Default 50 amp breaker #8 awg cu

On inspection, a 50 amp breaker was noted to have 8 awg copper wire. This was to an outdoor jacuzzi. We know that 40 amps is the max for 8 awg AND we know there are always exceptions to these rules. 60 amp breakers are required to have 6 awg so this seems to be on the fence with the judgement call going to the electrician. What are some of your comments?
Reply With Quote
  #2  
Old 1/19/08, 5:17 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Scott Schultz
We know that 40 amps is the max for 8 awg
Not true at all.
For THHN/THWN conductors in conduit #8cu is typical on a 50A breaker.
I guess this is the "exception" you were referring to, although it is not an exception. It is more the rule as far as conduit work goes.

THHN uses the 75 deg C column in figuring ampacity in newer work. #8 is rated right at 50 amps in that column.
I say "newer" work because most all modern fittings and breakers ARE rated for 75 deg C.
Reply With Quote
  #3  
Old 1/19/08, 5:21 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

One thing to check is the Mfg requirements. MANY tub manufacturers DO require a minimum of #6cu to wire tubs.
Reply With Quote
  #4  
Old 1/19/08, 5:21 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: 50 amp breaker #8 awg cu

Scott,

8 AWG may carry a maximum of 70 Amps in free air, or 50 Amps as part of a 3 conductor cable.
Reply With Quote
  #5  
Old 1/19/08, 5:23 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

David, if that cable is NM (Romex) then it actually cannot carry 50 amps. NM cable is limited to the 60 deg C column in T310.16 which is 40 amps.
Reply With Quote
  #6  
Old 1/19/08, 5:29 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
David, if that cable is NM (Romex) then it actually cannot carry 50 amps. NM cable is limited to the 60 deg C column in T310.16 which is 40 amps.
I don't get into the logistics of wiring (I'm not an Electrician). I simply report dangerous conditions if they exist in this sort of situation.
Reply With Quote
  #7  
Old 1/19/08, 5:34 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

No problem. I was not commenting on your judgement.
I was just correcting the "...or 50 Amps as part of a 3 conductor cable" statement.
Reply With Quote
  #8  
Old 1/19/08, 5:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
No problem. I was not commenting on your judgement.
I was just correcting the "...or 50 Amps as part of a 3 conductor cable" statement.
Ok..Harley guy.
Reply With Quote
  #9  
Old 1/19/08, 5:49 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

LOL! Oh man! Is that my new image?

Cool. Everyone will be afraid of me.
Reply With Quote
  #10  
Old 1/19/08, 6:06 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
LOL! Oh man! Is that my new image?

Cool. Everyone will be afraid of me.
Why would people be afraid of a Harley dude?

You should see me on a Harley...I just feel out of place with the black clothes and thick wornout leather jacket and the thick chains hanging from my shoulders, and the huge group emblem on the back. Then placing the earring in my left ear and not shaving for weeks so I can look rugged. And then I place the black helmet over my long un-sanitized hair of mine and then I put on a facade by not smiling, so I can look REAL mean.

Do you think I'll get stared at? NOOOOOOOOO....

Last edited by dvalley; 1/19/08 at 6:32 PM..
Reply With Quote
  #11  
Old 1/19/08, 6:18 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by dvalley
Why would people be afraid of a Harley dude?

You should see me on a Harley...I just feel out of place with the black clothes and thick wornout leather jacket and the thick chains hanging from my shoulders, and the huge group emblem on the back. Then placing the earring in my right ear and not shaving for weeks so I can look rugged. And then I place the black helmet over my long un-sanitized hair of mine and then I put on a facade by not smiling, so I can look REAL mean.

Do you think I'll get stared at? NOOOOOOOOO....
Dave if you would just put on your Nachi hat, decal and tattoo, you would look more respectable.
Reply With Quote
  #12  
Old 1/19/08, 6:35 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: 50 amp breaker #8 awg cu

My brother just bought a Harley. I sent him an old joke to help him get over the hump of transitioning from a rice burner to a Harley..

Difference between a Harley and a vacuum cleaner....?




The Position of the dirt bag.
Reply With Quote
  #13  
Old 1/20/08, 7:21 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by dedwards
My brother just bought a Harley. I sent him an old joke to help him get over the hump of transitioning from a rice burner to a Harley..

Difference between a Harley and a vacuum cleaner....?




The Position of the dirt bag.
I own six antique Harley's, and an Indian! I once owned a Harley back in 1976 and it was terrible, after that I owned a few Honda's, Gold Wings, and collected many and restored many old bikes, Harley 37 Trike, BSA, and Matchless, I used to find them in the back yard around Glendale and Pasadena and for little money had a garage full of them, won lots of Trophies, I never did Motor Racing though.

Where is Kingston, NY?
Reply With Quote
  #14  
Old 1/20/08, 9:01 AM
Carmine Fuoco's Avatar
Carmine Fuoco Carmine Fuoco is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: New Paltz, NY
Posts: 350
Default Re: 50 amp breaker #8 awg cu

Kingston NY is about 1.75-2 hrs North of the city or about 1 hr South of Albany. Exit 19 on the NYS thruway.



Carmine Fuoco
Peace Of Mind Home Inspections
PO Box 664
New Paltz, NY 12561
(845) 399-1661
www.pom-hi.com
NACHI ID #04102691
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker Question mhawley Electrical 5 1/14/08 4:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 3:40 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147