Default 400 amp main

Had a 400 amp outside fpe main shut off feeding 5 other main breakers that then fed 5 sub panels.

All wires were tied and taped togeather in a gutter before the wiring fed each individual main shut off.

Help!!!

The house also had two very old stablock panels. I have never seen ones this old before, house built in the 50s. NO heat and very clean panels for their age.
Attached Thumbnails
400-amp-main-5311024.jpg   400-amp-main-5311-034.jpg   400-amp-main-5311-e-030.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/16/11, 9:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 amp main

So do you have some specific questions? How many condcutors were under one of those big taped up monstrosities?
Reply With Quote
  #3  
Old 6/16/11, 9:48 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 400 amp main

Quote:
Originally Posted by Robert Meier View Post
So do you have some specific questions? How many condcutors were under one of those big taped up monstrosities?
Several. I would say 5 or 6 for each leg.

That was my main concern. Is this kosher? The other was mainly all the single mains feeding the subs. Overall the panels themselves were clean but due to age of the wires and panels many lacked modern safety and wiring practices.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 6/16/11, 9:49 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 400 amp main

other was the fpe panels. These were older than what I am used to seeing. Did they have the same problematic issues as the colorful red ones?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #5  
Old 6/16/11, 10:24 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 amp main

Well if those are sub-panels then the neutrals and EGC's need to be on separate buses. Typically if those are split bolt connectors they're only listed for two conductors, not 5 or 6. I'm not sure about those CB's as to whether or not they're a known problem. The GEC should be at the 400 amp switch or somewhere up stream of that. The bonding jumper should be in the 400 amp switch.
Reply With Quote
  #6  
Old 6/16/11, 10:31 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 400 amp main

Quote:
Originally Posted by Robert Meier View Post
Well if those are sub-panels then the neutrals and EGC's need to be on separate buses. Typically if those are split bolt connectors they're only listed for two conductors, not 5 or 6. I'm not sure about those CB's as to whether or not they're a known problem. The GEC should be at the 400 amp switch or somewhere up stream of that. The bonding jumper should be in the 400 amp switch.
No bonding jumper. They just ran the wires into the gutter and connected about 5 to them each. Then to their respected boxes.

I know so many things either wrong or aged you dont know where to begin. I pulled the grounding wire from the 400 main out of the gorund. It was stuck in about 3 inches.

What should I say, start over??




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #7  
Old 6/17/11, 12:11 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 400 amp main

Based on what I see, I'd say everything in your first picture is service equipment. The 400A breaker is the service disconnect. The other breakers are OCPD's for the load-side equipment, but are still part of the service equipment.

5 or 6 conductors under a split-bolt is excessive. I don't know of any connector that would properly accommodate that many ungrounded conductors for a "splice."

The breakers are Stab-loks. No different than the red ones, just older.

In your last picture (the sub panel), as Robert stated, the EGC's need to be removed from the neutral terminal and bonded to the panel, while the neutrals remain isolated.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 6/17/11, 8:01 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 400 amp main

Thanks Jeff.
Long night and longer inspection. My mind was fried and had to pick up this morning.

Yes, due to the age of the home there was a ton of grounding and bonding issues, but they just didnt do wiring the same then.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #9  
Old 6/17/11, 10:28 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 400 amp main

Quote:
Originally Posted by sfogarty View Post
they just didnt do wiring the same then.
True, but the principles of electricity were the same.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Disconnect missing verbage & cut main wire rwashington Electrical Inspections 19 1/16/11 2:07 PM
Shut off valves required? jcahill Plumbing Inspections 11 9/2/08 1:07 AM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts