225 amp main panel
Sub Panel 100 amp breaker is a number 4 copper ok to use for a feeder?
seems to a lot of confusion over this one i marked for being under sized and refereed it to a electrician, builder refused and sent it was Ok under
Article 310-15-B6 NEC #4 awg
Buyer want it changed on his report
Wayne Wilson
East TN Home Inspections LLC
865-256-1490
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 3/2/12, 7:18 PM
Robert Meier's Avatar
Default Re: #4 for 100 amp sub panel ?
No good. #4 THHN is only rated for 85 amps at 75° C. This would be for MC cable or conductors in a raceway. SE cable in thermal insulation or NM cable would be rated at 60° C which has an ampacity of 70 amps.
Old 3/2/12, 7:38 PM
kwood kwood is offline
Banned
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
What the InterNachi says is #3 AWG for a remote distribution panel.
19th edition of Canadian Electrical says #3 RX 90XLPE copper
Old 3/2/12, 7:50 PM
I still stayed with my statement and didn't change the report. Seems to be a lot of confusion on this topic 600.000 Plus home 5 feet of wire Who knows
Wayne Wilson
865-256-1490
Old 3/2/12, 8:09 PM
Banned
Mike Holt Knows and agrees with the #3 and #4 is only good for 70Amps, so Robert is right also.
Old 3/2/12, 8:43 PM
Thanks guys, I am glad i stuck to my guns lolol
Wayne Wilson
865-256-1490
Old 3/2/12, 9:27 PM
Depending on the connected load of the subpanel you might be able to change the OCPD to a smaller size without changing the conductors.
Old 3/2/12, 9:29 PM
Thanks Robert, I told them that but i left it up to the Electrician .
Wayne Wilson
865-256-1490
Old 3/3/12, 10:01 AM
Unmoderated Guest
There are two charts for wire sizing, one was for when the entire load of the dwelling was served and the other one that was for the other sizings. Many did not distinguish the difference.
Old 3/3/12, 10:52 AM
The breaker still has to protect the conductor.
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Certified Level II Infrared Thermographer
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Old 3/3/12, 11:20 AM
Originally Posted by wwilson3 View Post
Got a question
225 amp main panel
Seems like the builder has no idea how to read the codebook. What is the voltage system that this is being used on? That table is very specific in that it is only used for certain dwellings and 1Ø, 120/240 volt systems. Considering you mentioned a 225 amp main panel I would guess that neither of those criteria apply.
Old 3/4/12, 12:26 AM
Paul W. Abernathy, CMI's Avatar
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
Send a message via Skype™ to pabernathy
Remember....That smaller table [310.15(B)(7)] is only good if you are dealing with 120/240 volt, single phase dwelling service conductors, service- lateral conductors and main power feeders and in your example you have none of those. The client would have to use the traditional ampacity ratings in accordance with Section 310.15(B)(16) to be compliant.
Paul W. Abernathy
Manager, Electrical Codes & Standards
Encore Wire Corporation
Master The NEC Radio Show
“Promise me you'll always remember: You're braver than you believe, and stronger than you seem, and smarter than you think.” -RIP Dad, Love You!.10/10/2014
Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of Encore Wire, or other associations, organizations or affiliations.
Old 3/4/12, 9:16 AM
Good lord we are still going around on this . I referred to a electrician, Builder is saying i am wrong and wants it changed in my report. According to this Paul #4 is Under sized Am I right?
Wayne Wilson
865-256-1490
Old 3/4/12, 9:28 AM
Let's start with the wiring method, is it conductors in a raceway, SE cable, MC cable, NM cable? The differences were listed in post #2.
Old 3/4/12, 10:08 AM
Here is the panel in question
Main 225
Home built in 2007 ( never lived in)
sub 100 amp
one breaker 60 amp
rest 20 amp
Sub panel is right beside main wire is run through conduit
I am trying to up load a picture but nothing happens
I try later
Wayne Wilson
865-256-1490
Help proof the safety section on inspecting electrical panels: read here kshepard Electrical Inspections 58 6/8/14 5:52 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 2:18 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM