InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 4/9/07, 11:55 PM
Kenneth (Kip) R. McCullough, Jr. Kenneth (Kip) R. McCullough, Jr. is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Smyrna, GA
Posts: 29
Default 50 amp disconnect for 1600sf condo

Today while inspecting an 1600sf condo I noticed that the main disconnect was only a 50 amp disconnect. The condo was originally built in 1910 and the electrical system was updated with a new electrical panel in 2001. The panel and meter were both 200 amps. The condo had several plasma TVs, 2 refrigerators, washer & dryer, computer, and plenty of lighting/ canlights. It seems to me that a 50 amp main disconnect is not large enough for a 1600 sf condo. Any commits would be greatly appreciated.

Thanks.
Reply With Quote
  #2  
Old 4/10/07, 12:19 AM
William E. Siegel William E. Siegel is online now
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,789
Default Re: 50 amp disconnect for 1600sf condo

I would agree with you. You may have a very unhappy client when his TV goes poof.

Did they upgrage the wiring too, or just the panel and meter.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #3  
Old 4/10/07, 12:23 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp disconnect for 1600sf condo

What you are saying doesn't add up. If the panel and meter were both 200 amps, where was this 50 amp disconnect? Are you sure it wasn't for an AC unit? Or maybe the panel is a split bus with a 50 amp lighting main? Or could it be a sub panel disconnect? Could you give us more details or pics?

thanks..................Brian
Reply With Quote
  #4  
Old 4/10/07, 12:42 AM
Kenneth (Kip) R. McCullough, Jr. Kenneth (Kip) R. McCullough, Jr. is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Smyrna, GA
Posts: 29
Default Re: 50 amp disconnect for 1600sf condo

The 50 amp disconnect was located just above the meter in the basement of a 6 story condo building. There is the possibility that there was another main disconnect. The boiler room was locked and not all of the basement could be accessed. I am going to write up this one as "the size of the electrical system could not be determined at the time of the inspection due to inaccessible mechanical room."
Reply With Quote
  #5  
Old 4/10/07, 1:50 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp disconnect for 1600sf condo

On minimum service sizes:
  • For a one family dwelling, the minimum service size is 100 amp
  • For a dwelling (other than one family) that does not have more than 2 branch circuits, the minimum service size is 30 amp
  • For a dwelling (other than one family) that has more than 2 branch circuits, the minimum service size is 60 amp.
Definition of a one-family dwelling: A building that consists solely of one dwelling unit.
Reply With Quote
  #6  
Old 4/10/07, 9:49 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp disconnect for 1600sf condo

A quick load calc comes up with 60a or so based on what you posted.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Well pump disconnect sfalvey Plumbing 0 11/17/06 1:23 AM
A/C Disconnect question rslocum HVAC 15 9/21/06 1:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical 8 8/15/06 1:32 PM
HVAC Disconnect kgore HVAC 11 7/11/06 7:58 PM


All times are GMT -4. The time now is 11:20 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts