This is a first for me.
It looked like a "standard" parallel service entrance, however, only one of the neutrals actually continued through the mast, to the meter base. So it was in fact, a 5 wire service, as indicated on the meter. But is it actually 2 phase? If so, what does that mean? I've also included pictures of the dual Federal Pacific service panels. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#2
|
||||
|
||||
|
|
|
#3
|
||||
|
||||
|
Thanks for the link Mike. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Quote:
Do you have any good pictures of the transformer connections? The transformers will tell you what type of service it is. Licensed Electrical Contractor Master Electrician BS Electrical Engineering Certified Master Inspector BestInspectors.Net License Prep and Continuing Education Home and Commercial Building Inspection - Electrical Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm Fire and Explosion Investigation - Commercial Sign Installation - Real Estate (Agent and Broker) - Appraisal Inspection Report Software for Windows - iOS - Mac - Android - Linux est. 1992
|
|
#5
|
||||
|
||||
|
I couldn't see the transformer from the property. What would I expect to see from a transformer supplying this type of service?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Please Note:
phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Ever notice how hot dogs cooked using 2 phase just seem to taste better than hot dogs cooked using single phase or even 3 phase?
|
|
#7
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
||||
|
||||
|
Quote:
Every coil has two legs extending from it. It may also have one or more taps. Single-phase has one coil, two-phase has two coils, three-phase has three coils, etc. The transformers and the connections tell you what the service type is. A proper two-phase five-wire service will have all five conductors landed on a single disconnect. There can be multiple disconnects but all five conductors have to enter the building together into the same enclosure. From what I can see in your photo of the transformer connections, it appears to be a two-phase connection. However, your photos from the panels do not show a single entry point. I developed a very effective classroom exercise that illustrates isolation transformer connections. Once you see this classroom demonstration, it all becomes very clear almost instantly. It is difficult for most people to visualize real transformer connections from schematic diagrams. I don’t have any photos of two-phase five-wire transformer connections but I do have a schematic. Licensed Electrical Contractor Master Electrician BS Electrical Engineering Certified Master Inspector BestInspectors.Net License Prep and Continuing Education Home and Commercial Building Inspection - Electrical Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm Fire and Explosion Investigation - Commercial Sign Installation - Real Estate (Agent and Broker) - Appraisal Inspection Report Software for Windows - iOS - Mac - Android - Linux est. 1992
Last edited by gwells; 8/20/07 at 2:48 PM.. |
|
#9
|
||||
|
||||
|
Thanks for the explanation, although I'm not sure I understand the need for a single disconnect.
How does the disconnect affect the configuration? The panels were side-by-side, each wired with 240 volts and bonded together after the meter pan. The single neutral was attached to the panel on the right, which was a split-bus with six throws. The left-side panel had no single disconnect. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 4 | 3/25/07 11:41 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 2:08 AM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 10:44 AM |