Amps........Copper........Alum
====================== 40.............8 ga..........6 ga 60.............6 ga..........4 ga What size for 50 amps? Does it remain at 8 and 6? “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
| Find an InterNACHI certified Indiana Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
I would always go to the next size up. But that is what i do
|
|
#3
|
||||
|
||||
|
Most 6 gauge copper is only good for 55 amps due to the temperature rating but its allowed for 60 around here since you can rarely see the specs on the sheathing.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#4
|
||||
|
||||
|
Rule of thumb 125% should be used
|
|
#5
|
||||
|
||||
|
So, 12 AWG is not good. Cause that's what I found.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
LOLOL you have to be kidding
|
|
#7
|
|||
|
|||
|
I think it's okay. I'm sure they're just trying to pre-melt it for recycling.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#8
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe, there are many factors involved, for instance #8 CU THHN is good for 50 amps but 8/3 Romex is not, you would need 6/3 if Romex. Also, there are applications where #12 would be acceptable on a 50 amp circuit, for example a tap on a cooking appliance circuit (210.19(A)exception No 1), or a motor circuit where overload protection is provided at the motor.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 10:24 AM |
| Square D HOM Breaker & Max Wire Size | pbennett1 | Electrical Inspections | 20 | 3/3/08 10:22 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 1:35 PM |
| Service wire size to breaker panel | sfalvey | Electrical Inspections | 12 | 10/31/06 5:28 PM |