There were 2 4 wire (red, black, white & ground) cables (12AWG) with both reds and blacks connected to breakers (4 110v circuits). So single neutral and ground for 2 branch circuits, twice. I feel I should know if this is OK but....I ain't sure.
Shared neutrals/grounds? Don't remember the rules! Help appreciated. BTW, branches were ceiling fixtures. |
| Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
What you've described is a MWBC or multiwire branch circuit which is fine as long as the two circuits sharing a neutral are not on the same phase.
|
|
#3
|
||||
|
||||
|
Thanks Robert,
My memory came back after I posted this! |
|
#4
|
|||
|
|||
|
You mean same bus, right. Single phase system.
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, not connected to the same phase within a panel but this usage (a MWBC) is not limited to a single phase system. There is some debate as to whether or not in a 120/240 volt system we can call them phases since they're both physically on the same single coil of a transformer. We generally use the word phase even if by some definitions it's not entirely correct.
|
|
#6
|
||||
|
||||
|
A common example is the dishwasher and disposal on a multi-wire circuit. Always make sure a handle-tie exists on the breaker.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Short circuit failures with 12/3 NM-B cable and NM clamp connectors | pabernathy | Electrical Inspections | 10 | 4/17/11 1:43 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Did you KNOW this about NM Cable? | pabernathy | Electrical Inspections | 0 | 12/19/06 8:46 AM |