Default 50 amp receptacle

On a 1yr warranty inspection,

The builder added a 240V 50 amp outlet in the garage for the owners ceramic kiln.

The kiln is rated at 30A 240V but has a factory looking 50A cord on it.

The circuit added is 30A 240V using 10ga copper to a 50amp receptacle.

Any exceptions in the code to allow this?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 3/6/08, 4:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

What size was the overcurrent protective device? You can supply a "big" receptacle at less than its rated capacity. The rating of the receptacle is the potential "heavy duty-ness" of the receptacle.

When evaluating large, high-current receptacles, check for:
  • The receptacle has a rating at least as large as the overcurrent protective device (fuse or breaker)
  • The branch circuit conductors serving the receptacle have a rating the seems to meet or exceed the sizing required for the fuse or breaker that serves the receptacle.

Problems to look out for:
  • Branch circuit conductors smaller than required for the overcurrent protective device
  • Breakers or fuses larger than the rating of the receptacle

A "large" receptacle on a "small" circuit is no problem at all. The breaker will trip if someone, for instance, tries to weld at a full 50 amps with a large welder.
Reply With Quote
  #3  
Old 3/6/08, 5:52 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

As posted, the circuit is 30 amps. (30 amp breaker)


It seems the same issue as putting a 20 amp receptacle on a 15 amp circuit which is not allowed, right?

Then why is a 50 on a 30 amp circuit ok?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937

Last edited by bking; 3/6/08 at 5:56 PM..
Reply With Quote
  #4  
Old 3/6/08, 5:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

Quote:
Originally Posted by bking
So, its ok until they do that....
Right.

Someone could eventually install a larger breaker for any circuit. There's nothing peculiar about this circuit that would cause this to happen any quicker than any other circuit.
Reply With Quote
  #5  
Old 3/6/08, 5:58 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

Marc, please recheck my last post, I was editing while you were posting...



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 3/6/08, 5:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

Quote:
Originally Posted by bking
It seems the same issue as putting a 20 amp receptacle on a 15 amp circuit which is not allowed, right?
Right... you can always put a "big" receptacle on a "small" circuit if you feel the need. The only time you're allowed to put a "small" receptacle on a "big" circuit is the special exception that permits 15 amp receptacles on 20 amp circuits.
Reply With Quote
  #7  
Old 3/6/08, 5:59 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

That does not agree with previous posts about 20 amp recepts on 15 amp circuits.

http://www.nachi.org/forum/showthrea...ghlight=outlet



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 3/6/08, 6:03 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

Is it because the 50 amp receptacle is dedicated or single?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 3/6/08, 6:04 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

Quote:
Originally Posted by bking
That does not agree with previous posts about 20 amp recepts on 15 amp circuits.

http://www.nachi.org/forum/showthrea...ghlight=outlet
The man asked why a 20 amp receptacle can't be used on a 15 amp circuit, but nobody (other than the OP) ever suggested that it couldn't .
Reply With Quote
  #10  
Old 3/6/08, 6:05 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

see post 6 on that thread



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #11  
Old 3/6/08, 6:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

Quote:
Originally Posted by bking
see post 6 on that thread
If you want to talk about code, we can do that...

That chart in post 6 of that thread is for circuits with 2 or more receptacles. That chart is taken out of context with respect to this thread.

A single receptacle on an individual branch circuit has to have a rating at least as much as the circuit, and that is the only requirement. You could put a 100 amp receptacle on a 15 amp branch circuit if you wanted to, in the case of a dedicated circuit.

If you have more than one receptacle on the circuit, then and only then, that table you linked to applies.
Reply With Quote
  #12  
Old 3/6/08, 6:19 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: 50 amp receptacle

Thanks Marc!



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 3/7/08, 9:08 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

Quote:
Originally Posted by bking
On a 1yr warranty inspection,

The builder added a 240V 50 amp outlet in the garage for the owners ceramic kiln.

The kiln is rated at 30A 240V but has a factory looking 50A cord on it.

The circuit added is 30A 240V using 10ga copper to a 50amp receptacle.

Any exceptions in the code to allow this?
I would look at the instructions before evaluating this situation.

Here's a link that may be of some help.
Reply With Quote
  #14  
Old 3/7/08, 2:56 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

I am curious as to what the instructions have to do with anything.
All I would see is a receptacle and would not care what is plugged in.
Is it wired properly?
Is the circuit sized properly?
Is the overcurrent sized properly?

You are inspecting the house and the wiring. NOT the kiln.
IMO even considering what is being plugged in to a receptacle is far beyond the scope of a home inspection.
Reply With Quote
  #15  
Old 3/7/08, 3:18 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 50 amp receptacle

See 110.3(B), I want to know what the instructions say about the kiln! I am not inspecting anything, I want to see in black and white what the product instructions say!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Microwave receptacle jwardenski Electrical Inspections 17 9/9/07 7:18 PM
What's This Receptacle For? cmettel Electrical Inspections 7 5/25/07 7:35 AM
Bedroom receptacle dnasser Electrical Inspections 9 4/16/07 10:33 AM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 3:39 PM
Wiring a Receptacle jallingham Electrical Inspections 9 8/6/06 4:34 PM