#1
|
|||
|
|||
|
It seems that using #8 wire for 50 Amp breakers is a common practice when so many electrical charts say #6 wire should be used. Any rule of thumb pointers out there for the inspection or report? Thanks.
|
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
you can use #8-3 MC cable with a 50 amp breaker, but not #8 romex, nonmetallic
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
It also depends on the application. #8 on a 50 amp feeding an HVAC unit or a motor would likely be code compliant.
Although their conductors are rated for 90° C, for NM cable, SE cable, or AC cable embedded in insulation, you must use the 60° C column of NEC Table 310.16 to find their ampacity. The requirements for interior SE cable installations in Article 338 send you over to Article 334 (NM cable) to determine their ampacity. Quote:
Quote:
Quote:
|
|
#4
|
|||
|
|||
|
So, in regards to a home inspection report, what should be stated (if anything) when there is a 50 amp breaker with #8 wire for a range? AC?
|
|
#5
|
||||
|
||||
|
Do NOT quote the NEC. It is NOT a code violation unless and until the AHJ has determined it to be so.
I would write it up something like this: Quote:
|
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I'm not an HI so I will defer to Joe's advice. However, for an AC unit the conductor size does not have to match the circuit breaker size. You would need to know the Minimum Circuit Ampacity (MCA) of the unit and the Maximum CB or Fuse size. This information is listed on the nameplate of the unit. The conductors are sized according to the MCA and they can be protected by any size OCPD from the MCA up to the maximum. Take a look at the example nameplate below. [MCA 23.3 amps, Max fuse or CB 30 amps]. It would be permissible to have #12 conductors protected by a 30 amp CB or fuse.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main panel...recommendation ? | dnasser | Electrical Inspections | 6 | 11/22/09 9:55 PM |
| FYI - Counterfeit Circuit Breakers Recalled By Specialty Lamp International Due to Fi | rmaday | Electrical Inspections | 0 | 5/28/08 10:03 AM |
| Counterfeit Breakers | jallingham | Electrical Inspections | 0 | 5/27/08 4:25 PM |