12 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 372
Default Re: 3 wire feeds to sub panels

Thanks for the feed back. In most cases around here, the distribution panel is quite a distance from the service panel and is fed only with the wire (no conduit). You conformed what I was thinking, that it needed the 4th wire to provide a return for the ground to the service panel.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
3 wire system scroenne Electrical Inspections 2 8/8/08 1:36 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM


All times are GMT -4. The time now is 4:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts