It seems that using #8 wire for 50 Amp breakers is a common practice when so many electrical charts say #6 wire should be used. Any rule of thumb pointers out there for the inspection or report? Thanks.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/1/10, 10:29 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 50 Amp breakers

you can use #8-3 MC cable with a 50 amp breaker, but not #8 romex, nonmetallic



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 4/2/10, 5:03 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 Amp breakers

It also depends on the application. #8 on a 50 amp feeding an HVAC unit or a motor would likely be code compliant.

Although their conductors are rated for 90° C, for NM cable, SE cable, or AC cable embedded in insulation, you must use the 60° C column of NEC Table 310.16 to find their ampacity. The requirements for interior SE cable installations in Article 338 send you over to Article 334 (NM cable) to determine their ampacity.

Quote:
334.80 Ampacity.
The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor.
Quote:
320.80 Ampacity.
The ampacity shall be determined by 310.15.
(A) Thermal Insulation. Armored cable installed in thermal insulation shall have conductors rated at 90°C (194°F). The ampacity of cable installed in these applications shall be that of 60°C (140°F) conductors. The 90°C (194°F) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor.
Quote:
II. Installation
338.10 Uses Permitted.
(A) Service-Entrance Conductors. Service-entrance cable shall be permitted to be used as service-entrance conductors and shall be installed in accordance with 230.6, 230.7, and Parts II, III, and IV of Article 230.
(B) Branch Circuits or Feeders.
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334.
FPN: See 310.10 for temperature limitation of conductors.
Reply With Quote
  #4  
Old 4/2/10, 9:52 AM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 97
Default Re: 50 Amp breakers

So, in regards to a home inspection report, what should be stated (if anything) when there is a 50 amp breaker with #8 wire for a range? AC?
Attached Thumbnails
50-amp-breakers-img_8796-small-.jpg.JPG
Views:	395
Size:	56.9 KB
ID:	36176  
Reply With Quote
  #5  
Old 4/2/10, 11:12 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: 50 Amp breakers

Do NOT quote the NEC. It is NOT a code violation unless and until the AHJ has determined it to be so.

I would write it up something like this:

Quote:
Inspector observed #8 electrical conductor connected to a 50-ampere circuit breaker. It is possible that the current wiring configuration is not properly suited for the application, and further investigation/evaluation by a licensed electrical contractor is recommended, to ensure that the installation is proper and conforms to all applicable electrical codes and requirements.
Reply With Quote
  #6  
Old 4/2/10, 3:43 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 Amp breakers

Quote:
Originally Posted by abolt View Post
So, in regards to a home inspection report, what should be stated (if anything) when there is a 50 amp breaker with #8 wire for a range? AC?

I'm not an HI so I will defer to Joe's advice. However, for an AC unit the conductor size does not have to match the circuit breaker size. You would need to know the Minimum Circuit Ampacity (MCA) of the unit and the Maximum CB or Fuse size. This information is listed on the nameplate of the unit. The conductors are sized according to the MCA and they can be protected by any size OCPD from the MCA up to the maximum. Take a look at the example nameplate below. [MCA 23.3 amps, Max fuse or CB 30 amps]. It would be permissible to have #12 conductors protected by a 30 amp CB or fuse.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
FYI - Counterfeit Circuit Breakers Recalled By Specialty Lamp International Due to Fi rmaday Electrical Inspections 0 5/28/08 10:03 AM
Counterfeit Breakers jallingham Electrical Inspections 0 5/27/08 4:25 PM