Default 4300 SF plus detached building setup

This looks like a way to draw more than 200 amps without tripping a breaker.
Any problems with code?

200 amp meter feeding a 200 amp panel that has 5 breakers as follows:
a. 100 amp feeding house indoor panel that has another 50 amp panel off it.
b. 100 amp feeding exterior hvac's, panel has a 50A and a 35A in it.
c. 50 amp feeding an oven.
d. 30 amp feding a smaller oven.
e. 60 amp feeding the detached building.

No 200A disconnect present in the main service equip. panel.
House has gas heat with 8.5 tons of Air cond.
The service was underground and size of cable not visible.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 2/12/06, 5:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

ok....without seeing the setup and so on I will kinda explain a few things....

1.) Total breaker calculations do not factor in the size of the service, Not sure of the best wording for that but I will give an example.

A typical 200A panel that has 42 spaces...could mathmatically have nearly 600 A of breaker markings.....HOW CAN THIS BE...lol...

Well basically it boils down to usage factors and so on and the concept that not everything is on at the same time and so on....

Now the idea of (5) breakers meets the 230.71 allowance of 2-6 disconnects per service without having a main breaker per se.....

Well...long story short....the actual demand on this would need to be calculated out fully to know what the total demand is......we simply can't guess that from seeing a 100A panel inside...might only have 30A draw on it...just dont know.....have to factor in these loads...

Again really outside the scope of what any HI should venture into...otherwise their heads will explode...lol..But if you would like to try to do the math I will gladly post the procedure for you...

Now we can do the calculation math and come up with that the service should be....which actually is WAY outside the HI's scope....`



Paul W. Abernathy
Reply With Quote
  #3  
Old 2/12/06, 5:55 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

BUT I will comment on one thing....lol........regardless of doing the CALC....any house I have wired over 3,500 sq feet has always gotten a 400A service..if it needed it or not.......

I tell you....the COST difference in a rough in for a 400A over a 200A is just well.......double that of a 200A...thehehee.....

In other words...when doing the cost for a 200A... lets say $ 235.00 for 200A panels and breakers you would already buy anyway...just spaced out more...it really is not a issue in terms of additional cost...more SE.....and so on....considering my last electrical price for a 4,000 Sq Ft home the other day was $ 17,890.00 for the electrical...I think I can throw in another 200A panel...thehehehe



Paul W. Abernathy
Reply With Quote
  #4  
Old 2/12/06, 6:01 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 4300 SF plus detached building setup

Quote:
Originally Posted by pabernathy
Now we can do the calculation math and come up with that the service should be....which actually is WAY outside the HI's scope....`
I would agree that this outside our scope, however, based on what Brian said, there seems to be a great potential for an over-load.

Based on his information, I might air on the side of caution and recommend that an electrician be hired to perform a load calc or have a service disconnect installed.

Obviously, the lateral is sized by the POCO at their discretion, but the SEC was likely sized for a 200 amp service.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/12/06, 6:22 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

Certainly within the thought of having it looked at...most certainly the prevailing option....however on the service disconnect issue....not nearly as clean cut

BUT it NEVER hurts to refer.............better to be SAFE than SORRY !

Hell...Send me the specs....all of them and I will do the calc for ya....free...no cashola....no moola...no denero....man I cant spell all the ways to put it FREE.....lolololo

I figured I better cut this one short to keep it simple...lol



Paul W. Abernathy

Last edited by pabernathy; 2/12/06 at 6:27 PM..
Reply With Quote
  #6  
Old 2/12/06, 9:12 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 4300 SF plus detached building setup

I don't have all the specs for a load calc.

I always thought that 3500SF and over should have a 400 amp service but with gas water heaters and gas heat it is not as critical.

One thing that will draw some juice on these big houses is when the heat pumps get covered during an ice storm and the aux heat on 2 or 3 airhandlers cuts in for about 85 to 130 amps total. Add to that a couple of electric water heaters, double ovens and two laundry rooms and you see why 400 amps is needed.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 2/12/06, 11:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 4300 SF plus detached building setup

The Florida IAEI tossed this around. It is possible, using the article 220 rules, to end up with big houses that have very low load calcs.Remember, using the normal calc, all of the general lighting and receptacle load over 3.5kva gets taken at 35% so basically all of that 4500 sq/ft amounts to a tad less than 20a of calculated load. At that point you are really looking at "fixed in place" equipment and adding that up.Worse is the "optional" way you can do the calc. With that one you end up taking everything at nameplate and anything over 10kva at 40%. If you have a lot of electric "toys" that are on at the same time you can have a problem.The scenario is a party. Every light in the house is on, the kitchen is going full blast, lots of hot water being used, doors are open so HVAC is blasting and people are in the pool, the spa and maybe the sauna. The service is sized at 40% of THAT.
Reply With Quote
  #8  
Old 2/14/06, 11:02 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 4300 SF plus detached building setup

Quote:
Originally Posted by bking
No 200A disconnect present in the main service equip. panel.
While a load calc is beyond a home inspection, the Service Entrance feeders from the drip loop or pull box to the service/distribution panel need overcurrent protection that match the wires, which should be verified during the inspection.

This wire protection is most commonly a main breaker/fuses at the service panel, but can be a breaker/fuses at the meter enclosure (combo meter/disconnect) or within a separate enclosure between the meter and panel.

If the SE feeders are sized for 200A (2/0 Cu or 4/0 Al), then that is a defect which should be written up as they could be overloaded (panel breakers total 340A). But since it's a large house, I guess it's possible the SE feeders are larger.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 2/14/06, 11:11 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

Robert,

That totally depends on the Service Setup- In many cases you will have (2) 200A panels with both being fed with 4/0 AL SE which is totally allowed and is rated as a 400A service.....yet (2) individual 200A panels....The meter cab itself is usually rated 380-400A and is in most cases provided by the UTY and no cost......could be different in other areas...but in ours they provide it free.

The service can truly be a (2) 200A services with a total AMP rating of 400A....which is what the UTY will figure on when supplying the power to this system.

As as side note....The cost factors in most cases of doing something less than 400A but more than 200A is negatible...and in many cases as a contractor the cost of the 150A panel can be more than the cost of a 200A...depending on the supplier and supply house.

In most cases the houses will be either 200A or 400A....atleast all the electricians I deal with...and myself.....and we use a golden rule to save time......if the house is under 3,500 we have to calc. it out...if over 3,500 it is automatically a 400A service.......and their are obvious exceptions to every rule....but it helps save time.... on the ones under 3,500 we then go into more detail just to make sure...and then let that decide if it is 200A or 400A....but as stated on a 3,400 sq ft and up house....automatically 400A....NOW if it is a 10,000 sq ft and up...thats a whole new ball game....



Paul W. Abernathy

Last edited by pabernathy; 2/14/06 at 11:15 AM..
Reply With Quote
  #10  
Old 2/14/06, 12:03 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 4300 SF plus detached building setup

While there are work arounds, a service calc is beyond a home inspection. So IMO a home inspector simply should look for a main breaker or main fuses that match the SE feeders, or it gets written up for further evaluation by a licensed professional. Keeps it real simple ...

JMO & 2-nickels



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 2/14/06, 1:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

ahhh....I think I was the one saying it is beyond the scope...lol.....I was just explaining how we look at determining service sizes...lol......

Nothing more my friend......not really a work around....factual electrical wiring to current standards.



Paul W. Abernathy
Reply With Quote
  #12  
Old 2/14/06, 2:13 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 4300 SF plus detached building setup

Hey Paul ... We seem to look at this issue a little differently, as I tend to think of the exception under IRC E3503.3.1 or NEC 230.90.A that allows 2-6 breakers/fuses totaling more than the capacity of the SE feeders if a load calc is done as somewhat of a work-around.

Perhaps I have just seen too many things done wrong ... ... and think avoiding the minimal cost of having an additional single overcurrent protection device that matches the service feeders wires just isn't worth the risk of additional future load being added without correctly repeating the load calc to ensure the feeders are not overloaded. Murphy's Law strikes again ...

JMO and 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 2/14/06, 2:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

Robert,

I believe you are refering to Exception # 3 of the Art 230.90 (A)....however it is common practice to envoke 310.15(B)(6) which allows for 4/0 AL to a 200A panel......the ability to tap the service entrance meter cab into two individual protected panels of combined 400A via this method using (2) individual 4/0 AL cables.

Panels for general residential wiring come in normal 100,125,150 and 200 Amp rated formats.....However meter cabs usualy are in a broader range of usage.

It is totally acceptacle for the Electrician to provide the service in this method.

230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception Nos. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be no more than six sets of disconnects per service grouped in any one location. For the purpose of this section, disconnecting means used solely for power monitoring equipment, or the control circuit of the ground-fault protection system or power-operable service disconnecting means, installed as part of the listed equipment, shall not be considered a service disconnecting means.

The key is 230.2 supports this.......

BUT with that said...maybe I am getting too technical here versus the question....because I seem to have forgotten the question...thehehehe

I think in the end all you can do as the HI is look at the sizes of the conductors, look at the service size at the loop and also look for signs of overheating and so on.

As for calculations.......we have just developed the concept of CALC on services under 3,500 sq ft and when they are over 3,500 sq ft....400A automatically unless the house is excessive.....BUT it is very rare to need more than 400A in service.......to an electrician if more is needed even before calculations take place...it will be obvious to the trained eye...or should I say....BATTLE TESTED eye...lol

No problem mate ( I got the mate part from GERRY...thehehe ) just figured they would like to know how electricians think when sizing and so on.



Paul W. Abernathy
Reply With Quote
  #14  
Old 2/14/06, 7:12 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: 4300 SF plus detached building setup

The question isn't really the sizing of the feeders, which wasn't posted (and should be verified), or the number of switches to shut off the service. Bruce indicated there was a 200A meter and panel, with five breakers that add up to 340A and no 200A disconnect (breaker/fuses). I'm assuming that it's also 200A rated SE feeders (2/0 Cu or 4/0 Al per my previous post), which is why he is concerned.

Per IRC E3503.3.1-Exception or NEC 230.90.A-Exception#3 you can have up to 6 breakers/fuses that add up to more that the capacity of the service feeders if a load calc is done that shows the feeders are not overloaded. That is what I look at as the work-around to just providing a main breaker/fuses rated for the same capacity as the SE feeders, and concerns me also.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #15  
Old 2/14/06, 7:44 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 4300 SF plus detached building setup

Ahhh.......I think I get where you are going...I WAS being overly technical...lol....

Quote:
Well...long story short....the actual demand on this would need to be calculated out fully to know what the total demand is......we simply can't guess that from seeing
lol....I think this is why I offered to do the CALC for him if he wanted me too....as I stated in the original post.....always err on the side of caution...while the setup is allowed...the CALC could prove otherwise....

I just happen to be an electrician so I was offering to do the CALC is all...lol.....Thanks Robert for sorting that out....lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
Article on Commercial and Residential Inspections and Assessment mcyr Commercial Inspections 2 8/6/07 1:26 AM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 2:28 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM