Default 6 breaker exceeded

If sub-panels have more than 6 breakers should it have a service disconnect or does that only apply to the main panel?

Thanks ahead of time




Mike Hazelwood
Bakersfield, California
mike@calproinspections.com
www.calproinspections.com
Reply With Quote
  #2  
Old 3/11/08, 1:39 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Mike check out the thread under yours.
I just had that answered.
Reply With Quote
  #3  
Old 3/11/08, 8:20 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Detached structure it does. Within the same structure NO main is required.
Reply With Quote
  #4  
Old 3/11/08, 11:04 PM
Mike Hazelwood's Avatar
Mike Hazelwood Mike Hazelwood is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Bakersfield, Ca
Posts: 443
Default Re: 6 breaker exceeded

Quote:
Originally Posted by Speedy Petey
Detached structure it does. Within the same structure NO main is required.
sub-panel is in a detached garage???




Mike Hazelwood
Bakersfield, California
mike@calproinspections.com
www.calproinspections.com
Reply With Quote
  #5  
Old 3/11/08, 11:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by mhazelwood
sub-panel is in a detached garage???
I'm confused. You made a statement, but put question marks on the end. Is that panel in question in a detached garage or not?
Reply With Quote
  #6  
Old 3/12/08, 12:04 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Yeah, I'm confused too.
Maybe I was not clear.
Reply With Quote
  #7  
Old 3/12/08, 1:38 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

I often wondered if anyone tried to invoke 225.32 exception 1 in the residence of a qualified person
Quote:
Exception No. 1: For installations under single management, where documented safe switching procedures are established and maintained for disconnection, and where the installation is monitored by qualified individuals, the disconnecting means shall be permitted to be located elsewhere on the premises.
Reply With Quote
  #8  
Old 3/12/08, 1:46 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by Greg Fretwell
I often wondered if anyone tried to invoke 225.32 exception 1 in the residence of a qualified person
Yeah, nice try.

That exception is mainly for industrial establishments with a central powerhouse.
Reply With Quote
  #9  
Old 3/12/08, 2:13 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: 6 breaker exceeded

Quote:
Originally Posted by mhazelwood
If sub-panels have more than 6 breakers should it have a service disconnect or does that only apply to the main panel?

Thanks ahead of time
It applies to the main panel.
Reply With Quote
  #10  
Old 3/12/08, 8:20 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by bkelly2
It applies to the main panel.
....AND to a panel in a detached structure.

Even though you guys don't do codes this seems to be a hard sell. So here:

II. More Than One Building or Other Structure
225.31 Disconnecting Means
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
Reply With Quote
  #11  
Old 3/12/08, 11:59 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
That exception is mainly for industrial establishments with a central powerhouse.

Marc, it doesn't say that. I know I would have a hard time approving the installation but if the owner had placards on the subpanel and demonstrated he was "qualified" (licensed) I am not sure how I would justify the rejection if he fought it.

The fact that any installation was compliant at the time of inspection does not guarantee that those procedures will remain in place or that it will continue to be supervised by qualified people. As far as I am concerned the exception guts the intent of the rule.
Reply With Quote
  #12  
Old 3/12/08, 1:19 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: 6 breaker exceeded

Speedy, Not disagreeing, trying to understand. This code is not clear to me.

Quote:
II. More Than One Building or Other Structure
225.31 Disconnecting Means
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

If the main panel is feeding the subpanel and there is a main disconnect (or 6 throw) in the main panel that doesn't cover the subpanel? Doesn't that count as means of disconnecting?

Last edited by kgerhauser; 3/12/08 at 1:33 PM..
Reply With Quote
  #13  
Old 3/12/08, 2:02 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

Quote:
Originally Posted by kgerhauser
Speedy, Not disagreeing, trying to understand. This code is not clear to me.


If the main panel is feeding the subpanel and there is a main disconnect (or 6 throw) in the main panel that doesn't cover the subpanel? Doesn't that count as means of disconnecting?
I am curious, if the logic (of having a sub panel main disconnect) is to ensure the sub panel (in a detached structure) doesn't get energized by someone at the service panel, why wouldn't that apply to a remote (not in line of sight) location?

Or perhaps a better question is what is the difference between a detached structure and (for example) a different level/room of the same structure?

If that is not the logic, please disregard.
</IMG>
Reply With Quote
  #14  
Old 3/12/08, 2:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,759
Default Re: 6 breaker exceeded

Here is the section where location is addressed.

Quote:
225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 3/12/08, 2:17 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 6 breaker exceeded

So in English, he is trying to say the kill needs to be near the entrance of the conductors, for the structure.
Not really an answer but a statement of CODE.
Seems to me it should be required since so many are mis labeled.(refering to the subs)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
Breaker Question mhawley Electrical Inspections 5 1/14/08 4:25 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 10:04 AM


All times are GMT -4. The time now is 10:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts