Default 400 Amp Service and GFCI Limitations

This weekend I did and inspection on a 5,500SF home. It appears that the service is 400amp's. There are 2 200amp service disconnects, and the label on the panel indicated that the panel is rated for 400 amp the the service is determined by the totaling up the 2 service disconnects.

On another note one of the breakers was a 20 amp breaker that was connected to and exterior GFCI outlet that had 15 outlets connect down stream. Is there a limit to how many outlets can be downstream and protected by a GFCI outlet.
Attached Images
File Type: jpg 100_4970.jpg (47.4 KB, 38 views)
File Type: jpg 100_4985.jpg (25.0 KB, 46 views)
File Type: jpg 100_4987.jpg (55.8 KB, 54 views)
File Type: jpg 100_4988.jpg (77.7 KB, 45 views)
File Type: jpg 100_4992.jpg (112.2 KB, 37 views)




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #2  
Old 10/20/08, 7:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

That's a 320 amp service, which is sometimes called a 400 amp service for slang (don't ask me why, because I don't know). Really and truly, it's max rating is 320 amps. An electrician would refer to that service as a "three-twenty".

No, there is no limit as to how many downstream receptacles may be protected by a GFCI breaker or receptacle. In real life, one would try to keep this to a reasonable amount to assist in later troubleshooting when it trips. I, personally, favor point-of-use GFCI receptacles at each location where GFCI protection is required. This eliminates lots of headaches later on, but at additional initial cost. This exterior circuit you saw, with 15 downstream receptacles on the GFCI, while legal, is just nuts. It's the outdoor equipment and outdoor receptacles that cause the biggest headaches trying to sort out what tripped the GFCI. As an electrician, I'd highly advise you to note that in your report as a very probable nuisance in later years, and consideration should be given to point-of-use GFCI protection at each exterior receptacle. Many manufacturers have a functional limit of 250 feet of wire on the load side of the GFCI also.
Reply With Quote
  #3  
Old 10/20/08, 7:44 PM
David B. Alvares David B. Alvares is offline
InterNACHI Member
 
Join Date: May 2008
Location: Hilmar, CA
Posts: 12
David B. Alvares hasn't had much positive or negative feedback
Default Re: 400 Amp Service and GFCI Limitations

Thanks for the input on the CL320 because I was ready to call it out as a 400amp service.

A future note on the GFCI outlet; it was located on the exterior of the house but it also controlled the 9 garage outlets and 6 or more outlets on the front and back side of the house. I made many trips around that 5,500 sf house. I have no problem recommending future evaluation by an electrician because there were may other electrical issues with this house.




David Alvares
Modesto, CA 95354
866-757-8480
Reply With Quote
  #4  
Old 10/20/08, 7:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by dalvares View Post
A future note on the GFCI outlet; it was located on the exterior of the house but it also controlled the 9 garage outlets and 6 or more outlets on the front and back side of the house. I made many trips around that 5,500 sf house. I have no problem recommending future evaluation by an electrician because there were may other electrical issues with this house.
Word it however it pleases you most, but I'm not sure it needs evaluated by an electrician now. They just at least need to be on notice that it's going to be a royal pain in the donkey for them one day.
Reply With Quote
  #5  
Old 10/21/08, 12:12 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 400 Amp Service and GFCI Limitations

Generally we see 320/400 meter enclosures as 320A Continuous and 400A Non-Continuous.

But do refer to them as 320A services as well, but I would venture to say 3 of 4 electricians would call it a 400A service.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #6  
Old 10/21/08, 1:04 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 412
brian winkle has had a little positive feedback
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by pabernathy View Post
Generally we see 320/400 meter enclosures as 320A Continuous and 400A Non-Continuous.

But do refer to them as 320A services as well, but I would venture to say 3 of 4 electricians would call it a 400A service.
I like to call them 400 amp services too, looks better on the invoice!
Reply With Quote
  #7  
Old 10/21/08, 1:09 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 42
Joseph M. Whitt is generally well trusted
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by pabernathy View Post
Generally we see 320/400 meter enclosures as 320A Continuous and 400A Non-Continuous.

But do refer to them as 320A services as well, but I would venture to say 3 of 4 electricians would call it a 400A service.
I think that 320A Continuous and 400A max if on the label of the panel posted.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #8  
Old 10/21/08, 1:19 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 226
Jeffrey R. Wicklander is often very helpful Jeffrey R. Wicklander is often very helpful
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by jwhitt View Post
I think that 320A Continuous and 400A max if on the label of the panel posted.
or just call it 320 Amp since that's the rating of the meter.

Jeff
Reply With Quote
  #9  
Old 10/21/08, 9:12 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by jwicklander View Post
or just call it 320 Amp since that's the rating of the meter.

Jeff
Right, because there certainly are "real" 400 amp services.
Reply With Quote
  #10  
Old 10/22/08, 2:25 AM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: nord-est [ northeast] wisconsin
Posts: 125
Marc Benz is generally well trusted
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

For myself when I writeup the service size typically I will marked down R400 or C400 The R is 320 resdential service while the C is a true 400 amp commercal and normally it will be either CT'ed or bolted on depending on which POCO I deal with it.

Merci,Marc
Reply With Quote
  #11  
Old 10/23/08, 9:36 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 200
Pierre Belarge is generally well trusted
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by pabernathy View Post
Generally we see 320/400 meter enclosures as 320A Continuous and 400A Non-Continuous.

But do refer to them as 320A services as well, but I would venture to say 3 of 4 electricians would call it a 400A service.


The listing on this equipment is just as Paul has mentioned, that is the reason some call them 400A services.


Just a small hijacking...
We see a ton of 400A services being installed around my area. We have tested a bunch of these services to see loads of less than 150A. Talk about keeping upe with the Jones.
Reply With Quote
  #12  
Old 10/25/08, 11:57 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: 400 Amp Service and GFCI Limitations

Quote:
Originally Posted by Pierre Belarge View Post
We see a ton of 400A services being installed around my area. We have tested a bunch of these services to see loads of less than 150A. Talk about keeping upe with the Jones.
Very True - I have a 4000+ sq. ft. house that the AHJ insisted had to have a 400 A service in spite of the fact that only the A/C is electric. The rest of the usually large loads are natural gas (water heaters, cooktop, furnaces, clothes dryer, etc.). They base the requirement strictly on square footage, reasoning that someone in the future may want to convert to all electric. I haven't measured the total load under various conditions, but would bet that it would be hard to find 150 A at any time.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Tags
400amp , gfci

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical 13 2/8/07 2:18 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
GFCI breaker in service panel cobarr Electrical 11 4/17/06 10:59 PM


All times are GMT -4. The time now is 8:06 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics