On a 1yr warranty inspection,
The builder added a 240V 50 amp outlet in the garage for the owners ceramic kiln. The kiln is rated at 30A 240V but has a factory looking 50A cord on it. The circuit added is 30A 240V using 10ga copper to a 50amp receptacle. Any exceptions in the code to allow this? B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
What size was the overcurrent protective device? You can supply a "big" receptacle at less than its rated capacity. The rating of the receptacle is the potential "heavy duty-ness" of the receptacle.
When evaluating large, high-current receptacles, check for:
Problems to look out for:
A "large" receptacle on a "small" circuit is no problem at all. The breaker will trip if someone, for instance, tries to weld at a full 50 amps with a large welder. |
|
#3
|
||||
|
||||
|
As posted, the circuit is 30 amps. (30 amp breaker)
It seems the same issue as putting a 20 amp receptacle on a 15 amp circuit which is not allowed, right? Then why is a 50 on a 30 amp circuit ok? B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 Last edited by bking; 3/6/08 at 5:56 PM.. |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Someone could eventually install a larger breaker for any circuit. There's nothing peculiar about this circuit that would cause this to happen any quicker than any other circuit. |
|
#5
|
||||
|
||||
|
Marc, please recheck my last post, I was editing while you were posting...
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
That does not agree with previous posts about 20 amp recepts on 15 amp circuits.
http://www.nachi.org/forum/showthrea...ghlight=outlet B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#8
|
||||
|
||||
|
Is it because the 50 amp receptacle is dedicated or single?
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#9
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
||||
|
||||
|
see post 6 on that thread
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
That chart in post 6 of that thread is for circuits with 2 or more receptacles. That chart is taken out of context with respect to this thread. A single receptacle on an individual branch circuit has to have a rating at least as much as the circuit, and that is the only requirement. You could put a 100 amp receptacle on a 15 amp branch circuit if you wanted to, in the case of a dedicated circuit. If you have more than one receptacle on the circuit, then and only then, that table you linked to applies. |
|
#12
|
||||
|
||||
|
Thanks Marc!
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Here's a link that may be of some help. |
|
#14
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am curious as to what the instructions have to do with anything.
All I would see is a receptacle and would not care what is plugged in. Is it wired properly? Is the circuit sized properly? Is the overcurrent sized properly? You are inspecting the house and the wiring. NOT the kiln. IMO even considering what is being plugged in to a receptacle is far beyond the scope of a home inspection. |
|
#15
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
See 110.3(B), I want to know what the instructions say about the kiln! I am not inspecting anything, I want to see in black and white what the product instructions say!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Microwave receptacle | jwardenski | Electrical Inspections | 17 | 9/9/07 7:18 PM |
| What's This Receptacle For? | cmettel | Electrical Inspections | 7 | 5/25/07 7:35 AM |
| Bedroom receptacle | dnasser | Electrical Inspections | 9 | 4/16/07 10:33 AM |
| Online Code Check- Reference | pabernathy | Electrical Inspections | 31 | 11/9/06 3:39 PM |
| Wiring a Receptacle | jallingham | Electrical Inspections | 9 | 8/6/06 4:34 PM |