At todays inspection the heat pump/AC unit stated max amp of 20.
When we inspected the panel, there is a 30amp breaker with 10awg.
supplying the AC. Is this installed incorrectly or is it just over kill for protection?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/14/10, 6:33 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 30amp?

Forget I asked fellas. I found a thread that Mr. Pope responded to.
There is a OCPD at the disconnect.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #3  
Old 3/14/10, 7:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30amp?

Since your disconnect had the proper size OCPD you're good.

In general HVAC units should have a minimum (MCA) and a maximum (MOCPD) written on their nameplate. The conductors can be sized to the MCA, the overcurrent protection device can be sized anywhere between the MCA and the maximum listed on the nameplate. The conductor size does not have to correspond to the size of the OCPD since it only provides short circuit and ground fault protection.

For example, a unit with a 19 amp MCA and a 30 amp MOCPD can use #14 conductors on a 30 amp breaker and be code compliant.
Reply With Quote
  #4  
Old 3/15/10, 4:28 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: 30amp?

Couldn't the current fry the motor of the AC unit, or somehow otherwise overload it, if a 20A max is stated for the unit itself?

Seems to me 10 gauge wiring with a 20A circuit breaker would be "overkill for protection," and perfectly fine.
Reply With Quote
  #5  
Old 3/17/10, 2:36 AM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: 30amp?

This is how I word oversized breakers on AC units.

The AC condensing unit's data plate calls for a maximum fuse size of 20-amps and the unit is currently fused on an 30-amp breaker. This condition can void the manufacturer’s and may not provide the proper over-current protection for the unit.



Priority Home Inspections has teamed up with the Dish Network to give you a FREE Dish Network system. Log onto www.Free-Dish-For-You.com for all the details.



Priority Home Inspections, Inc.
321-368-9921

www.BrevardHomeInspector.com
www.AvoidAMoneyPit.com
www.BrevardInsuranceSavings.com
www.BrevardBuildersWarranty.com
www.PrioritySignPosts.com

Info@BrevardHomeInspector.com
Reply With Quote
  #6  
Old 3/17/10, 7:51 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30amp?

Quote:
Originally Posted by mhawley View Post
This is how I word oversized breakers on AC units.

The AC condensing unit's data plate calls for a maximum fuse size of 20-amps and the unit is currently fused on an 30-amp breaker. This condition can void the manufacturer’s and may not provide the proper over-current protection for the unit.
I like Mathew's idea. For accuracy I would just change a few words. Since this unit is protected by a circuit breaker I would change the word fuse to circuit breaker or Over-Current Protection Device. In the second sentence change over-current protection to ground fault and short circuit protection. In this case the circuit breaker does not provide over-current protection, that is provided by the overloads integral to the unit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 5:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts