#1
|
||||
|
||||
|
At todays inspection the heat pump/AC unit stated max amp of 20.
When we inspected the panel, there is a 30amp breaker with 10awg. supplying the AC. Is this installed incorrectly or is it just over kill for protection? "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
| Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Forget I asked fellas. I found a thread that Mr. Pope responded to.
There is a OCPD at the disconnect. "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since your disconnect had the proper size OCPD you're good.
In general HVAC units should have a minimum (MCA) and a maximum (MOCPD) written on their nameplate. The conductors can be sized to the MCA, the overcurrent protection device can be sized anywhere between the MCA and the maximum listed on the nameplate. The conductor size does not have to correspond to the size of the OCPD since it only provides short circuit and ground fault protection. For example, a unit with a 19 amp MCA and a 30 amp MOCPD can use #14 conductors on a 30 amp breaker and be code compliant. |
|
#4
|
|||
|
|||
|
Couldn't the current fry the motor of the AC unit, or somehow otherwise overload it, if a 20A max is stated for the unit itself?
Seems to me 10 gauge wiring with a 20A circuit breaker would be "overkill for protection," and perfectly fine. |
|
#5
|
|||
|
|||
|
This is how I word oversized breakers on AC units.
The AC condensing unit's data plate calls for a maximum fuse size of 20-amps and the unit is currently fused on an 30-amp breaker. This condition can void the manufacturer’s and may not provide the proper over-current protection for the unit. Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details. Priority Home Inspections, Inc. 321-368-9921 www.BrevardHomeInspector.com www.AvoidAMoneyPit.com www.BrevardInsuranceSavings.com www.BrevardBuildersWarranty.com www.PrioritySignPosts.com Info@BrevardHomeInspector.com |
|
#6
|
||||
|
||||
|