Default 6 breaker exceeded

If sub-panels have more than 6 breakers should it have a service disconnect or does that only apply to the main panel?

Thanks ahead of time




Mike Hazelwood
Bakersfield, California
cal-proinspections@sbcglobal.net
www.calproinspections.com
Reply With Quote
  #2  
Old 3/11/08, 1:39 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Mike check out the thread under yours.
I just had that answered.
Reply With Quote
  #3  
Old 3/11/08, 8:20 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Detached structure it does. Within the same structure NO main is required.
Reply With Quote
  #4  
Old 3/11/08, 11:04 PM
Mike D. Hazelwood's Avatar
Mike D. Hazelwood Mike D. Hazelwood is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Bakersfield, Ca
Posts: 358
Default Re: 6 breaker exceeded

Quote:
Originally Posted by Speedy Petey
Detached structure it does. Within the same structure NO main is required.
sub-panel is in a detached garage???




Mike Hazelwood
Bakersfield, California
cal-proinspections@sbcglobal.net
www.calproinspections.com
Reply With Quote
  #5  
Old 3/11/08, 11:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by mhazelwood
sub-panel is in a detached garage???
I'm confused. You made a statement, but put question marks on the end. Is that panel in question in a detached garage or not?
Reply With Quote
  #6  
Old 3/12/08, 12:04 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Yeah, I'm confused too.
Maybe I was not clear.
Reply With Quote
  #7  
Old 3/12/08, 1:38 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

I often wondered if anyone tried to invoke 225.32 exception 1 in the residence of a qualified person
Quote:
Exception No. 1: For installations under single management, where documented safe switching procedures are established and maintained for disconnection, and where the installation is monitored by qualified individuals, the disconnecting means shall be permitted to be located elsewhere on the premises.
Reply With Quote
  #8  
Old 3/12/08, 1:46 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by Greg Fretwell
I often wondered if anyone tried to invoke 225.32 exception 1 in the residence of a qualified person
Yeah, nice try.

That exception is mainly for industrial establishments with a central powerhouse.
Reply With Quote
  #9  
Old 3/12/08, 2:13 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,738
Default Re: 6 breaker exceeded

Quote:
Originally Posted by mhazelwood
If sub-panels have more than 6 breakers should it have a service disconnect or does that only apply to the main panel?

Thanks ahead of time
It applies to the main panel.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #10  
Old 3/12/08, 8:20 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by bkelly2
It applies to the main panel.
....AND to a panel in a detached structure.

Even though you guys don't do codes this seems to be a hard sell. So here:

II. More Than One Building or Other Structure
225.31 Disconnecting Means
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
Reply With Quote
  #11  
Old 3/12/08, 11:59 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
That exception is mainly for industrial establishments with a central powerhouse.

Marc, it doesn't say that. I know I would have a hard time approving the installation but if the owner had placards on the subpanel and demonstrated he was "qualified" (licensed) I am not sure how I would justify the rejection if he fought it.

The fact that any installation was compliant at the time of inspection does not guarantee that those procedures will remain in place or that it will continue to be supervised by qualified people. As far as I am concerned the exception guts the intent of the rule.
Reply With Quote
  #12  
Old 3/12/08, 1:19 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: 6 breaker exceeded

Speedy, Not disagreeing, trying to understand. This code is not clear to me.

Quote:
II. More Than One Building or Other Structure
225.31 Disconnecting Means
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

If the main panel is feeding the subpanel and there is a main disconnect (or 6 throw) in the main panel that doesn't cover the subpanel? Doesn't that count as means of disconnecting?

Last edited by kgerhauser; 3/12/08 at 1:33 PM..
Reply With Quote
  #13  
Old 3/12/08, 2:02 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: 6 breaker exceeded

Quote:
Originally Posted by kgerhauser
Speedy, Not disagreeing, trying to understand. This code is not clear to me.


If the main panel is feeding the subpanel and there is a main disconnect (or 6 throw) in the main panel that doesn't cover the subpanel? Doesn't that count as means of disconnecting?
I am curious, if the logic (of having a sub panel main disconnect) is to ensure the sub panel (in a detached structure) doesn't get energized by someone at the service panel, why wouldn't that apply to a remote (not in line of sight) location?

Or perhaps a better question is what is the difference between a detached structure and (for example) a different level/room of the same structure?

If that is not the logic, please disregard.
</IMG>



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #14  
Old 3/12/08, 2:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,035
Default Re: 6 breaker exceeded

Here is the section where location is addressed.

Quote:
225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 3/12/08, 2:17 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

So in English, he is trying to say the kill needs to be near the entrance of the conductors, for the structure.
Not really an answer but a statement of CODE.
Seems to me it should be required since so many are mis labeled.(refering to the subs)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker Question mhawley Electrical 5 1/14/08 4:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 6:34 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts