Default 4 leads?

This is feeding a 220 outlet for a window A/C unit. The wires are too small for the breaker, 12awg, twisted. This does not appear or is actual incorrect? Thanks

4-leads-copy-p4140172.jpg



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 4/14/09, 8:12 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: 4 leads?

It not right but it should work alright, I would not call it out because the codes in my area are a joke. Your mileage my vary.
Reply With Quote
  #3  
Old 4/14/09, 8:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 4 leads?

If you don't call this out, you shouldn't be a home inspector.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/14/09, 8:36 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 4 leads?

Quote:
Originally Posted by nbhi View Post
This is feeding a 220 outlet for a window A/C unit. The wires are too small for the breaker, 12awg, twisted. This does not appear or is actual incorrect? Thanks

Attachment 27986

It's not right. Either they paralleled 2 cables to the unit, or they are supplying two loads or receps off the one breaker. In any case, it is in violation.
Reply With Quote
  #5  
Old 4/14/09, 8:50 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 4 leads?

I am calling it out. I know about the wrong size wire for the breaker, 10awg should be used. The single strands how would you expalin?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #6  
Old 4/14/09, 9:08 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 4 leads?

Did you turn the breaker off or was it off when you arrived?

www.MauiHomeInspections.com
Reply With Quote
  #7  
Old 4/14/09, 9:48 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: 4 leads?

Breaker was off when we arrived.



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #8  
Old 4/14/09, 10:01 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 4 leads?

Quote:
Originally Posted by nbhi View Post
I am calling it out. I know about the wrong size wire for the breaker, 10awg should be used. The single strands how would you expalin?

What do you mean the single strands??? It's two wires under a screw, plain and simple.
Reply With Quote
  #9  
Old 4/14/09, 10:19 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 4 leads?

Quote:
Originally Posted by nbhi View Post
The single strands how would you expalin?
I would write it up as a double lug.

www.MauiHomeInspections.com
Reply With Quote
  #10  
Old 4/14/09, 10:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 4 leads?

Quote:
Originally Posted by nbhi View Post
This is feeding a 220 outlet for a window A/C unit. The wires are too small for the breaker, 12awg, twisted. This does not appear or is actual incorrect? Thanks

Attachment 27986
And what else is it feeding? You have 2 circuits. A 4 wire 220 AC rec. will have 2 hot, 1 neutral, 1 ground. Not 4 hot.




Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 4/14/09, 10:55 PM
GARY R. EVANS GARY R. EVANS is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Coconut Creek, FL
Posts: 55
Default Re: 4 leads?

Besides being double lugged the NEC 310.4 says that conductors smaller than 1/0 shall not be paralleled.
Reply With Quote
  #12  
Old 4/15/09, 10:46 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: 4 leads?

Quote:
Originally Posted by jpope View Post
If you don't call this out, you shouldn't be a home inspector.
The reason why I would not call it out is because the code official in my area would say that it is okay because the wires are twisted together at the terminal thus not making it two separate wires under one lug. I have been done this road before with my heating and cooling company. Come to Jefferson City and you will see things are different.
You need to get to know your local officials, not fight against them. That is why we are reading so many problems with inspectors and code officials. Some inspectors are overstepping their bounds. Inspectors need to use their head when calling something out. If it is not going to hurt the the client in anyway, why call it out?
You passing judgment on an inspectors ability, when you do not understand what is going on is getting really old, Jeff. I have seen you belittle another inspector on this board after his first post, a couple years back. You told this new inspector that he should not be an inspector because he did not spell a few words right. You need to think before you post.
Reply With Quote
  #13  
Old 4/15/09, 11:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 4 leads?

Quote:
Originally Posted by jbraun View Post
You passing judgment on an inspectors ability, when you do not understand what is going on is getting really old, Jeff.
I stand by my comment. It's not our job to coddle an "AHJ" who feels they can make up their own standards. If the AHJ disagrees with your opinion, that's his option. But to say it's ok, just because you can't "change things" is absurd.

If you don't like my posts, you have the option of ignoring them, but when you suggest that it may be ok to overlook this type of installation, I will certainly post my opinion.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #14  
Old 4/15/09, 12:07 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: 4 leads?

You need to read my first post again.
I am not for knocking heads against local authorities. The inspector will always lose. We should not call out code. That is why our SOP is written that way. It is reckless to tell inspectors to do so.
And saying somebody should not be a home inspector because he does follow the SOP or because a newbie has some misspelling in his first post is wrong.
Reply With Quote
  #15  
Old 4/15/09, 3:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 4 leads?

I'm sorry if you were offended when I was critical of a post made by another inspector.

Quote:
Originally Posted by jbraun View Post
I am not for knocking heads against local authorities.
Nor am I, but that has nothing to do with making the right call.

Regardless of codes, improper conditions/installations should always be pointed out to the client. Do you not agree? Otherwise, what is the point of having a home inspection?

"Improper conditions" usually have the support of a building code or manufacturers requirements.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Anyone got leads on good weather seal for doors wwilson3 General Inspection Discussion 12 1/29/09 12:49 AM
Scheduling Pro and Leads Nick Gromicko recommends this software. Ed Maxwell General Inspection Discussion 8 1/8/09 11:12 AM
Canadian tax expert sought for upcoming Pillar to Post Conference. Leads? gromicko Canadian Inspectors 7 11/29/07 1:36 PM


All times are GMT -4. The time now is 5:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts