  #1  
Old 1/19/08, 4:08 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default 50 amp breaker #8 awg cu

On inspection, a 50 amp breaker was noted to have 8 awg copper wire. This was to an outdoor jacuzzi. We know that 40 amps is the max for 8 awg AND we know there are always exceptions to these rules. 60 amp breakers are required to have 6 awg so this seems to be on the fence with the judgement call going to the electrician. What are some of your comments?
Reply With Quote
  #2  
Old 1/19/08, 4:17 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Scott Schultz
We know that 40 amps is the max for 8 awg
Not true at all.
For THHN/THWN conductors in conduit #8cu is typical on a 50A breaker.
I guess this is the "exception" you were referring to, although it is not an exception. It is more the rule as far as conduit work goes.

THHN uses the 75 deg C column in figuring ampacity in newer work. #8 is rated right at 50 amps in that column.
I say "newer" work because most all modern fittings and breakers ARE rated for 75 deg C.
Reply With Quote
  #3  
Old 1/19/08, 4:21 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

One thing to check is the Mfg requirements. MANY tub manufacturers DO require a minimum of #6cu to wire tubs.
Reply With Quote
  #4  
Old 1/19/08, 4:21 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 50 amp breaker #8 awg cu

Scott,

8 AWG may carry a maximum of 70 Amps in free air, or 50 Amps as part of a 3 conductor cable.
Reply With Quote
  #5  
Old 1/19/08, 4:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

David, if that cable is NM (Romex) then it actually cannot carry 50 amps. NM cable is limited to the 60 deg C column in T310.16 which is 40 amps.
Reply With Quote
  #6  
Old 1/19/08, 4:29 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
David, if that cable is NM (Romex) then it actually cannot carry 50 amps. NM cable is limited to the 60 deg C column in T310.16 which is 40 amps.
I don't get into the logistics of wiring (I'm not an Electrician). I simply report dangerous conditions if they exist in this sort of situation.
Reply With Quote
  #7  
Old 1/19/08, 4:34 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

No problem. I was not commenting on your judgement.
I was just correcting the "...or 50 Amps as part of a 3 conductor cable" statement.
Reply With Quote
  #8  
Old 1/19/08, 4:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
No problem. I was not commenting on your judgement.
I was just correcting the "...or 50 Amps as part of a 3 conductor cable" statement.
Ok..Harley guy.
Reply With Quote
  #9  
Old 1/19/08, 4:49 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

LOL! Oh man! Is that my new image?

Cool. Everyone will be afraid of me.
Reply With Quote
  #10  
Old 1/19/08, 5:06 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by Speedy Petey
LOL! Oh man! Is that my new image?

Cool. Everyone will be afraid of me.
Why would people be afraid of a Harley dude?

You should see me on a Harley...I just feel out of place with the black clothes and thick wornout leather jacket and the thick chains hanging from my shoulders, and the huge group emblem on the back. Then placing the earring in my left ear and not shaving for weeks so I can look rugged. And then I place the black helmet over my long un-sanitized hair of mine and then I put on a facade by not smiling, so I can look REAL mean.

Do you think I'll get stared at? NOOOOOOOOO....

Last edited by dvalley; 1/19/08 at 5:32 PM..
Reply With Quote
  #11  
Old 1/19/08, 5:18 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by dvalley
Why would people be afraid of a Harley dude?

You should see me on a Harley...I just feel out of place with the black clothes and thick wornout leather jacket and the thick chains hanging from my shoulders, and the huge group emblem on the back. Then placing the earring in my right ear and not shaving for weeks so I can look rugged. And then I place the black helmet over my long un-sanitized hair of mine and then I put on a facade by not smiling, so I can look REAL mean.

Do you think I'll get stared at? NOOOOOOOOO....
Dave if you would just put on your Nachi hat, decal and tattoo, you would look more respectable.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 1/19/08, 5:35 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: 50 amp breaker #8 awg cu

My brother just bought a Harley. I sent him an old joke to help him get over the hump of transitioning from a rice burner to a Harley..

Difference between a Harley and a vacuum cleaner....?




The Position of the dirt bag.
Reply With Quote
  #13  
Old 1/20/08, 6:21 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Quote:
Originally Posted by dedwards
My brother just bought a Harley. I sent him an old joke to help him get over the hump of transitioning from a rice burner to a Harley..

Difference between a Harley and a vacuum cleaner....?




The Position of the dirt bag.
I own six antique Harley's, and an Indian! I once owned a Harley back in 1976 and it was terrible, after that I owned a few Honda's, Gold Wings, and collected many and restored many old bikes, Harley 37 Trike, BSA, and Matchless, I used to find them in the back yard around Glendale and Pasadena and for little money had a garage full of them, won lots of Trophies, I never did Motor Racing though.

Where is Kingston, NY?
Reply With Quote
  #14  
Old 1/20/08, 8:01 AM
cfuoco's Avatar
cfuoco cfuoco is offline
Active Poster
 
Join Date: Oct 2004
Location: New Paltz, NY
Posts: 350
Please Note: cfuoco is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp breaker #8 awg cu

Kingston NY is about 1.75-2 hrs North of the city or about 1 hr South of Albany. Exit 19 on the NYS thruway.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 3:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 4:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts