On inspection, a 50 amp breaker was noted to have 8 awg copper wire. This was to an outdoor jacuzzi. We know that 40 amps is the max for 8 awg AND we know there are always exceptions to these rules. 60 amp breakers are required to have 6 awg so this seems to be on the fence with the judgement call going to the electrician. What are some of your comments?
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
For THHN/THWN conductors in conduit #8cu is typical on a 50A breaker. I guess this is the "exception" you were referring to, although it is not an exception. It is more the rule as far as conduit work goes. THHN uses the 75 deg C column in figuring ampacity in newer work. #8 is rated right at 50 amps in that column. I say "newer" work because most all modern fittings and breakers ARE rated for 75 deg C. |
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
One thing to check is the Mfg requirements. MANY tub manufacturers DO require a minimum of #6cu to wire tubs.
|
|
#4
|
||||
|
||||
|
Scott,
8 AWG may carry a maximum of 70 Amps in free air, or 50 Amps as part of a 3 conductor cable. |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
David, if that cable is NM (Romex) then it actually cannot carry 50 amps. NM cable is limited to the 60 deg C column in T310.16 which is 40 amps.
|
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
No problem. I was not commenting on your judgement.
I was just correcting the "...or 50 Amps as part of a 3 conductor cable" statement. |
|
#8
|
||||
|
||||
|
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
LOL! Oh man! Is that my new image?
Cool. Everyone will be afraid of me. |
|
#10
|
||||
|
||||
|
Quote:
You should see me on a Harley...I just feel out of place with the black clothes and thick wornout leather jacket and the thick chains hanging from my shoulders, and the huge group emblem on the back. Then placing the earring in my left ear and not shaving for weeks so I can look rugged. And then I place the black helmet over my long un-sanitized hair of mine and then I put on a facade by not smiling, so I can look REAL mean. Do you think I'll get stared at? NOOOOOOOOO....
Last edited by dvalley; 1/19/08 at 6:32 PM.. |
|
#11
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
||||
|
||||
|
My brother just bought a Harley. I sent him an old joke to help him get over the hump of transitioning from a rice burner to a Harley..
Difference between a Harley and a vacuum cleaner....? The Position of the dirt bag. |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Where is Kingston, NY? |
|
#14
|
||||
|
||||
|
Kingston NY is about 1.75-2 hrs North of the city or about 1 hr South of Albany. Exit 19 on the NYS thruway.
Carmine Fuoco Peace Of Mind Home Inspections PO Box 664 New Paltz, NY 12561 (845) 399-1661 www.pom-hi.com NACHI ID #04102691 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Breaker Question | mhawley | Electrical | 5 | 1/14/08 4:25 PM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical | 4 | 9/7/07 3:05 PM |
| Double Tapped Breaker | tjohnson3 | Electrical | 8 | 4/20/07 10:04 AM |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical | 0 | 7/7/06 1:24 PM |