I did an inspection for a coop apartment which is approximately 50 years old. There is a sub panel in the apartment with a 40 amp main breaker, the panel appears to be recently upgraded but not the service feed (they just added a new panel and used the old panel as junction box). The apartment is a 3 bedroom, approximately 1100 sf. There are no electric appliances or heating systems. Heat is supplied by a main boiler for the building. Would this 40 amp service be considered adequate in this situation?
|
| Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only real way to know is by doing a load calculation. Since the existing sub-panel was 40 amps and has been that way for 50 years a load calc is probably not needed.
|
|
#3
|
|||
|
|||
|
Yes, a calculation of the loads connected and served would be required, but that that is well beyond the SOP for home inspections. You could, however, mention that such a calcuation might be appropriate.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Service size | acox | Electrical Inspections | 6 | 9/5/09 2:40 PM |
| Infrared Inspection Service | jwarner | Thermal Imaging, Infrared Cameras & Energy Audits | 25 | 7/28/09 7:32 AM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |