Amps........Copper........Alum
====================== 40.............8 ga..........6 ga 60.............6 ga..........4 ga What size for 50 amps? Does it remain at 8 and 6? Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
| Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
I would always go to the next size up. But that is what i do
|
|
#3
|
||||
|
||||
|
Most 6 gauge copper is only good for 55 amps due to the temperature rating but its allowed for 60 around here since you can rarely see the specs on the sheathing.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#4
|
||||
|
||||
|
Rule of thumb 125% should be used
|
|
#5
|
||||
|
||||
|
So, 12 AWG is not good. Cause that's what I found.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
LOLOL you have to be kidding
|
|
#7
|
|||
|
|||
|
I think it's okay. I'm sure they're just trying to pre-melt it for recycling.
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#8
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe, there are many factors involved, for instance #8 CU THHN is good for 50 amps but 8/3 Romex is not, you would need 6/3 if Romex. Also, there are applications where #12 would be acceptable on a 50 amp circuit, for example a tap on a cooking appliance circuit (210.19(A)exception No 1), or a motor circuit where overload protection is provided at the motor.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| What's this video worth? | jtedesco1 | Education | 5 | 4/18/08 10:24 AM |
| Square D HOM Breaker & Max Wire Size | pbennett1 | Electrical | 20 | 3/3/08 10:22 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical | 0 | 7/2/07 1:35 PM |
| Service wire size to breaker panel | sfalvey | Electrical | 12 | 10/31/06 5:28 PM |