Lately I have run into many 30 amp pool equipment circuits run with 12awg wire. These have been in newer homes and have passed city inspection etc. My Code Check book says 30amp breakers get 10awg wire. Am I missing something here?
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
Based on Table 310.16, 12AWG CU is allowed for 30 amps if it's Type TBS, SA, SIS, FEP, FEPB, MI, RHH, RHW-2, THHN, THHW, THW-2, THWN-2, USE-2, XHH, XHHW, XHHW-2, or ZW-2 Check the sheathing and it's probably THHN or THHW IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
Yes. Breaker to wire size is not always black and white. Such as #10 on a 30 amp breaker.
Breaker sizes for motors, welders and A/C units follow different rules than other branch circuits. So to say #12 on a 30 amp breaker is wrong, is, well, wrong. If the circuit is dedicated to the pump motor it very well may be legal for #12 to be on a 30 amp breaker. A single phase motor on a dedicated branch circuit can have an ovecurrent device rated at 300% of full load current, yet the branch circuit conductors must be rated for the full load current at 125%. Current is valued by Tables in the code book according to motor type. I must say, for residential applications I rarely use these figures. Too many times things are added to circuits,or circuits are changed and used for other loads. |
I say typically because....see above post. |
Splain "Tap Conductor," if you would be so kind.
Nevermind, I found it.
But I'm not sure I understand it. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
as Speedy says......# 10 AWG is good for 30A......and nothing MORE unless otherwise specified and allowed within the CODE.....as with motors and AC units and so on as Speedy stated.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
normally when you see a residential motor load served by a larger wire than the breaker would normally allow, you will also see overcurrent protection at the motor disconnect itself at a lower rating.
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff
The tap conductors definition is located at 240.2. For the benefit of those who do not have their NEC. "Tap Conductors: As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4." (the bold and italicize are mine) For instance: conductors from a 2-pole 100amp breaker are installed to a trough. Those conductors are sized at 2 AWG copper. In the trough there are 2 sets of other conductors (the taps). Each is spliced directly to the 2 AWG conductors without any overcurrent protection at the splice. Those 2 sets are sized at 6 AWG and 8 AWG respectfully. The 8 & 6 conductors each are installed to separate disconnects, the 8 AWG disconnect has a 50 amp overcurrent device at the disco, and the 6 AWG disco has a 60 amp overcurrent device at the disco. Even though the overcurrent device ahead of the 8 & 6 is 100 amps, the tap rule in 240.21(B) permits this, if all of the applicable requirements of .21(B) are followed. |
It seems to me that checking the wire type on the sheathing is somewhat above and beyond the scope of an inspection. I don't check ALL the wires for their type. Often older wire is hard to read the writing on the sheathing or situated in such a way that you cannot read it.
So would you call this out? Or assume that they are using a proper wire type in 12awg. Assuming seems dangerous and is not one of my preferred practices. I suppose you could write something explaining the situation. Is that overkill and unneccesary? Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
It seems safe to say, that it should be called out as improper.
This is yet another reason I do not like to use these special rules regarding motors in a residential application. |
I can't see it as a "motor" circuit. Typically these conductors feed a panelboard with additional circuits for all of the pool equipment.
No, I do not mean feeders. I do mean a motor circuit.
The OP states these are circuits for "pool equipment", so I read that as circuits, not feeders. I am not being argumentative, I am merely trying to figure how this would be written up. Possibly something like: "Possible undersized circuit conductors for pool equipment." Or something like that. |
I am assuming he was referring to feeders on a 30 amp breaker at the service equipment (I could be wrong).
In any event, if the inspector is unsure that the conductors are properly sized, the recommendation should state something like; The conductors for the - (insert pool motor, equipment, etc.) - appear to be inadequately sized based on the rating of their OCPD. This circuit should be verified by a qualified electrician and serviced accordingly. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
| Tell me again what size wire goes on a 100 amp breaker? | jfunderburk | Electrical Inspections | 3 | 8/20/07 11:39 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 5:28 PM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 10:44 AM |